Genset running - stays at 0 amps - nothing 110v will run
The last time this happened it was just the breaker switch on the genset. This time I did notice a couple GFIs nearby were tripped. When resetting these the ems panel came on and shows 0 amps being taken from the gen. AC won’t turn on. Fridge won’t run on AC. Nothing 110v will/can take power.
Additionally, the ems panel will toggle between the genset and 30/50amp power lights - even though no shore power plugged in.
From everything I’ve read, and my experience with these issues, it’s almost always a breaker or something simple. I’ve checked everything I know to check. Oh and this did work a few weeks ago. It was just the switch on the genset and everything was fine then.
Location: Sarnialabad, Peoples Republik of Canuckistan
Posts: 1,251
That "toggle" on your EMS makes it sound like something to do with a transfer switch. Is there an auto-transfer switch? Maybe see if there's a way to reset it. It may be "locked" out on shore power, and not switching back to generator?