Rear A/C Loses Power on Generator in 1999 Adventurer 35C

Thread Summary

Summarized on:
Original Member Title: The rear A/C shuts off on generator. 1999 Adventurer 35C
This AI-generated summary may contain inaccuracies. Please refer to the full thread for complete details.
A member with a 1999 Adventurer 35C reported that the rear A/C worked on 30-amp shore power but lost 120V power when running on the generator, while the front A/C continued to work. Members reviewed the many possible Winnebago wiring layouts, asked about breaker count, shore cord type, generator model, voltage checks, and noted that a 30-amp coach with two A/C units relies on load management and may shed the rear A/C under heavier loads.

Testing showed the power management system behaved...
More...
My rear AC Unit would not run on Generator, okay on shore power. Turned out to be a bad relay.

Replaced the Switch with Go Power 30A. Now both AC units work fine, but the Power Monitor is reading way low. AC unit should be 14 amps but it shows 2 amps. Turn on second AC and it's 4 amps. Both AC's and Microwave is 9 amps.

Could it be a bad connection coming out of the Switch?
 
Found the problem. On one side of the connection of Output to Panel it reading 24 amps and on the outher side 2.4 amps, which is what is being displayed. I will fix that and all should be fine.
 
What you hear clicking is the 12v system that controls the unit. 120v only runs the compressor. You will find somewhere in the camper or in the Power Management, that the load is being "managed". It will not allow you to run to high of a load. I have one of these load management boxes under my sink behind a small wall. My camper is 30 amp and I have a 4000 watts generator. Your bigger generator might run it but the management system is not allowing it.
 
I realized I was late to the party, sorry. But also I don't think the AC wires are supposed to go directly to the AC units if that is what you mean. You also mentioned plugging into shore power caused the transfer switch to shut off the generator. This is opposite of any transfer switch I have dealt with. The generator always takes precedence when it starts, after a delay.
 