Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
 


Reply
 
Thread Tools Search this Thread Display Modes
 
Old 08-24-2015, 08:59 PM   #1
Winnebago Watcher
 
Trwolff's Avatar
 
Join Date: Aug 2015
Posts: 3
A/C amps

Ok, I'm an admitted newbie so I'm guessing one of you veterans will have an answer to this. I've got a 2005 Winnebago Voyage 38J with two A/C - heat pumps for HVAC. When on shore power and both units running, I pull 26 amps. However, when on generator and both units running, I'm only pulling 11 amps. My first thought was that the rear unit had tripped out and I was only running the front unit. Checked both the house and generator breakers and nothing had tripped. So I shut down both units and turned on just the rear unit. It was pulling just 3 amps, so I assumed it was just the fan blowing. However, in running it for a bit, it was blowing cold, so something was functioning. Turning the front unit back on, total amps jumped to 11, which is still way too low in my mind, but I'm getting cold air out of both units. Do I have a magical Onan or an A/C problem?
Trwolff is offline   Reply With Quote
Old 08-24-2015, 09:06 PM   #2
Winnebago Camper
 
96 Wideglide's Avatar
 
Join Date: Aug 2010
Posts: 26
11A is low for just one AC. The 26A you saw on shore power with two running is possible. I'm guessing you have 13,500btu units?
__________________
Ben & Sharon
2008 43' Holiday Rambler Scepter PDQ
96 Wideglide is offline   Reply With Quote
Old 08-24-2015, 09:10 PM   #3
Winnebago Master
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 2,113
I'll venture to say the rear unit compressor is not working, the circulating fan is drawing 3A, and circulating cool air. If they are ducted into the same plenum it's pulling cool air from the plenum. My roof mounted air conditioners drew around 9.5A each while compressor was running, surged to around 15A at start-up. Turn off both units, wait 2 minutes then start rear unit, if it does not show an amperage surge over 10 at start-up, the compressor did not run.
It could be as simple as replacing the start and/or run capacitors, which cost <$20.
__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA 1SG, retired;PPA,Good Sam Life member,FMCA. "We the people are the rightful masters of both the Congress and the Courts - not to overthrow the Constitution but to overthrow men who pervert the Constitution." Abraham Lincoln
Ray,IN is offline   Reply With Quote
Old 08-24-2015, 09:11 PM   #4
Winnebago Owner
 
Join Date: Sep 2012
Posts: 151
Off hand I'd say one of the compressors was not working at the moment. I'd try tracking over 15 minutes or maybe less to see if the line jumped up then dropped off again. There is some thermal lag.
nothermark is offline   Reply With Quote
Old 08-24-2015, 09:30 PM   #5
Winnebago Master
 
grtharris's Avatar
 
Join Date: Apr 2003
Location: Skiatook, OK
Posts: 1,467
Trwolff, do you have a 30 or 50 amp electrical system? And also do you have a EMS system?
Since it is late I will assume you have a 30 amp system with EMS. The EMS measures current on the neutral wire is the breaker box and that is what you see in the display and what the EMS uses to shed loads. When on shore power both the AC units are fed through the breaker panel. The front AC is fed directly from the breaker panel and the rear AC is fed from the breaker panel back through the transfer switch then to the rear AC.
When you run the generator one leg of the generator feeds the breaker panel and thus feeds the front AC. The other leg feeds the rear AC directly from the transfer switch and thus the current for that AC unit does not go through the neutral in the breaker box and will not show up in the EMS current display.
All that said you do not have a magical Onan or a problem!!
__________________
Grant & Pat
2014 Adventurer 35P
2021 Rapid Red 4dr Bronco OBX
grtharris is offline   Reply With Quote
Old 08-25-2015, 06:48 AM   #6
Winnebago Owner
 
Johndale's Avatar
 
Join Date: Sep 2013
Location: Ft Worth texas
Posts: 105
If you look at your electric panel you will see a switch and it will say rear ac. On it it will say gen or shore yours is set to gen mode and will not read on display. The 20 amp breaker supplies the power to only the rear ac unit. It took me awhile on this. So if you are on gen and switch is set to gen and have the rear on you can have more things running on the main unit. If your unit is like mine 5500 kW read the tag and it will tell you 45 amps. I hope this helps you.


Sent from my iPhone using iRV2 - RV Forum
__________________
2003 Sightseer 33L
Ford F53
Johndale is offline   Reply With Quote
Old 08-25-2015, 07:32 AM   #7
Winnebago Master
 
grtharris's Avatar
 
Join Date: Apr 2003
Location: Skiatook, OK
Posts: 1,467
Johndale, OP's coach is not wired like yours, his coach has a auto transfer switch.
__________________
Grant & Pat
2014 Adventurer 35P
2021 Rapid Red 4dr Bronco OBX
grtharris is offline   Reply With Quote
Old 08-25-2015, 01:37 PM   #8
Winnebago Watcher
 
Trwolff's Avatar
 
Join Date: Aug 2015
Posts: 3
Thanks, guys! You are 100% correct! I must admit, though, I was really hoping I had a magical Onan.....
Trwolff is offline   Reply With Quote
Old 08-25-2015, 04:12 PM   #9
Winnebago Master
 
wa8yxm's Avatar
 
Join Date: Mar 2009
Posts: 851
How are you measuring the amps? That will make a difference.
__________________
Home is where I park it!
[SIGPIC][/SIGPIC]
wa8yxm is offline   Reply With Quote
Old 08-25-2015, 05:24 PM   #10
Winnebago Owner
 
Johndale's Avatar
 
Join Date: Sep 2013
Location: Ft Worth texas
Posts: 105
Quote:
Originally Posted by grtharris View Post
Johndale, OP's coach is not wired like yours, his coach has a auto transfer switch.

And you think mine doesn't. It has ATS. So be carful on your corrections.


Sent from my iPhone using iRV2 - RV Forum
__________________
2003 Sightseer 33L
Ford F53
Johndale is offline   Reply With Quote
Old 08-25-2015, 07:30 PM   #11
Winnebago Camper
 
Join Date: Aug 2012
Posts: 28
A/C amps

Quote:
Originally Posted by Trwolff View Post
Ok, I'm an admitted newbie so I'm guessing one of you veterans will have an answer to this. I've got a 2005 Winnebago Voyage 38J with two A/C - heat pumps for HVAC. When on shore power and both units running, I pull 26 amps. However, when on generator and both units running, I'm only pulling 11 amps. My first thought was that the rear unit had tripped out and I was only running the front unit. Checked both the house and generator breakers and nothing had tripped. So I shut down both units and turned on just the rear unit. It was pulling just 3 amps, so I assumed it was just the fan blowing. However, in running it for a bit, it was blowing cold, so something was functioning. Turning the front unit back on, total amps jumped to 11, which is still way too low in my mind, but I'm getting cold air out of both units. Do I have a magical Onan or an A/C problem?

The only real way to determine if the compressors are running is to measure the voltage being applied to the actual compressor and measuring the current draw at the compressor. This requires taking the rooftop cover off and finding the wires.

It is not uncommon for only one to run when on generator. Often the generator is not sized to run both. With that said and was said above, they may be ducted together so one compressor cools everything with both fans running while on generator.

The other issue is depending on where your meter is detecting the current draw, it may not be accurate when on generator.

Every coach is wired differently. So without knowing the actual wiring, everything else is just a guess based on some experiences.


Sent from my iPad using iRV2 - RV Forum
TravellingRVDoctor, LLC
shiggs68 is offline   Reply With Quote
Old 08-25-2015, 07:45 PM   #12
Winnebago Master
 
grtharris's Avatar
 
Join Date: Apr 2003
Location: Skiatook, OK
Posts: 1,467
shiggs68, OP's AC units are running as designed. Read post #5.
__________________
Grant & Pat
2014 Adventurer 35P
2021 Rapid Red 4dr Bronco OBX
grtharris is offline   Reply With Quote
Old 08-25-2015, 07:49 PM   #13
Winnebago Master
 
grtharris's Avatar
 
Join Date: Apr 2003
Location: Skiatook, OK
Posts: 1,467
Johndale, sorry about that the drawings for your coach shows a plug box for the power cord to the generator.
__________________
Grant & Pat
2014 Adventurer 35P
2021 Rapid Red 4dr Bronco OBX
grtharris is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
RV is 50 amps, RV Park Spot is 30 amps jmraz73 Plumbing | Systems and Fixtures 30 01-06-2014 05:12 PM
Power Line One Panel Limits One Leg 50 Amp circuit to 30 Amps SteveG Electrical | Charging, Solar and Electronics 17 03-05-2008 04:43 PM
Convert watts to DC amps formula SteveG Electrical | Charging, Solar and Electronics 15 03-01-2008 07:26 PM
Basement A/C & 15 Amps? Pubtym Electrical | Charging, Solar and Electronics 29 07-17-2007 07:34 AM
Control Panel @ 50 AMPs John and Elaine Electrical | Charging, Solar and Electronics 12 10-15-2005 04:58 AM

» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Winnebago Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 10:32 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.