Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
 

Go Back   Winnebago Owners Online Community > WINNEBAGO TECH & TOW > Heating, Cooling and Appliances
Click Here to Login
Register FilesRegistry Blogs FAQ Community Calendar Today's Posts Log in

Reply
 
Thread Tools Search this Thread Display Modes
 
Old 09-02-2010, 08:17 AM   #41
Winnie-Wise
 
Thudman's Avatar
 
Join Date: Sep 2003
Location: Destin, FL
Posts: 494
Roadking; RVP told me they are going to make more basement units & the lead unit is at the UL facility for testing & approval. They estimate production by year's end. Caveat: Units MUST have 50 Amps (they also have R410 vs R22).

Thudman
__________________
03 Adventurer 38G, W22, 22.5 Whls

Koni FSD's, TracBar rear, SteerSafe, 50A SurgeGuard, Eternabond; 2012 Honda CRV EXL w/Nav & AWD
Thudman is offline   Reply With Quote
Old 09-02-2010, 08:45 AM   #42
Winnie-Wise
 
Thudman's Avatar
 
Join Date: Sep 2003
Location: Destin, FL
Posts: 494
Dan: Have been hassling with svc ctr (Tom Johnson, Marion, NC) for over three weeks. Parts finally on order, but next week they have a BBQ shindig so cannot sched me then. The good news is, it's cooling off, so one lung does reasonably well.

I'm upgrading the outside blower wheel to plastic and putting in two sealed bearings per Duner's FABULOUS post. Also check both systems' Freon. So I'll have two Schrader valves. Also R&R all (five?) Start Caps. I'll have to pay for the upgrades, Freon & Start Caps. For #1 compressor R&R, Good Sam CSP pays $1217 (of that I pay 500 ded).

Still waiting for appt to do it. As a side note, svc rep said fridge cannot be On, even elec mode. Never heard of that. LP mode, yes; but elec??? 'Nuther irritant

Will
__________________
03 Adventurer 38G, W22, 22.5 Whls

Koni FSD's, TracBar rear, SteerSafe, 50A SurgeGuard, Eternabond; 2012 Honda CRV EXL w/Nav & AWD
Thudman is offline   Reply With Quote
Old 09-02-2010, 10:41 AM   #43
Winnebago Owner
 
Join Date: Dec 2006
Location: Tx
Posts: 130
Roadking - I went and checked on my coach at my Winnie dealer, the new ac unit is in place and checked out.

The 4 in stock you refer to are 4 of the old "matching part number" units that they will not sell. Still don't know the part # of the new replacements yet.

One weird thing, the parts guy said he had to sign and fax back a letter to Winnie stating that "under no circumstances" would this unit be returned to Winnie. I said if it arrived DOA, it damn sure would be going back.
__________________
Rather be Ridin' than Rollin'
2003 UA 40E(wheelchair accessible)
McDuff is offline   Reply With Quote
Old 09-02-2010, 10:45 AM   #44
Winnebago Master
 
smlranger's Avatar
 
Join Date: Sep 2004
Location: Glen Allen, VA
Posts: 2,169
Some comfort to know that RVP will be producing new basement heat pumps, especially for those of us who have decided to keep our rigs.

I do wonder if they will be similar size and configuration so they can be retrofitted to the older rigs if replacement is necessary.
__________________
'07 Country Coach Allure 470 Siskiyou Summit #31578, Cummins ISL 425; 2014 Ford F150 toad; Air Force One Toad Brake.
Glen Allen, VA; Smith Mountain Lake, VA.
smlranger is offline   Reply With Quote
Old 09-02-2010, 10:48 AM   #45
Winnebago Owner
 
Join Date: Dec 2006
Location: Tx
Posts: 130
Smlranger - just had one "dropped in" in place on my 2003 UA.
__________________
Rather be Ridin' than Rollin'
2003 UA 40E(wheelchair accessible)
McDuff is offline   Reply With Quote
Old 09-02-2010, 05:05 PM   #46
Winnie-Wise
 
Thudman's Avatar
 
Join Date: Sep 2003
Location: Destin, FL
Posts: 494
New Unit P/N 46515-811, with R-410.

Thudman
__________________
03 Adventurer 38G, W22, 22.5 Whls

Koni FSD's, TracBar rear, SteerSafe, 50A SurgeGuard, Eternabond; 2012 Honda CRV EXL w/Nav & AWD
Thudman is offline   Reply With Quote
Old 09-02-2010, 07:00 PM   #47
Winnebago Master
 
smlranger's Avatar
 
Join Date: Sep 2004
Location: Glen Allen, VA
Posts: 2,169
Quote:
Originally Posted by McDuff View Post
Smlranger - just had one "dropped in" in place on my 2003 UA.
Outstanding. Give us a report on how well it works compared to the original unit before you had problems. What is the BTU rating of the new unit?
__________________
'07 Country Coach Allure 470 Siskiyou Summit #31578, Cummins ISL 425; 2014 Ford F150 toad; Air Force One Toad Brake.
Glen Allen, VA; Smith Mountain Lake, VA.
smlranger is offline   Reply With Quote
Old 09-03-2010, 04:56 PM   #48
Winnebago Owner
 
Join Date: Dec 2006
Location: Tx
Posts: 130
I will report back, still don't have my coach back yet. And I'm having a birthday pool party tomorrow, yea I made another year, so I haven't checked back in a few days. Wife as been on a tear getting the house ready.

Don't know the BTU's either, would be great if they dropped some 15K's in there. I'll add that to my report.

They were waiting on a new inverter, and a couple hydraulic hoses. When he pulled the ac, it was covered with hyd fluid. There are 2 little hoses that feed the BR slide and one of them had a bubble in it and was leaking. According to the tech, after talking to Winne, for 2 yrs only, mine in '03 and either one up or down, they outsourced these 2 hoses. The sub co. went belly up and now HWH is trying to mate up these lines.

Always something.
__________________
Rather be Ridin' than Rollin'
2003 UA 40E(wheelchair accessible)
McDuff is offline   Reply With Quote
Old 09-07-2010, 03:42 PM   #49
Winnie-Wise
 
edgray's Avatar
 
Join Date: Oct 2002
Location: Madison, MS
Posts: 450
Can someone please confirm the amp draw that should be displayed when running basement A/C on genset. I'm looking to know how many amps when only one compressor is in use and how many when both compressors are running simultaneously. THANKS, Ed
__________________
2016 EC Aspire 42RBQ / 2014 CR-V
edgray is offline   Reply With Quote
Old 09-07-2010, 06:35 PM   #50
Winnebago Camper
 
Whaler's Avatar
 
Join Date: Jul 2006
Location: SE PA
Posts: 43
Last week I was down in Assateague MD,and it was pretty hot.So I ran my genny.As I recall,when the A/C first came on,I would see a 34 or so flash,then it would go down to about 24/22,then eventually drop to about 14/12 when the coach had cooled down.
__________________
'09 Winnebago Adventurer 32H

Workhorse W-22, UltraPower,496 cubic inches of
Whaler is offline   Reply With Quote
Old 09-07-2010, 06:56 PM   #51
Winnie-Wise
 
azloafer's Avatar
 
Join Date: Oct 2009
Posts: 277
Quote:
Originally Posted by edgray View Post
Can someone please confirm the amp draw that should be displayed when running basement A/C on genset. I'm looking to know how many amps when only one compressor is in use and how many when both compressors are running simultaneously. THANKS, Ed
I put the generator on and the Basement Air at high cool. It was drawing 22 amps. Then I put the new rooftop Coleman Mach 13,500 on at high cool and the One Place Panel showed a total amp use of 35. I turned the TV on and the panel read-out didn't change. Adding the microwave the amp meter read 48. Joe
__________________
2008 Itasca Latitude 39W. Cummins ISB 6.7 Turbo 340HP. Allison 6 Speed. Freightliner XCS. Michelin XRV 255/80R 22.5 LRG. SuperSteer MCU. Safe-T-Plus.
azloafer is offline   Reply With Quote
Old 09-07-2010, 09:01 PM   #52
Winnie-Wise
 
edgray's Avatar
 
Join Date: Oct 2002
Location: Madison, MS
Posts: 450
Thanks for the answers so far. What I'm trying to determine is if one or both compressors are running. I have the T-stat set for a temp greater than 15 degrees below the displayed room temp. I was told was more than enough to call for both compressors to be on together. I'm only seeing 18-19 amps running (after start surge), which has me questioning if the second compressor is coming on. Do you know of any other way to tell if there is one or two running? THANKS, Ed
__________________
2016 EC Aspire 42RBQ / 2014 CR-V
edgray is offline   Reply With Quote
Old 09-07-2010, 09:12 PM   #53
Winnebago Owner
 
Fossilhog's Avatar
 
Join Date: Feb 2006
Location: Howell, New Jersey
Posts: 165
Send a message via AIM to Fossilhog
Quote:
Originally Posted by edgray View Post
Can someone please confirm the amp draw that should be displayed when running basement A/C on genset. I'm looking to know how many amps when only one compressor is in use and how many when both compressors are running simultaneously. THANKS, Ed
Ed, not sure how you're wired but in my unit, there's a dedicated 20 amp circuit breaker on the generator that goes right to the AC. When it's running I get 14-15 amps reading but I can hear when the second compressor kicks in and there's no additional reading on the amp guage. On shore power I read 26-28 with both compressors running.
__________________
Tim ,Retired Police Lt. 2002 Winnebago Adventurer+16' Trailer
Harley Road King and Heritage Classic+,Trik-L-start,Hughes Autoformer. Blue Tick Coon hound
Fossilhog is offline   Reply With Quote
Old 09-07-2010, 09:30 PM   #54
Winnie-Wise
 
edgray's Avatar
 
Join Date: Oct 2002
Location: Madison, MS
Posts: 450
Quote:
Originally Posted by Fossilhog View Post
Ed, not sure how you're wired but in my unit, there's a dedicated 20 amp circuit breaker on the generator that goes right to the AC. When it's running I get 14-15 amps reading but I can hear when the second compressor kicks in and there's no additional reading on the amp guage. On shore power I read 26-28 with both compressors running.
When I'm plugged in to 50 amp shore power, the display won't show amps being used at all, it remains blank. When plugged in to 30 amps, I'm "assuming" it won't allow both compressors to run at the same time, but I'll try that tomorrow. I've been wrong once before.
Ed
__________________
2016 EC Aspire 42RBQ / 2014 CR-V
edgray is offline   Reply With Quote
Old 09-07-2010, 09:36 PM   #55
Winnie-Wise
 
Sammie's Avatar
 
Join Date: Jun 2006
Location: Southern California
Posts: 489
Quote:
Originally Posted by edgray View Post
When I'm plugged in to 50 amp shore power, the display won't show amps being used at all, it remains blank. When plugged in to 30 amps, I'm "assuming" it won't allow both compressors to run at the same time, but I'll try that tomorrow. I've been wrong once before.
Ed
Ed, I have a 30amp outlet at my house that is strictly for my motorhome. When I turn on the air conditioner the display will read 14 to 16 amps for a couple of minutes until the second compressor kicks in, then it will read from 22 to 24 amps.

Sammie
__________________
2015 Tiffin Bus 37AP
2016 Ford Explorer
"A Job Begun is Half Done"
Sammie is offline   Reply With Quote
Old 09-08-2010, 07:45 AM   #56
Winnebago Owner
 
Fossilhog's Avatar
 
Join Date: Feb 2006
Location: Howell, New Jersey
Posts: 165
Send a message via AIM to Fossilhog
Quote:
Originally Posted by edgray View Post
When I'm plugged in to 50 amp shore power, the display won't show amps being used at all, it remains blank. When plugged in to 30 amps, I'm "assuming" it won't allow both compressors to run at the same time, but I'll try that tomorrow. I've been wrong once before.
Ed
That sure doesn't sound right at all.....no amps shown.
__________________
Tim ,Retired Police Lt. 2002 Winnebago Adventurer+16' Trailer
Harley Road King and Heritage Classic+,Trik-L-start,Hughes Autoformer. Blue Tick Coon hound
Fossilhog is offline   Reply With Quote
Old 09-08-2010, 08:09 AM   #57
Winnie-Wise
 
azloafer's Avatar
 
Join Date: Oct 2009
Posts: 277
Quote:
Originally Posted by Fossilhog View Post
That sure doesn't sound right at all.....no amps shown.
When on shore power the amps do not show on Winnebago/Itasca products. It only has a readout on generator. Joe
__________________
2008 Itasca Latitude 39W. Cummins ISB 6.7 Turbo 340HP. Allison 6 Speed. Freightliner XCS. Michelin XRV 255/80R 22.5 LRG. SuperSteer MCU. Safe-T-Plus.
azloafer is offline   Reply With Quote
Old 09-08-2010, 08:23 AM   #58
Winnebago Owner
 
Fossilhog's Avatar
 
Join Date: Feb 2006
Location: Howell, New Jersey
Posts: 165
Send a message via AIM to Fossilhog
Quote:
Originally Posted by azloafer View Post
When on shore power the amps do not show on Winnebago/Itasca products. It only has a readout on generator. Joe
Does that only pertain to 50 amp coaches? My Adventurer is a 30 amp unit and I get readouts on my ems panel of anything on the 30 amp side of the generator when running. Only the 2nd compressor doesn't show because its on the 20 amp side.
__________________
Tim ,Retired Police Lt. 2002 Winnebago Adventurer+16' Trailer
Harley Road King and Heritage Classic+,Trik-L-start,Hughes Autoformer. Blue Tick Coon hound
Fossilhog is offline   Reply With Quote
Old 09-08-2010, 08:53 AM   #59
Winnie-Wise
 
edgray's Avatar
 
Join Date: Oct 2002
Location: Madison, MS
Posts: 450
Quote:
Originally Posted by Fossilhog View Post
Does that only pertain to 50 amp coaches? My Adventurer is a 30 amp unit and I get readouts on my ems panel of anything on the 30 amp side of the generator when running. Only the 2nd compressor doesn't show because its on the 20 amp side.
Yes, I think that is correct. Apparently they believe if that you are on a 50 amp 4 wire service, you have no need to know what the load is because you "can't" consume more than is available. I think it would be nice if it would read the amp draw even while on 50, but it does not.

I'm now plugged into my 30 amp 3 wire service at home and it alternately shows 1 or 2 amps with nothing "on" except the converter. When the T-stat is set for 2 degrees below the displayed room temp, the A/C comes on and the display shows 12 amps. Turning the T-stat down to 20 degrees below the room temp caused the A/C to make a slight noise (I assume 2nd compressor kicked in) and the amps went up to 17.

Unfortunately, if in fact both compressors are running, then I must have another problem because the A/C is not cooling the coach satisfactorily. Ed
__________________
2016 EC Aspire 42RBQ / 2014 CR-V
edgray is offline   Reply With Quote
Old 09-08-2010, 09:01 AM   #60
Winnebago Owner
 
Fossilhog's Avatar
 
Join Date: Feb 2006
Location: Howell, New Jersey
Posts: 165
Send a message via AIM to Fossilhog
Quote:
Originally Posted by edgray View Post
Yes, I think that is correct. Apparently they believe if that you are on a 50 amp 4 wire service, you have no need to know what the load is because you "can't" consume more than is available. I think it would be nice if it would read the amp draw even while on 50, but it does not.

I'm now plugged into my 30 amp 3 wire service at home and it alternately shows 1 or 2 amps with nothing "on" except the converter. When the T-stat is set for 2 degrees below the displayed room temp, the A/C comes on and the display shows 12 amps. Turning the T-stat down to 20 degrees below the room temp caused the A/C to make a slight noise (I assume 2nd compressor kicked in) and the amps went up to 17.

Unfortunately, if in fact both compressors are running, then I must have another problem because the A/C is not cooling the coach satisfactorily. Ed
Ed can you turn off the circuit breaker for #2 and see a change in the reading? 17 seems awful low for 2 comps. running.
__________________
Tim ,Retired Police Lt. 2002 Winnebago Adventurer+16' Trailer
Harley Road King and Heritage Classic+,Trik-L-start,Hughes Autoformer. Blue Tick Coon hound
Fossilhog is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
If you have not replaced your Hot Water Heater check valves, read this. LK23 Plumbing | Systems and Fixtures 28 05-07-2010 12:51 PM
Should Have Read The Manuals First Wayne M Winnebago General Discussions 16 08-24-2008 06:48 PM
Those pesky glass cabinet door clips.. SCVJeff General Maintenance and Repair 17 10-19-2007 05:04 PM
SCS/Frigette keyless entry system weirdness - if you have this, please read! John_Canfield General Maintenance and Repair 7 06-04-2005 03:19 PM
Where do you store those dining chairs while mobile? John_Canfield Winnebago General Discussions 16 05-30-2005 09:44 AM

» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Winnebago Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 10:57 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.