Originally Posted by brican
As a former electrician and now an electrical engineer, I often get accused of over engineering everything, I really don't care if it means being safe. In this case I installed a 30 amp outlet with a 30 amp GFCI breaker. Even though we live in the desert it does rain and a ground is a ground. There is no reason to not do GFCI since code requires it for all outside outlets just like in the RV park. If you don't spend the extra money to do it you shouldn't do it at all. I looked all over Phoenix for a 30 amp GFCI breaker and finally found one in California. The installation I did is to code and safe. If your electrician/handy man says you don't need to do it, remind him/her who the customer is and insist on having a GFCI circuit. It is required in all bathrooms, utility rooms, garages, kitchens and outside for a good reason.
|
Up until the 2020 NEC GFCI protection was not required on a 30 amp 120 volt circuit except for certain applications such as pool equipment, however the 2020 NEC has removed the "15 & 20 amp" language basically making the TT receptacle now required to be GFCI protected. The language still states "supplied by a single phase branch circuit rated at 150 volts or less" which will exclude 240 volt GFCI requirements unless otherwise required such as pool equipment and spas.-https://www.electricallicenserenewal.com/Electrical-Continuing-Education-Courses/NEC-Content.php?sectionID=808.0
Not to say it's not a good idea anyway, but as the 2020 code is adopted it is now a requirement.