Hi, I’m running my 5500 Watt Onan gennie with two ACs on while driving due to very hot weather. They both ran for several hours and all of a sudden they shut down and the control panel beeped with the gennie still running. It eventually reset itself. This happened several times. We had a full tank of gas. I had the gennie serviced recently. Why is this happening?
__________________
2016 Winnebago Vista LX 30T
2012 Equinox V6 AWD w/Sterling AT & RViBrake3
Safe T Plus steering, Koni FSD shocks, rear track bar, heavy duty anti-sway bars
Lakejumper is offline   Reply With Quote
Old 09-04-2022, 08:34 AM   #2
Winnie-Wise
 
Join Date: Dec 2019
Location: Kansas
Posts: 393
Have you checked the oil level in the generator? Also, did it set any fault codes? You can download operator and service manuals by searching online that contain good troubleshooting information. They also explain how to check for and interpret the fault codes. You might check around the generator to see if the cover got reinstalled correctly and that nothing is blocking the airflow around it since it seems like the problem might be related to heat.

This is a long shot but with the generator off and not connected to shore power turn off your 12V disconnect switch (the salesman's switch) by the entry door for a few minutes. Sometimes just removing power allows the logic boards to reset and helps sort things out.
__________________
The things you own control your life.
2021 Winnebago Vista 35U towing a 2022 Jeep Cherokee Trailhawk
2010 Cadillac SRX 2003 Itasca Sunova 30B
Bones2003 is offline   Reply With Quote
Old 09-04-2022, 09:37 AM   #3
Winnebago Master
 
Join Date: Nov 2018
Location: Pflugerville/Austin, Tx
Posts: 7,530
I would first want to decide which was giving me trouble. If the monitor beeps and the generator is still running, that would lead me to think it was not the generator.
So what does the manual say about the beeps? Is it a series of beeps to"decode" the error message?
I would think a check of the manual for what those beeps mean might be a first clue.

When you say it eventually reset itself, do you mean you did not look at the alarm to see what it was telling you? That can get us into a lot of trouble if we ignore warning signals!

Are you sure it was not the smoke detector you were hearing?

We need more precise info on what happened.
__________________
Richard
Why no RV year, make and floorplan on MY signature as we suggest for others?
I currently DO NOT have one!
Morich is offline   Reply With Quote
Old 09-04-2022, 11:32 AM   #4
Site Team
 
creativepart's Avatar
 
Join Date: Sep 2009
Location: Spring Branch, TX
Posts: 7,830
I had this happen to me once recently, too. The generator never stopped running but the AC power seemed to reset. It, too, was when I was driving. I was near a place to stop and when I did the power came back on because the microwave chirped the way it does when power is applied. The A/C units took a while to restart because of the 5-min delay when resetting the units.

Because the power from the generator came back just as I stopped there was nothing to investigate. I have a generator switch on my dash that has a light. Sometimes when the generator is running as I drive if I'm forced to make a sudden stop or hit a very big drop or bump the generator will shut down. But I've never seen it restart all by itself. I have to restart it with the switch.

The power problem has not happened previously or since. So, I'm going to say all is fine until it does it again.
__________________
2017 Winnebago Adventurer 37F
2016 Lincoln MKX Toad
creativepart is offline   Reply With Quote
Old 09-04-2022, 03:28 PM   #5
Winnebago Owner
 
Join Date: Feb 2007
Location: Northern California
Posts: 118
Thank you for your replies. I think that I know what happened. I failed to mention that I was in the high Sierra mountains at about 6000-7200 feet when this occurred. I believe that the Power Management System did a “load shed”. The manual states that the AC’s use at least 2400 when starting up. I have a 15k btu in the front and either a 13.5k or 11k in the rear. The manual states that the 5500watt gennie loses 3.5% power for every 1000 feet gain in elevation.This, I was losing about 23% of the gennie power. It couldn’t keep up with the ACs.This has been a good lesson.
__________________
2016 Winnebago Vista LX 30T
2012 Equinox V6 AWD w/Sterling AT & RViBrake3
Safe T Plus steering, Koni FSD shocks, rear track bar, heavy duty anti-sway bars
Lakejumper is offline   Reply With Quote
Old 09-12-2022, 04:56 PM   #6
Winnebago Master
 
jerichorick's Avatar
 
Join Date: Jun 2013
Location: Full-timer/volunteer w/SOWERS
Posts: 2,737
Quote:
Originally Posted by Lakejumper View Post
Hi, I’m running my 5500 Watt Onan gennie with two ACs on while driving due to very hot weather. They both ran for several hours and all of a sudden they shut down and the control panel beeped with the gennie still running. It eventually reset itself. This happened several times. We had a full tank of gas. I had the gennie serviced recently. Why is this happening?
I can think of a couple of things and I hope they pertain to your coach.

1/ can you adjust the shore power charge rate? This must be set to a low setting when on the generator.

2/ is your water heater ac switch on? This must be off when running on the generator. In both cases the EMS will see an overload and shut everything down to preserve the system. When on shore power there is enough available power to allow the EMS to shed loads on at a time. The generator power is so small in comparison it shuts everything off. After a period of time it brings things back on line.
This is only my theory. You can test this by watching your amp reading when running these things from the generator. You have only about 22A per leg available. When the HVAC units are running you have about 8 amps per leg to spare.
__________________
Rick & Melissa Young & Dawson (RIP), 2011 Meridian 40U, FL XCL, ISL 380HP/DEF, Al 3000 MH, 2014 Honda CR-V, SMI AF1, Blue Ox TruCenter & tow equip.,EEZTire TPMS.
Servants On Wheels Ever Ready. Best job we ever paid to do . (full time volunteers)
jerichorick is offline   Reply With Quote
Reply

Tags
generator


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
2011 Winnebago Tour ACs touring2 Winnebago Class A Motorhomes 19 08-12-2014 09:56 PM
Onan shuts down Multiengine Electrical | Charging, Solar and Electronics 6 08-18-2010 06:30 AM
Gas Onan 5500 shuts down after start antec7 Winnebago General Discussions 10 07-04-2006 03:28 AM

» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Winnebago Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 08:21 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.