Old 05-02-2023, 07:13 PM   #1
Winnebago Camper
 
gabbyh's Avatar
 
Join Date: Aug 2020
Location: virginia S.E.
Posts: 34
only 30 amps on 50 amp circuit

on last 4 of 5 hook up to known 50 amp pedestals inside panel only shows 30 amps , switches to genset as it should . at home now hooked to 50 amp , both legs show 50 amps , panel still shows 30 amps . cable and other connections in auto switch are tight . no known breakers tripped . any ideas were to next thanks Gabby
__________________
2006 journey 36 se /highlander
super co-pilot karen
navigator corgi kringle
gabbyh is offline   Reply With Quote
Old 05-02-2023, 07:38 PM   #2
Winnie-Wise
 
Join Date: Jul 2006
Location: Michigan
Posts: 471
Some thoughts...

Make sure all the 120v breakers are turned on, flipping them a time or two to clear them. The system display is based on measuring voltages in your breaker panel, and even if you have both legs energized, if the two breakers being checked are not both on, it will default to a 30amp display. Some have been hit by this when they turned off a breaker (i.e. water heater) when not used, not realizing it affects the display depending on how the system was installed and what breakers are being checked.

Another way to clear the display and do a reset is to totally power down the RV. Unplug, no gen, salesman switch "off" so everything goes dark. Then try powering back up.

Beyond that you will need to get into the 120v panel to check things, like the 12v fuse on the Intellitec circuit board.

You can also remove the bezel around the display, unscrew the display, GENTLY pull it away from the cutout and make sure all the cables going into the display are tight, though it does seem like that it is working properly.
__________________
Ed & Joie
2004 Vectra 40KD
Freightliner Chassis and Cummins ISC
emiddleb is offline   Reply With Quote
Old 05-03-2023, 04:21 AM   #3
Just Trying to Help
 
Join Date: Aug 2015
Posts: 526
Gabby-

Wiring diagrams for the 2006 Journey 36 are here, and for the 36SG are here.

The "meter" is part of the Intellitec Energy Management System (EMS). An EMS Installation and Service Manual is at this link. "Trouble Shooting" part "VIX," page 14 (link here) describes the symptom you are seeing. Start by troubleshooting using that section.

Here is another version of the EMS manual, labeled "Powerline 2004." I may be incorrect, but I seem to recall that "Powerline" was Winnebago's label for the Intellitec EMS.

Here are some of the reasons the EMS display could be showing 30A when connected to 50A service:

1) One of the circuit breakers that feeds the EMS is off, tripped or broken. In your coach's case, that would be the refrigerator and water heater breakers.
2) The EMS is broken.
3) One of the two 50A legs to the load center (breaker panel) is broken

If all the 120V loads work correctly when connected to 50A service, you can be pretty sure the problem is with the EMS (1 or 2, above). On the other hand, if you can't demonstrate or measure that each 50A leg into the load center is OK, the problem is upstream, often in the transfer switch and sometimes in the shore cord.
__________________
Mark
2008 Holiday Rambler Admiral 30PDD (Ford F-53 chassis)
2009 Honda Fit Sport
l1v3fr33ord1 is offline   Reply With Quote
Old 05-03-2023, 09:43 AM   #4
Winnebago Master
 
cbeierl's Avatar
 
Join Date: Aug 2005
Location: Nashua, NH
Posts: 1,827
Page 5 of the 110 Volt Load Center/Auto Transfer Switch diagram (same for both 36 and 36SG) shows that the rightmost breaker must be ON for the EMS to work correctly (see note /8\).
__________________
Chris Beierl

2005 Winnebago Vectra 36RD
cbeierl is offline   Reply With Quote
Old 05-04-2023, 09:09 PM   #5
Winnebago Master
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 2,114
Do you have a reel for the shore power cord? If so, the contacts between the reel and the base are not making full contact.
DO NOT attempt to work on the reel when attached to shore power, nor move the reel when on shore power.
The contacts can be refurbished.
__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA 1SG, retired;PPA,Good Sam Life member,FMCA. "We the people are the rightful masters of both the Congress and the Courts - not to overthrow the Constitution but to overthrow men who pervert the Constitution." Abraham Lincoln
Ray,IN is online now   Reply With Quote
Old 05-04-2023, 09:22 PM   #6
Winnebago Master
 
powercat_ras's Avatar
 
Join Date: May 2015
Location: Manhattan, Kansas USA
Posts: 1,318
Since you are parked at a location where the EMS sees 50 amp service that should indicate that all breakers are on & good and that the shore power cord is good. 50 amp is actually two 50 amp feeds, one on phase 1 and other on phase 2 of a 240 volt 2 phase electric service. Each hot feed is 120 volts to Neutral, but they are 180 degrees out of phase.

30 amp is just one 30 amp feed, a single phase. This is why a 30 amp 120 Volt RV outlet only has 3 slots (Hot, Neutral, Ground), and a 50 amp outlet has 4 slots (Hot Feed 1, Hot Feed 2, Neutral, Ground).

If you read AC voltage between the Hot Feed 1 and Hot Feed 2 outlet slots , if wired correctly it will read 240 VAC, because of the two feeds being 180 degrees out of phase with each other. When you use a 30 amp to 50 amp adapter, both sides are fed from 1 phase and if you read between the Hot 1 and Hot 2 outlet slots on the adapter you will read zero volts. This is how the EMS can tell you are using an adapter to plug into 30 amp, it samples AC voltage from the 2 hot feeds inside your RV, if it sees 0 V it knows it is not plugged into a properly wired 50 A shore power outlet.

Hopefully this background will assist you in troubleshooting.
__________________
Randy - Manhattan, Kansas
2015 Vista 27N
2020 Ford Escape Hybrid
powercat_ras is offline   Reply With Quote
Old 08-02-2023, 05:41 PM   #7
Winnebago Camper
 
gabbyh's Avatar
 
Join Date: Aug 2020
Location: virginia S.E.
Posts: 34
Quote:
Originally Posted by gabbyh View Post
on last 4 of 5 hook up to known 50 amp pedestals inside panel only shows 30 amps , switches to genset as it should . at home now hooked to 50 amp , both legs show 50 amps , panel still shows 30 amps . cable and other connections in auto switch are tight . no known breakers tripped . any ideas were to next thanks Gabby
sorry 4 late update and this may be in the wrong place. having cked everything , determined it was the intellatic control board in the main 110 panel , foot of the bed . easy fix 6 110 volt wires and 3 plug in . get board from M&M RV electrics in Ohio. NOT Amazon
__________________
2006 journey 36 se /highlander
super co-pilot karen
navigator corgi kringle
gabbyh is offline   Reply With Quote
Old 08-02-2023, 05:46 PM   #8
Winnebago Camper
 
gabbyh's Avatar
 
Join Date: Aug 2020
Location: virginia S.E.
Posts: 34
fixed

finally got to work on this problem . found out it was the intelletic control board located in the main 110 volt panel foot of bed . easy swap out 6 110 wires and 3 harness plugs . get new board at M&M electronics in Ohio ,not on Amazon
__________________
2006 journey 36 se /highlander
super co-pilot karen
navigator corgi kringle
gabbyh is offline   Reply With Quote
Old 08-02-2023, 07:37 PM   #9
Winnie-Wise
 
Join Date: Jul 2006
Location: Michigan
Posts: 471
Congrats on the fix!
__________________
Ed & Joie
2004 Vectra 40KD
Freightliner Chassis and Cummins ISC
emiddleb is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
50 amp service only reading 30 amps on panel Diver2diver Electrical | Charging, Solar and Electronics 29 08-12-2021 02:14 PM
Plug in to 50 amp, only getting 30 amps Lake11969 Electrical | Charging, Solar and Electronics 15 02-27-2016 09:56 AM
House amp gauge only displays #'s on 30 amp. Tomtall Electrical | Charging, Solar and Electronics 16 06-24-2014 09:11 PM
RV is 50 amps, RV Park Spot is 30 amps jmraz73 Plumbing | Systems and Fixtures 30 01-06-2014 05:12 PM
Power Line One Panel Limits One Leg 50 Amp circuit to 30 Amps SteveG Electrical | Charging, Solar and Electronics 17 03-05-2008 04:43 PM

» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Winnebago Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 09:38 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.