I find even the Manufacturers of Batteries Fail to properly State the Configuration of Battery Cells, as the Ah is usually stating what the Cell Rating is, as with Modern Battery Inverter Technology a 48VDC System commonly can safely have a Full Charge voltage of 51.2VDC of higher, without an adverse affects.
Leaving out the Cave-man LAB, and looking at the Safest of the Lithium Batteries, being LiFePO4 ("Lithium IRON" Not "Lithium ION" the Dangerous type), nearly all use Cells with 3.2VDC.
If Cells are 100Ah and configures 3.2V
15/2 (Series/Parallel) you get 48V (
Power) System that provides 9.60kWh of
Energy.
However, if Cells are 100Ah and configures 3.2V
16/2 you get 51.2V (
Power) System that provides 10.24kWh
Energy, and the higher Voltage is better for High Amp Equipment Draw.
This is a useful Battery Calculator;
https://www.micropowergrids.com.au/C...alculator.html
Manufacturers/Retailers should also be telling people how much kWh (Wh) of ENERGY the Battery can Deliver as shown above, as the Amp Hour is Not an indication how much Energy is Stored in your battery Module !
Get to Know the Difference between POWER & ENERGY;
https://www.micropowergrids.com.au/_...Explained.html