Have your batteries load-tested, I think you'll find at least one of them is faulty if they are the OEM batteries.
Another aspect;
Do you have a setting in your inverter for a low battery alarm? If this is set above 11V, then while the battery bank is being drawn-on the alarm will usually sound. While the inverter is drawing on the batteries they are depleting @ 10X the AC amperes being produced.
So if your appliance is drawing 10A AC, the batteries are losing 100A DC per hour.