Lightbulb Basement AC Compressor #2 overamps blows breaker

2005 Itasca Horizon 40FD basement unit. The AC never seemed to cool enough and I now know why. When activated Compressor#1 comes on and runs just fine, seconds later Compressor#2 activates and the EMS ampmeter shows amperage at 65 or greater and then the Comp#2 breaker trips. Any ideas where to look to repair. Thanks in advance for any wisdom and suggestions.
jeffro is offline   Reply With Quote
Old 06-30-2013, 11:04 AM   #2
Winnebago Camper
 
Join Date: Jul 2010
Location: Daphne,Al
Posts: 37
Most likely cause is the #2 compressor is locked up. This would explain the high amps and breaker trip.
__________________
2006 Itasca Suncruiser 38T
Traveling with Westies, Max, Ellie and new addition Sophie.
bobbyl is offline   Reply With Quote
Old 06-30-2013, 04:39 PM   #3
Winnie-Wise
 
Harry B's Avatar
 
Join Date: May 2006
Location: Central Florida
Posts: 358
I had the same thing. Turned out it was a bad exhaust fan motor (Higjh speed winding) as it goes into high speed mode with both compressors on. As mentioned it could also be a locked or shorted compressor. In either of these cases the unit has to be pulled to repair it. Not fun
__________________
Harry
2015 Tuscany 40 KQ
2013 Honda CR-V
Harry B is offline   Reply With Quote
Old 07-01-2013, 09:48 AM   #4
Winnebago Master
 
DancinCampers's Avatar
 
Join Date: Nov 2004
Location: On the Road Westward
Posts: 711
Check the #2 compressor start capacitor, especially the attached little black square PTCR device attached on top. Start cap should be black and round.

Don't let the compressor try to start for any long length of time, as internal overload device could be damaged.
__________________
Dan & Sharon & Kasey (Our Yorkie Puppy (12 Yrs Old) On the Road (2012 Journey 36M, 2006 Jeep Liberty)
USN-Ret ('65-'93) Fulltimers, Class of 2012
DancinCampers is offline   Reply With Quote
Old 07-01-2013, 04:35 PM   #5
Winnebago Watcher
 
Join Date: Jul 2010
Posts: 4
Thanks

Thanks for the advice from everyone. Local shop says caps are ok. Seems we may be looking at locked up compressor (?) Anything internal needing repair is not easy on these basement units. I'll let you know what we find.
jeffro is offline   Reply With Quote
Old 07-01-2013, 07:45 PM   #6
Winnie-Wise
 
Harry B's Avatar
 
Join Date: May 2006
Location: Central Florida
Posts: 358
They are straight forward to work on once they are out. Most of the labor is in removing and reinstalling the unit. Fork lift is the key to making it easier. You also might consider replacing the squirel cage on the exhaust fan while you are in there. They do get squeaky. my AC got quite a bit quieter with the new cage. Good luck
__________________
Harry
2015 Tuscany 40 KQ
2013 Honda CR-V
Harry B is offline   Reply With Quote
Old 07-03-2013, 12:17 PM   #7
Winnebago Owner
 
pameridan04's Avatar
 
Join Date: Oct 2007
Location: Allentown, PA
Posts: 230
Same thing happened to my#2 , Exhaust Fan Motor also.

PAM4
__________________
Meridian 2004 36G DP
2010 Jeep Sahara Unlimited
Two HD's for company
pameridan04 is offline   Reply With Quote
Old 07-10-2013, 03:00 PM   #8
Winnebago Master
 
Duner's Avatar
 
Join Date: Jul 2002
Location: Camarillo, CA
Posts: 548
Back in 2008 my basement A/C outdoor blower bearing went out. I replaced it myself and documented the procedure. Many members on the forum have used my write-up to successfully do their own repairs. It's pretty straightforward and you don't have to be an a/c wizz. Also if you read it you will get some tips that you can have a repair tech look at if you decide to pay a guy to do the work.

Here's a link to download A/C Removal Procedure.

All the Coleman basement units use a brass bearing on both the indoor and outdoor blowers that wear out if they are not lubed with a few drops of oil every year. Of course nobody does that because it's too muchof a PITA and there's nothing in the manual to tell you it's needed. On the roof a/c units (which use the very same brass bearing), Coleman manual says maintenance requirement to oil these guys once a year. In my procedure, I have the part number of a sealed ball bearing replacement that will last a lifetime.

The other common problem is with the metal squirrel cage fatiguing over time and they will get noisy, start to wobble and crack. It is well worth the money to use the new composite plastic squirrel cage......unit is much quieter and draws about 1 amp less power.

Good luck,
Bill
__________________
Bill & Helen, Last of the Chieftains, 2004 39T, W22, UltraPower, Banks Headers, Koni's, Safe-T-Plus, SMI Stay-n-Play, 2017 Lincoln MKZ Hybrid towed 4-down
https://www.winnieowners.com/forums/...-picture97.jpg
Duner is offline   Reply With Quote
Old 07-10-2013, 03:07 PM   #9
Winnie-Wise
 
UFO Pilot's Avatar
 
Join Date: Aug 2007
Location: Sonoma County, CA
Posts: 429
My over amperage problem was due to bad starting capacitors for the fans. The fans come on before the compressors engage and if the fans don't start the compressors won't run. That is the way the RV repair man explained it to me. When you remove the outside AC cover there is a small "door" in the upper left side. The "door" has 3 or 4 screws holding it on. Removing the "door" will get you to the starting capacitors.
__________________
Wayne & Roberta and Maggie the Miracle Dog
08 Winnebago Destination 39W Gas UFO Workhorse Chassis
Making the Journey in our Destination

UFO Pilot is offline   Reply With Quote
Old 07-10-2013, 03:51 PM   #10
Winnebago Camper
 
Jimooo's Avatar
 
Join Date: Jun 2011
Location: Amite, La.
Posts: 33
Could be start cap not enough energy to start compressor , the fans should start after compressors start up from delay switch.

You can OHM that compressor out to see if windings are shorted just to be sure before you go any further .

Good luck,

James
Jimooo is offline   Reply With Quote
Old 07-10-2013, 04:02 PM   #11
Winnebago Master
 
Join Date: Dec 2005
Location: Buxton, North Dakota
Posts: 1,037
Both 30 amp and 50 amp are single phase. With the 50 to 30 amp converter the two legs of a 50 amp circuit are put on one leg plus the neutral, giving the hot side twice the wire capacity compared to the neutral. When hooked up to 50 amp you are pulling from L1 and L2 and using the common neutral.

Since the currents ‘flow’ in opposite directions we subtract to get the net current flowing in the Neutral. If L1 and L2 loads are exactly the same the Neutral current will be Zero. In fact when the loads are assigned electricians try to balance the load on Line 1 and Line 2 so that the neither leg is overloaded, the result of this is that the Neutral current should be about zero in a well designed system.

With the converter there shouldn't be a problem because it is properly sized for 30 amps, but it does carry more current then when connected to a 50 amp circuit.
__________________
2003 Winnebago Adventurer 38G F53/ V10 605 watts of Solar
1999 Winnebago Brave 35C Handicap Equipped
F53/V10
1999 Jeep Cherokee & 1991 Jeep Wrangler Renegade
John Hilley is offline   Reply With Quote
Old 07-11-2013, 02:20 PM   #12
Winnie-Wise
 
ChasA's Avatar
 
Join Date: Mar 2007
Location: Apex, NC
Posts: 449
John Hilley, the part about the 50 to 30 amp adapter connecting L1 and L2 together is wrong. If it did that it would be a dead short and trip the pedestal breaker as soon as power is applied. The adapter just connects one of the input lines to the output.
__________________
2010 Winnebago Journey Express 34Y
2010 Freightliner XCS (mfd 9/'09)
'07 Saturn Vue V6
ChasA is offline   Reply With Quote
Old 07-11-2013, 03:36 PM   #13
Winnebago Master
 
Join Date: Dec 2005
Location: Buxton, North Dakota
Posts: 1,037
No it is not wrong. The RV load center is not a 240 vac load center, but two 120 vac in parallel each with it's own main breaker.
__________________
2003 Winnebago Adventurer 38G F53/ V10 605 watts of Solar
1999 Winnebago Brave 35C Handicap Equipped
F53/V10
1999 Jeep Cherokee & 1991 Jeep Wrangler Renegade
John Hilley is offline   Reply With Quote
Old 07-15-2013, 08:35 PM   #14
Winnie-Wise
 
ChasA's Avatar
 
Join Date: Mar 2007
Location: Apex, NC
Posts: 449
Sorry John but it is wrong. You cannot connect the 2 50 amp lines to one wire, it will blow the breaker. It has nothing to do with what you are powering. The fact is that a 50 amp pedestal supplies 2 120 volt 50 amp lines that are 180º out of phase, and if you measure volts between the 2 hot lines, it will be 240 volts. The RV does not use the hot lines in this manner. It uses the hot lines separately, creating 2 separate 50 amp 120 volt circuits. Circuit 1 loads will be connected to line 1 and the common neutral, circuit 2 will be connected to line 2 and the common neutral.
__________________
2010 Winnebago Journey Express 34Y
2010 Freightliner XCS (mfd 9/'09)
'07 Saturn Vue V6
ChasA is offline   Reply With Quote
Old 07-15-2013, 09:46 PM   #15
Winnebago Master
 
Join Date: Dec 2005
Location: Buxton, North Dakota
Posts: 1,037
Quote:
Originally Posted by ChasA View Post
Sorry John but it is wrong. You cannot connect the 2 50 amp lines to one wire, it will blow the breaker. It has nothing to do with what you are powering. The fact is that a 50 amp pedestal supplies 2 120 volt 50 amp lines that are 180º out of phase, and if you measure volts between the 2 hot lines, it will be 240 volts. The RV does not use the hot lines in this manner. It uses the hot lines separately, creating 2 separate 50 amp 120 volt circuits. Circuit 1 loads will be connected to line 1 and the common neutral, circuit 2 will be connected to line 2 and the common neutral.
Reread what I posted above. The adapter takes 120 VAC circuit 1 and 120 VAC circuit 2 and connects them in parallel to the 120 VAC 30 AMP receptacle on the pedestal. What was 100 amps of capacity in the RV Load Center is reduced to 30 amps. No shorts, just two 120 VAC, 50 amp circuits bridged and plugged into a another 120 VAC circuit. There isn't 240 VAC any place in this configuration.
__________________
2003 Winnebago Adventurer 38G F53/ V10 605 watts of Solar
1999 Winnebago Brave 35C Handicap Equipped
F53/V10
1999 Jeep Cherokee & 1991 Jeep Wrangler Renegade
John Hilley is offline   Reply With Quote
Old 07-15-2013, 09:56 PM   #16
Winnebago Master
 
Join Date: Dec 2005
Location: Buxton, North Dakota
Posts: 1,037
ChasA, I think we are talking about opposite pigtails. I am talking about a 30 amp male plug to a 50 amp female receptacle. This feeds 120 VAC to each of the two 120 VAC sides of the load center sharing 30 amps. I think you are talking about a 50 amp male plug to a 30 amp female receptacle.
__________________
2003 Winnebago Adventurer 38G F53/ V10 605 watts of Solar
1999 Winnebago Brave 35C Handicap Equipped
F53/V10
1999 Jeep Cherokee & 1991 Jeep Wrangler Renegade
John Hilley is offline   Reply With Quote
Old 07-16-2013, 05:43 AM   #17
Winnie-Wise
 
ChasA's Avatar
 
Join Date: Mar 2007
Location: Apex, NC
Posts: 449
John Hilley, you are right, I was talking about 50 amp male to 30 amp female. I tend to describe adapters in terms of source to load. I would call the adapter you're talking about a 30 amp to 50 amp adapter. Glad we got that cleared up.
__________________
2010 Winnebago Journey Express 34Y
2010 Freightliner XCS (mfd 9/'09)
'07 Saturn Vue V6
ChasA is offline   Reply With Quote
Reply

Tags
compressor


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
2003 Journey second a/c compressor trips breaker Kelm130 Winnebago Class A Motorhomes 10 08-22-2014 06:07 AM

» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Winnebago Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 11:35 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.