09-02-2010, 08:17 AM
|
#41
|
Winnie-Wise
Join Date: Sep 2003
Location: Destin, FL
Posts: 494
|
Roadking; RVP told me they are going to make more basement units & the lead unit is at the UL facility for testing & approval. They estimate production by year's end. Caveat: Units MUST have 50 Amps (they also have R410 vs R22).
Thudman
__________________
03 Adventurer 38G, W22, 22.5 Whls
Koni FSD's, TracBar rear, SteerSafe, 50A SurgeGuard, Eternabond; 2012 Honda CRV EXL w/Nav & AWD
|
|
|
09-02-2010, 08:45 AM
|
#42
|
Winnie-Wise
Join Date: Sep 2003
Location: Destin, FL
Posts: 494
|
Dan: Have been hassling with svc ctr (Tom Johnson, Marion, NC) for over three weeks. Parts finally on order, but next week they have a BBQ shindig so cannot sched me then. The good news is, it's cooling off, so one lung does reasonably well.
I'm upgrading the outside blower wheel to plastic and putting in two sealed bearings per Duner's FABULOUS post. Also check both systems' Freon. So I'll have two Schrader valves. Also R&R all (five?) Start Caps. I'll have to pay for the upgrades, Freon & Start Caps. For #1 compressor R&R, Good Sam CSP pays $1217 (of that I pay 500 ded).
Still waiting for appt to do it. As a side note, svc rep said fridge cannot be On, even elec mode. Never heard of that. LP mode, yes; but elec??? 'Nuther irritant
Will
__________________
03 Adventurer 38G, W22, 22.5 Whls
Koni FSD's, TracBar rear, SteerSafe, 50A SurgeGuard, Eternabond; 2012 Honda CRV EXL w/Nav & AWD
|
|
|
09-02-2010, 10:41 AM
|
#43
|
Winnebago Owner
Join Date: Dec 2006
Location: Tx
Posts: 130
|
Roadking - I went and checked on my coach at my Winnie dealer, the new ac unit is in place and checked out.
The 4 in stock you refer to are 4 of the old "matching part number" units that they will not sell. Still don't know the part # of the new replacements yet.
One weird thing, the parts guy said he had to sign and fax back a letter to Winnie stating that "under no circumstances" would this unit be returned to Winnie. I said if it arrived DOA, it damn sure would be going back.
__________________
Rather be Ridin' than Rollin'
2003 UA 40E(wheelchair accessible)
|
|
|
09-02-2010, 10:45 AM
|
#44
|
Winnebago Master
Join Date: Sep 2004
Location: Glen Allen, VA
Posts: 2,169
|
Some comfort to know that RVP will be producing new basement heat pumps, especially for those of us who have decided to keep our rigs.
I do wonder if they will be similar size and configuration so they can be retrofitted to the older rigs if replacement is necessary.
__________________
'07 Country Coach Allure 470 Siskiyou Summit #31578, Cummins ISL 425; 2014 Ford F150 toad; Air Force One Toad Brake.
Glen Allen, VA; Smith Mountain Lake, VA.
|
|
|
09-02-2010, 10:48 AM
|
#45
|
Winnebago Owner
Join Date: Dec 2006
Location: Tx
Posts: 130
|
Smlranger - just had one "dropped in" in place on my 2003 UA.
__________________
Rather be Ridin' than Rollin'
2003 UA 40E(wheelchair accessible)
|
|
|
09-02-2010, 05:05 PM
|
#46
|
Winnie-Wise
Join Date: Sep 2003
Location: Destin, FL
Posts: 494
|
New Unit P/N 46515-811, with R-410.
Thudman
__________________
03 Adventurer 38G, W22, 22.5 Whls
Koni FSD's, TracBar rear, SteerSafe, 50A SurgeGuard, Eternabond; 2012 Honda CRV EXL w/Nav & AWD
|
|
|
09-02-2010, 07:00 PM
|
#47
|
Winnebago Master
Join Date: Sep 2004
Location: Glen Allen, VA
Posts: 2,169
|
Quote:
Originally Posted by McDuff
Smlranger - just had one "dropped in" in place on my 2003 UA.
|
Outstanding. Give us a report on how well it works compared to the original unit before you had problems. What is the BTU rating of the new unit?
__________________
'07 Country Coach Allure 470 Siskiyou Summit #31578, Cummins ISL 425; 2014 Ford F150 toad; Air Force One Toad Brake.
Glen Allen, VA; Smith Mountain Lake, VA.
|
|
|
09-03-2010, 04:56 PM
|
#48
|
Winnebago Owner
Join Date: Dec 2006
Location: Tx
Posts: 130
|
I will report back, still don't have my coach back yet. And I'm having a birthday pool party tomorrow, yea I made another year, so I haven't checked back in a few days. Wife as been on a tear getting the house ready.
Don't know the BTU's either, would be great if they dropped some 15K's in there. I'll add that to my report.
They were waiting on a new inverter, and a couple hydraulic hoses. When he pulled the ac, it was covered with hyd fluid. There are 2 little hoses that feed the BR slide and one of them had a bubble in it and was leaking. According to the tech, after talking to Winne, for 2 yrs only, mine in '03 and either one up or down, they outsourced these 2 hoses. The sub co. went belly up and now HWH is trying to mate up these lines.
Always something.
__________________
Rather be Ridin' than Rollin'
2003 UA 40E(wheelchair accessible)
|
|
|
09-07-2010, 03:42 PM
|
#49
|
Winnie-Wise
Join Date: Oct 2002
Location: Madison, MS
Posts: 450
|
Can someone please confirm the amp draw that should be displayed when running basement A/C on genset. I'm looking to know how many amps when only one compressor is in use and how many when both compressors are running simultaneously. THANKS, Ed
__________________
2016 EC Aspire 42RBQ / 2014 CR-V
|
|
|
09-07-2010, 06:35 PM
|
#50
|
Winnebago Camper
Join Date: Jul 2006
Location: SE PA
Posts: 43
|
Last week I was down in Assateague MD,and it was pretty hot.So I ran my genny.As I recall,when the A/C first came on,I would see a 34 or so flash,then it would go down to about 24/22,then eventually drop to about 14/12 when the coach had cooled down.
__________________
'09 Winnebago Adventurer 32H
Workhorse W-22, UltraPower,496 cubic inches of
|
|
|
09-07-2010, 06:56 PM
|
#51
|
Winnie-Wise
Join Date: Oct 2009
Posts: 277
|
Quote:
Originally Posted by edgray
Can someone please confirm the amp draw that should be displayed when running basement A/C on genset. I'm looking to know how many amps when only one compressor is in use and how many when both compressors are running simultaneously. THANKS, Ed
|
I put the generator on and the Basement Air at high cool. It was drawing 22 amps. Then I put the new rooftop Coleman Mach 13,500 on at high cool and the One Place Panel showed a total amp use of 35. I turned the TV on and the panel read-out didn't change. Adding the microwave the amp meter read 48. Joe
__________________
2008 Itasca Latitude 39W. Cummins ISB 6.7 Turbo 340HP. Allison 6 Speed. Freightliner XCS. Michelin XRV 255/80R 22.5 LRG. SuperSteer MCU. Safe-T-Plus.
|
|
|
09-07-2010, 09:01 PM
|
#52
|
Winnie-Wise
Join Date: Oct 2002
Location: Madison, MS
Posts: 450
|
Thanks for the answers so far. What I'm trying to determine is if one or both compressors are running. I have the T-stat set for a temp greater than 15 degrees below the displayed room temp. I was told was more than enough to call for both compressors to be on together. I'm only seeing 18-19 amps running (after start surge), which has me questioning if the second compressor is coming on. Do you know of any other way to tell if there is one or two running? THANKS, Ed
__________________
2016 EC Aspire 42RBQ / 2014 CR-V
|
|
|
09-07-2010, 09:12 PM
|
#53
|
Winnebago Owner
Join Date: Feb 2006
Location: Howell, New Jersey
Posts: 165
|
Quote:
Originally Posted by edgray
Can someone please confirm the amp draw that should be displayed when running basement A/C on genset. I'm looking to know how many amps when only one compressor is in use and how many when both compressors are running simultaneously. THANKS, Ed
|
Ed, not sure how you're wired but in my unit, there's a dedicated 20 amp circuit breaker on the generator that goes right to the AC. When it's running I get 14-15 amps reading but I can hear when the second compressor kicks in and there's no additional reading on the amp guage. On shore power I read 26-28 with both compressors running.
__________________
Tim ,Retired Police Lt. 2002 Winnebago Adventurer+16' Trailer
Harley Road King and Heritage Classic+,Trik-L-start,Hughes Autoformer. Blue Tick Coon hound
|
|
|
09-07-2010, 09:30 PM
|
#54
|
Winnie-Wise
Join Date: Oct 2002
Location: Madison, MS
Posts: 450
|
Quote:
Originally Posted by Fossilhog
Ed, not sure how you're wired but in my unit, there's a dedicated 20 amp circuit breaker on the generator that goes right to the AC. When it's running I get 14-15 amps reading but I can hear when the second compressor kicks in and there's no additional reading on the amp guage. On shore power I read 26-28 with both compressors running.
|
When I'm plugged in to 50 amp shore power, the display won't show amps being used at all, it remains blank. When plugged in to 30 amps, I'm "assuming" it won't allow both compressors to run at the same time, but I'll try that tomorrow. I've been wrong once before.
Ed
__________________
2016 EC Aspire 42RBQ / 2014 CR-V
|
|
|
09-07-2010, 09:36 PM
|
#55
|
Winnie-Wise
Join Date: Jun 2006
Location: Southern California
Posts: 489
|
Quote:
Originally Posted by edgray
When I'm plugged in to 50 amp shore power, the display won't show amps being used at all, it remains blank. When plugged in to 30 amps, I'm "assuming" it won't allow both compressors to run at the same time, but I'll try that tomorrow. I've been wrong once before.
Ed
|
Ed, I have a 30amp outlet at my house that is strictly for my motorhome. When I turn on the air conditioner the display will read 14 to 16 amps for a couple of minutes until the second compressor kicks in, then it will read from 22 to 24 amps.
Sammie
__________________
2015 Tiffin Bus 37AP
2016 Ford Explorer
"A Job Begun is Half Done"
|
|
|
09-08-2010, 07:45 AM
|
#56
|
Winnebago Owner
Join Date: Feb 2006
Location: Howell, New Jersey
Posts: 165
|
Quote:
Originally Posted by edgray
When I'm plugged in to 50 amp shore power, the display won't show amps being used at all, it remains blank. When plugged in to 30 amps, I'm "assuming" it won't allow both compressors to run at the same time, but I'll try that tomorrow. I've been wrong once before.
Ed
|
That sure doesn't sound right at all.....no amps shown.
__________________
Tim ,Retired Police Lt. 2002 Winnebago Adventurer+16' Trailer
Harley Road King and Heritage Classic+,Trik-L-start,Hughes Autoformer. Blue Tick Coon hound
|
|
|
09-08-2010, 08:09 AM
|
#57
|
Winnie-Wise
Join Date: Oct 2009
Posts: 277
|
Quote:
Originally Posted by Fossilhog
That sure doesn't sound right at all.....no amps shown.
|
When on shore power the amps do not show on Winnebago/Itasca products. It only has a readout on generator. Joe
__________________
2008 Itasca Latitude 39W. Cummins ISB 6.7 Turbo 340HP. Allison 6 Speed. Freightliner XCS. Michelin XRV 255/80R 22.5 LRG. SuperSteer MCU. Safe-T-Plus.
|
|
|
09-08-2010, 08:23 AM
|
#58
|
Winnebago Owner
Join Date: Feb 2006
Location: Howell, New Jersey
Posts: 165
|
Quote:
Originally Posted by azloafer
When on shore power the amps do not show on Winnebago/Itasca products. It only has a readout on generator. Joe
|
Does that only pertain to 50 amp coaches? My Adventurer is a 30 amp unit and I get readouts on my ems panel of anything on the 30 amp side of the generator when running. Only the 2nd compressor doesn't show because its on the 20 amp side.
__________________
Tim ,Retired Police Lt. 2002 Winnebago Adventurer+16' Trailer
Harley Road King and Heritage Classic+,Trik-L-start,Hughes Autoformer. Blue Tick Coon hound
|
|
|
09-08-2010, 08:53 AM
|
#59
|
Winnie-Wise
Join Date: Oct 2002
Location: Madison, MS
Posts: 450
|
Quote:
Originally Posted by Fossilhog
Does that only pertain to 50 amp coaches? My Adventurer is a 30 amp unit and I get readouts on my ems panel of anything on the 30 amp side of the generator when running. Only the 2nd compressor doesn't show because its on the 20 amp side.
|
Yes, I think that is correct. Apparently they believe if that you are on a 50 amp 4 wire service, you have no need to know what the load is because you "can't" consume more than is available. I think it would be nice if it would read the amp draw even while on 50, but it does not.
I'm now plugged into my 30 amp 3 wire service at home and it alternately shows 1 or 2 amps with nothing "on" except the converter. When the T-stat is set for 2 degrees below the displayed room temp, the A/C comes on and the display shows 12 amps. Turning the T-stat down to 20 degrees below the room temp caused the A/C to make a slight noise (I assume 2nd compressor kicked in) and the amps went up to 17.
Unfortunately, if in fact both compressors are running, then I must have another problem because the A/C is not cooling the coach satisfactorily. Ed
__________________
2016 EC Aspire 42RBQ / 2014 CR-V
|
|
|
09-08-2010, 09:01 AM
|
#60
|
Winnebago Owner
Join Date: Feb 2006
Location: Howell, New Jersey
Posts: 165
|
Quote:
Originally Posted by edgray
Yes, I think that is correct. Apparently they believe if that you are on a 50 amp 4 wire service, you have no need to know what the load is because you "can't" consume more than is available. I think it would be nice if it would read the amp draw even while on 50, but it does not.
I'm now plugged into my 30 amp 3 wire service at home and it alternately shows 1 or 2 amps with nothing "on" except the converter. When the T-stat is set for 2 degrees below the displayed room temp, the A/C comes on and the display shows 12 amps. Turning the T-stat down to 20 degrees below the room temp caused the A/C to make a slight noise (I assume 2nd compressor kicked in) and the amps went up to 17.
Unfortunately, if in fact both compressors are running, then I must have another problem because the A/C is not cooling the coach satisfactorily. Ed
|
Ed can you turn off the circuit breaker for #2 and see a change in the reading? 17 seems awful low for 2 comps. running.
__________________
Tim ,Retired Police Lt. 2002 Winnebago Adventurer+16' Trailer
Harley Road King and Heritage Classic+,Trik-L-start,Hughes Autoformer. Blue Tick Coon hound
|
|
|
|
|