This summer I experienced an odd power problem and my Onan 7500QD was also throwing a 46 fault code; and my EMS/PMS was not showing me any amps when on 30A power, but all my power was working on all wall receptacles.
After some trial and error I started to figure out how all these things worked separately and together. For example:
* Onan Code 46 implies many things. Some say this code gets tripped when your batteries are low on voltage; and other claim the fixed this problem by replacing the inverter board in the Onan for over $2,000. In my case, it turns out I cleared this code by doing 1 of 2 things:
A) While plugged into shore power, I started the generator. And when I pulled the shore power cord, the Onan quit running. Hmmm? ...I surmise that when I pulled the 50A power cord it disconnected the Neutral Bond in the ATS (Automatic Transfer Switch) and all was well again. However, I really can't be sure. What I am sure of is that my Onan #46 fault code is gone!
B) Even though my batteries measured 12.7V, they were badly sulfated and failed the load test. So I replaced the house batteries and all was well again. ...Could "funky house batteries" cause the Onan Inverter to throw a #46 fault code? Maybe... Probably?
I honestly don't know which of the above solutions cleared the Onan Fault Code #46, but I do know I needed new batteries, because my inverter started shutting down in 3 hrs of use, then that time dropped to 1 hour, and soon it was 15 minutes. So the more I used my coach on inverter power the worse my battery bank got! ...Why?
I think when you have 4-6V-GC2 batteries, and one goes bad, it effects all the others. You also cannot "equalize" the cells; and you cannot buy just one battery to put in the set, because that one battery will only last so long; and you will never be able to equalize your cells.
My house batteries were 2.5 years old, so the only real solution was to replace them.
INTELLITEC "Power Line" 620 EMS/PMS CIRCUIT BOARD
My circuit board is located in the Main Power Panel Box. And I have read in other posts these things you can do to fixt it:
* You need to rest the Power panel.
* If that does not work, you can pull the board and replace several resistors on the circuit board. (Search other thread for this process.)
Note: Your 30A service passes though your inverter transfer switch so if you don't have power to your wall outlets then this maybe your problem. However, I believe your ATS fails more often.
New you can go to Amazon and still buy these things:
https://www.amazon.com/Intellitec-00.../dp/B00ODJ5NN8
https://www.amazon.com/Intellitec-00...55SCAT213VRDD1
OTHER COMMENTS ABOUT POWER
* Circuit breakers only protect (trip) on the "Black" hot wire. They do not protect the neutral wire.
* You also need a good "Neutral" connection for electricity to flow.
* In 120V-AC systems you don't need a ground, but you should have one for safety reasons.
* Many 12V system problems are due to a bad ground.