Quote:
Originally Posted by DavidM
The breaker contacts might have had a bit of corrosion or prior arcing that was causing a voltage drop and therefore it got hot. After a few trips it cleaned itself up.
The tripping might be due to the A/C pulling more current than normal due to the low voltage. Motors suck more current to compensate for low voltage.
I realize that both of these are a bit of a stretch, but are the only thing I can think of that explains all of the data.
You might want to replace that breaker just to be safe.
David
|
I suppose it's possible this was due to a bad breaker, I suspect there was low voltage at the shore power connection (we still don't know what the OP means by it was OK). The only sure way to test this is to hook up to a good shore power connection that's putting out the correct voltage.
It's also possible that there's a resistance issue with the shore power cord (unlikely) or the shore power circuit in the transfer switch (more likely) that's causing low voltage. I'd tighten all connections in the transfer switch. It's a good idea to do this annually.
In any case, breaker replacement is inexpensive but, afterward, it still needs to be tested with a good shore power connection.