Quote:
Originally Posted by danhannah
I almost never disagree, Randy, but check the picture of the thermostat posted above in comment #6 - this is the same one I have. The FAN switch says "Auto or On". So in the "On" position, the propane furnace fan runs constantly, regardless of a call for heat. It would be relatively easy to activate that wire with the overhead heat pump.
|
I agree that the thermostat has the separate FAN and GAS HEAT outputs, that each are either open or have +12 volts on them as determined by the thermostat.
However, all sizes of the standard Atwood propane furnace that Winnebago uses DOES NOT have a fan input connection. ONLY a heat input connection.
Could you modify it to have a fan on only mode? Yes. I have considered doing it myself to mine.
It would involve:
--- 12 volt coil 10 amp SPDT contact relay wired to switch the fan motor +12 lead between the control board output and direct 12 volts, added inside the furnace somewhere near the control board.
--- A new wire between the thermostat and the furnace to provide the switched fan signal wire to the coil of the relay added to the furnace.
--- two SPST switches at the thermostat, both would wire to the FAN output wire of the thermostat, switch 1 would connect to the roof unit FAN input, switch 2 would connect to the modified furnace FAN input. So one can control if one, other, or both of the fans run when the thermostat fan switch is turned on.
Here's the un-modified furnace wiring diagram ...