This vintage of Norcold has a set of cooling plates, one set in the back freezer wall, and one set behind the cooling fins in the refer. In the back through the access door, there are coils meant to transfer heat into the air and be exhausted out the top of the chamber. There is no air path from the refer compartment to the freezer compartment. The coolant flow goes to the freezer first, the refer compartment second.
The fans in the back access chamber really need to be working to get that hot air out. As you have found out. And it doesn't hurt to have an internal fan of some sort inside the refer compartment to move the cool air around for more uniform temps in the compartment.
Just for info purposes, after 16 years of full-time constant use on my Norcold box, my problem seems to be door seals and hinges. I say box, because we replaced the Norcold cooling unit with a JC Refrigeration compressor cooling unit nearly 7 years ago. Even with the bad door seals and hinges it does a great job keeping things cold, in all but the hottest temperatures. We have been in 100+ temps most of the summer, and refer temps vary in the 38–40-degree range. Last night, we had a cool night, down into the 70's. I noticed this morning the refer cooling fins were down to 32 degrees, hooray, hadn't seen that in months.