Finding GFCI Outlets in a 2015 Vista 30T

mthawsh

Member
Joined
Feb 10, 2014
Posts
17
I have a 2015 Vista 30T. We had two heaters plugged in and blew a circuit affecting 1/2 our A/C outlets. All fuses are good and we reset all breakers. We can only locate one GFI outlet (bottom of cabinet near fridge) and it is good. We can't locate another and have been told there are always at least 2. Does anyone know where the other may be?
 
Rarely safe to fully trust what folks tell you!
don't think I have ever owned an Rv with two GFCI!
And for actually looking at what your RV has, there are several kinks in that plan as there are both early and late year builds as well as 50 and 30 amp electrical in the 2015 Vista 30T !
So possibly the more direct way to get you back in shape is to let you look at these drawings to find the correct one to match your RV?
If not used to using this sort of drawing, one way to go is finding the outlets that are bad and then tracing the route back to the load center/breakers much like a road map.
 
I would look around the bathroom area for another GFCI. My past and present RV's have always had two, one for the kitchen area and the other for the bathroom area. If you have an outlet in one of your bays it may be there, or if you have an outside kitchen look there.
Good Luck
 
The thing about RV is how much difference there is between them!
In this question, the codes will require outside, bath, and galley where one is likely to be in contact with ground to all be GFCI protected. But since there are potentially several different builds of this year Vista 30T, it get hard to guess which drawing is correct.
If they have the early build , this drawing may be correct and it only has one GFCI to protect five different outlets in those three spaces!
gfci.jpg

Part of the question on how many outlets is often how large the RV as well as how the bath and kitchen are laid out. Since GFCI outlets are a pretty cheap item, running wires and adding them in different locations can often save money over fitting it in so one can do the job.
That left me with too many questions on whether the OP has a 30 or 50 amp, early or late year build!
And there is always the question of whether it is actually a GFCI tripped. Just too many questions to give a firm answer. One question might be why plugging a heater in would trip the GFCI as it is not meant for that? It can happen but it might be good to check what is actually happening as it can be smaller issues like a bad cord on the heater!
Or it may be as simple as the breaker tripped when they had the frig running, the coffee perking and the wife drying her hair. The breaker might trip as those are all on the same circuit, so they go fix the breaker and go back to what they were doing to trip it again. Easy to miss that the breaker you just fixed is needing fixed again!

But the devil really is in the details!
 
Last edited:
Okay, setting here waiting for folks to get to a jobsite, so I took a deeper dive for info.
I found an earlier pos thwere the RV was ID as late build, so this drawing is more likely correct as I beleive they are also a 50 amp RV!
It does still look like a single GFCI for the three locations but there is a step to check whether it might be a breaker tripped or GFCI as two possible problems!
A gfci2.jpg
I numbered the one at the sofa as 1 and the rest 2-7 for ease of speaking about them.
If you find the sofa outlet dead as well as the rest, it points back toward the breaker as they are both dead when it trips.
But if that sofa outlet is good but the rest 2-7 bad, then it loks more like a GFCI trip?
But I do only find one protecting exterior, galley, and bath outlets!
But I also have to point out that this depends on no changes being made to the OEM build. Always "possible" there have been GFCI added for some unknown reason?
Maybe folks who ride around in RV so much get too excited about working on them?? :unsure:
 
With 2 heaters plugged into the same circuit there is a very good chance that 1. a connection came apart in one of the self contained receptacles or 2. a circuit breaker tripped and you did not reset it correctly, once tripped a circuit breaker will not reset until it is forced hard to "OFF" then back to "ON".

A GFCI won't normally trip on an overload as they are not overcurrent protection devices, they trip on ground faults.
 
Last edited: