Hi, I’m running my 5500 Watt Onan gennie with two ACs on while driving due to very hot weather. They both ran for several hours and all of a sudden they shut down and the control panel beeped with the gennie still running. It eventually reset itself. This happened several times. We had a full tank of gas. I had the gennie serviced recently. Why is this happening?
|
I can think of a couple of things and I hope they pertain to your coach.
1/ can you adjust the shore power charge rate? This must be set to a low setting when on the generator.
2/ is your water heater ac switch on? This must be off when running on the generator. In both cases the EMS will see an overload and shut everything down to preserve the system. When on shore power there is enough available power to allow the EMS to shed loads on at a time. The generator power is so small in comparison it shuts everything off. After a period of time it brings things back on line.
This is only my theory. You can test this by watching your amp reading when running these things from the generator. You have only about 22A per leg available. When the HVAC units are running you have about 8 amps per leg to spare.