I bought a 10,000 btu Hisense portable AC unit that was rated at 10 amp. I was hoping to just cool the front or the bedroom of my Itasca while hooked to a friends household 20 amp outdoor receptacle. 1 melted gfi outlet later I'm a little wiser and warmer. Don't make my $400.mistake. I was also hoping to take some of the work off of the basement air when hooked to 30 amp. Oh, well. an expen$ive lesson.
Idiotasca is offline   Reply With Quote
Old 07-13-2018, 04:41 PM   #2
Winnebago Owner
 
Join Date: Dec 2007
Posts: 172
Quote:
Originally Posted by Idiotasca View Post
I bought a 10,000 btu Hisense portable AC unit that was rated at 10 amp. I was hoping to just cool the front or the bedroom of my Itasca while hooked to a friends household 20 amp outdoor receptacle. 1 melted gfi outlet later I'm a little wiser and warmer. Don't make my $400.mistake. I was also hoping to take some of the work off of the basement air when hooked to 30 amp. Oh, well. an expen$ive lesson.
As long as all the connections from the house c/b through the outdoor receptacle into the RV are in good shape and the wiring is the correct size to handle the current and length of wire, the 10,000 btu A/C should work just fine. Of course there can't be anything else in the RV operating on 120V AC. Basement air, microwave, water heater operating on elect, etc.
__________________
Al & Sharon
2006 Winnebago Sightseer 29R. Chevy Colorado (Toad)
2006 Winnebago Journey 36G (Not in use yet)
al1florida is offline   Reply With Quote
Old 07-13-2018, 05:59 PM   #3
Winnebago Camper
 
Join Date: Dec 2017
Posts: 9
Unhappy Portable AC

I made sure everything was turned off except for the refrigerator and a small fan,water heater was turned off, no microwave use. AC unit ran for about five minutes and then melted the outlet I don't know what else I can do except learn from it.
Idiotasca is offline   Reply With Quote
Old 07-13-2018, 06:12 PM   #4
Winnie-Wise
 
powercat_ras's Avatar
 
Join Date: May 2015
Location: Manhattan, Kansas USA
Posts: 320
The National Electric Code says that there should not be more than a 5 % drop between zero load and full load at any outlet, so for a 15 Amp Outlet that's 6 volts. If there is more than this than there is a bad connection somewhere that can overheat and destroy something. Like what happened to you, like what happens to people who report destroyed breakers, destroyed wire ends, and destroyed transfer switches due to bad connections.

For reference a properly made and maintained RV with no loose AC connections like my Winnebago Vista 27N will never see a voltage drop over 3 volts between no load and 15 amp load on any outlet.

You can self-test to see if an outlet can handle a heavy load so you can get a bad connection fixed before any damage is done ...

Get a Kill-A-Watt power monitor / analyzer, Menards sells them for $ 22. You can use this to confirm that any outlet in your RV and all of it's wiring feeding up to that outlet can handle a heavy load as follows:

1. Turn off other loads as possible. If another heavy load in the RV like AC changes from on/off or from off/on during your testing it will invalidate the result.

1. Plug the Kill-A-Watt into the outlet you want to validate.

2. Display and note the no-load AC volts.

3. Plug in your load, and turn it on

5. Display and note the load AC volts.

6. Display and note the load AC amps.

7. Turn off the load.

First of all the change in voltage should be well under 5 % or under 6 volts. In a RV we really want it to be 3 volts or less given the distances and number of devices in series.

The amount of loss turning into heat is the formula:
(No load AC volts - Load AC volts) * AC Amps.

For example if you are using a 10 amp load and voltage drops 3 volts, there is 30 watts of power turning into heat. That heat is distributed everywhere along the AC current path.

You can try this same test with the same load on all your different breaker fed circuits and different outlets, and if any have a much higher voltage drop than that's a red flag that there is a bad connection.

You can use a "gun" type infrared thermometer to find the bad connection that is heating but its a balancing act for how long to leave the load on to generate the heat so you can see it with the gun vs. leaving it on too long and damage occurs.

I use a Soleus Air 8,000 BTU Portable Air Conditioner in my Vista 27N, and it also happens to be plugged into an outlet that is fed thru another GFCI outlet and it works great, with nothing overheating. So it can be and is being done.
__________________
Randy - Manhattan, Kansas
2015 Vista 27N
2016 Honda HR-V
powercat_ras is offline   Reply With Quote
Old 07-14-2018, 03:58 AM   #5
Winnebago Camper
 
Join Date: Sep 2017
Location: Indiana
Posts: 29
Be sure to use a 12 gauge extension cord. Most cords sold are not heavy enough. That will help with the voltage drop.
__________________
2015 Winnebago 36 M Journey
2013 Wrangler Unlimited-Blue ox base plate-Demco bar
Airforce One brake
vanmark is offline   Reply With Quote
Old 07-14-2018, 07:25 AM   #6
Winnebago Owner
 
Join Date: Jan 2018
Posts: 125
Our old trailer had a 9K wall unit A/C and I ran it from a 15A circuit at home for a number of years. I did use a 12 ga extension cord. If the fridge was on electric that could have overloaded the circuit but a breaker should have popped for the 20A outlet. I would run the fridge on gas when hooked to the smaller circuit. Sounds like there is an electrical problem with the circuit you plugged into.


One other thing comes to mind and that pertains to the GFCI outlet. I had one fry due to a nearby lighting ground strike. I couldn't tell until I went to use it one day. It was stuck between on and tripped and started smoking due to the partial trip. I unplugged very quickly and killed the breaker until I could get a new outlet. My guess is it could have melted if I wasn't there see it happening.
__________________
2018 Micro Minnie 2106FBS
2015 F-150 XLT Ecoboost
old_engineer is online now   Reply With Quote
Old 07-15-2018, 05:27 AM   #7
Winnebago Owner
 
Join Date: Dec 2007
Posts: 172
Quote:
Originally Posted by Idiotasca View Post
I made sure everything was turned off except for the refrigerator and a small fan,water heater was turned off, no microwave use. AC unit ran for about five minutes and then melted the outlet I don't know what else I can do except learn from it.
Something had a poor or bad connection in or at the outlet that melted. If all connections at the outlet were truly in good condition, then there was some other significant 120V load left on in the RV.

I doubt there is any way to examine the melted outlet to see what the cause was.

To test, install a new outlet, clean up or replace the connector on the end of the cord that was plugged into the outlet and test again.

Bottom line, a 10-12 amp load on 15 or 20 amp outlet will not cause a problem. It is just that simple.

It is common practice for people in houses or RV's to plug a small 1500 watt space heater into 15amp outlets all the time without causing a problem. Other than momentary starting current for the air conditioner compressor the A/C doesn't pull any more current than the small space heater.
__________________
Al & Sharon
2006 Winnebago Sightseer 29R. Chevy Colorado (Toad)
2006 Winnebago Journey 36G (Not in use yet)
al1florida is offline   Reply With Quote
Old 07-15-2018, 05:52 AM   #8
Winnebago Owner
 
Podivin's Avatar
 
Join Date: Dec 2015
Location: Jacksonville, Fl
Posts: 70
I agree with the others. Anything that will work plugged in to a sticks and bricks house will also work plugged in to an RV - it's the same electricity, it has to work.
So there was some other issue preventing that from working in your RV. Some other heavy draw appliance else was running, a bad power cord, a bad connection - something.
Rather than giving up on the portable AC as a bad idea find what the problem is and correct it.
__________________
2013 Winnebago Sightseer 36V
Podivin is offline   Reply With Quote
Old 07-15-2018, 08:07 AM   #9
Winnebago Owner
 
Join Date: Jan 2018
Posts: 125
If it was excess power draw from the RV it should have tripped a circuit breaker in the house electrical box. Something was wrong with that circuit. As it is an outdoor outlet I wouldn't be surprised that they used a GFCI breaker in the electrical box and that it was bad.
__________________
2018 Micro Minnie 2106FBS
2015 F-150 XLT Ecoboost
old_engineer is online now   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Touch Lamp Won't work off Inverter BBBEEBOP Electrical | Charging, Solar and Electronics 6 09-02-2011 07:43 AM
slides & jacks won't work Big Ben General Maintenance and Repair 10 08-23-2010 10:00 AM
refrigerator won't work on LP when using inverter tofran Heating, Cooling and Appliances 9 06-30-2008 09:16 AM
Slides on 92 Winnebago won't work Woof General Maintenance and Repair 7 04-11-2008 09:20 AM
Both of my TV's won't work. Gary N. Tech | Toys and Gear 10 06-21-2006 08:12 AM

» Featured Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 09:34 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2018, vBulletin Solutions, Inc.