Extra thermostat in bedroom
New to me 2004 Vectra 40kd.
Has the basement air/heat pump with Coleman mach thermostat in hallway control panel. Also has a thermostat in bedroom for heat only with no on/off switch. I think it is for heat only because I have been turning it as low as it will go to keep it off. When it is on, it blows through 3 vents in the bedroom only and only blows warm if main heat is also on. Bedroom has other vents for main air/heat.
This morning low temp in the 40's for first time. Coach is sitting in my yard plugged in.
Went outside and heard fan running in rear of coach and cold air blowing from those 3 bedroom vents.
Could not find a way to turn it off. Thermostat is turned down but only goes down to 50. Tried several breakers labeled air and heat. Finally unplugged coach from power and it went off.
Anyone know why this thing even exist? Want to keep coach plugged in during winter but it's going to get below 50 a lot.
Any way to turn it off?
Thanks
Mike
|
|
|
10-17-2017, 08:09 AM
|
#2
|
Winnebago Owner
Join Date: Oct 2017
Posts: 55
|
We had a 5er with main thermostat that had no on/off. To turn off, we had to keep pushing at minn setting and it would click to off.
|
|
|
10-17-2017, 08:16 AM
|
#3
|
Winnie Vectra Full Timer
Join Date: Jul 2017
Posts: 23
|
That doesn't work on this one.
__________________
Mike and Becky
2004 Vectra 40KD
|
|
|
10-17-2017, 10:40 AM
|
#4
|
Winnebago Owner
Join Date: Oct 2017
Posts: 55
|
Bummer. Sorry that wasn't it.
|
|
|
10-17-2017, 04:21 PM
|
#5
|
Winnie Vectra Full Timer
Join Date: Jul 2017
Posts: 23
|
Well, I disconnected the wires in that thermostat. Both gas and electric heat still work properly from main thermostat.
Fixed my immediate problem but still don't know what this feature is for other than to just throw extra heat into bedroom.
__________________
Mike and Becky
2004 Vectra 40KD
|
|
|
10-17-2017, 05:33 PM
|
#6
|
Winnebago Camper
Join Date: Dec 2016
Location: Las Vegas NV
Posts: 45
|
Hello TenMillie,
I have a 2000 Winnebago Ultimate Advantage, in our bedroom is a thermostat that I thought did not work as well. It took me 6 months to figure out a switch on the bottom that had not been switched in years. It was really hard to flip. When I was able to turn it on I discovered I had heat on the driver's side of the RV. My main thermostat operates the AC and the right side forward heater.
Thanks
__________________
Bill and Mary
2000 Winnebago Ultimate Advantage
|
|
|
10-17-2017, 08:23 PM
|
#7
|
Winnebago Master
Join Date: Aug 2005
Location: Nashua, NH
Posts: 1,817
|
Quote:
Originally Posted by TenMillie
Well, I disconnected the wires in that thermostat. Both gas and electric heat still work properly from main thermostat.
Fixed my immediate problem but still don't know what this feature is for other than to just throw extra heat into bedroom.
|
You have a 40,000 BTU main furnace and a 25,000 BTU secondary furnace. That thermostat should control the secondary furnace. Does the thermostat look like this: Suburban 161154 Wall Thermostat? It doesn't have a separate OFF switch, but the leftmost position of the temperature control should be the OFF position (as can be seen labelled in the image at the above link).
(My 36' Vectra has only one furnace, so I have no personal experience to help with this.)
__________________
Chris Beierl
2005 Winnebago Vectra 36RD
|
|
|
10-18-2017, 07:11 AM
|
#8
|
Winnie Vectra Full Timer
Join Date: Jul 2017
Posts: 23
|
Quote:
Originally Posted by cbeierl
You have a 40,000 BTU main furnace and a 25,000 BTU secondary furnace. That thermostat should control the secondary furnace. Does the thermostat look like this: Suburban 161154 Wall Thermostat? It doesn't have a separate OFF switch, but the leftmost position of the temperature control should be the OFF position (as can be seen labelled in the image at the above link).
(My 36' Vectra has only one furnace, so I have no personal experience to help with this.)
|
Yes, that is the thermostat. Thank you!!
Guessing mine is bad.
Will order new thermostat.
Again thank you.
|
|
|
10-18-2017, 10:50 AM
|
#9
|
Winnie-Wise
Join Date: Dec 2000
Location: N Id
Posts: 284
|
cbeierl is correct. That is the same as my thermostat and controls the rear gas heater. I have one vent in the bathroom and two in the bedroom. No idea where yours are. It does show OFF at the left lowest heat setting. $13.10 plus shipping .
Welcome to the Vectra crowd.
__________________
Jerry J.
2008 Winnebago Vectra 40TD
2017 Lincoln MKX
|
|
|
10-25-2017, 04:50 PM
|
#10
|
Winnebago Master
Join Date: Dec 2003
Location: Weyauwega, WI US
Posts: 1,486
|
I have a rear furnace with a separate thermostat in the bedroom also. I hand the same thing happen in late fall. I entered the bedroom and the furnace was running. I found the setting was down to where it said OFF but I pushed a little harder to the left and I heard the thermostat snap to the off position. I now have learned that when we turn the heat down we have to make sure the thermostat snaps off. I also showed my DW how it works also.
Don
__________________
Don & Bev Morgan Weyauwega WI, 05 Itasca Horizon 40KD, 400 HP Cummins, Delorme GPS LT 40, Toad 07 Saturn Vue AWD, Air Force One, TST 510 TPMS, Mayor of Weyauwega 2007 - 2013, Waupaca Co Board Supervisor 2010 - 2014
|
|
|
10-25-2017, 07:07 PM
|
#11
|
Winnebago Master
Join Date: Jun 2013
Location: Full-timer/volunteer w/SOWERS
Posts: 2,734
|
Quote:
Originally Posted by TenMillie
New to me 2004 Vectra 40kd.
Has the basement air/heat pump with Coleman mach thermostat in hallway control panel. Also has a thermostat in bedroom for heat only with no on/off switch. I think it is for heat only because I have been turning it as low as it will go to keep it off. When it is on, it blows through 3 vents in the bedroom only and only blows warm if main heat is also on. Bedroom has other vents for main air/heat.
This morning low temp in the 40's for first time. Coach is sitting in my yard plugged in.
Went outside and heard fan running in rear of coach and cold air blowing from those 3 bedroom vents.
Could not find a way to turn it off. Thermostat is turned down but only goes down to 50. Tried several breakers labeled air and heat. Finally unplugged coach from power and it went off.
Anyone know why this thing even exist? Want to keep coach plugged in during winter but it's going to get below 50 a lot.
Any way to turn it off?
Thanks
Mike
|
Hi Mike,
Try shutting the breakers off. Also, depending on the type of thermostat, you might find a removable fuse under to cover. Simply pop it out and the thermostat is rendered dead.
Hope this helps.
Rick Y
__________________
Rick & Melissa Young & Dawson (RIP), 2011 Meridian 40U, FL XCL, ISL 380HP/DEF, Al 3000 MH, 2014 Honda CR-V, SMI AF1, Blue Ox TruCenter & tow equip.,EEZTire TPMS.
Servants On Wheels Ever Ready. Best job we ever paid to do . (full time volunteers)
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Thread Tools |
Search this Thread |
|
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|