I have installed the surge guard 50/30 Amp hard wire surge protector into the MH. The unit appears to be working well for a period of time and then at some point I loose power on the load side.
1. I have a 30 amp service from the house and have used it on numerious times to keep power to the MH.
2. I installed the SG protector yesterday and it worked as it was suppose to with the 2 min. 8 sec delay (blinking light).
3. I checked the panel in MH and it indicated normal, 30 amp service. With heater running it was pulling approximately 15 to 20 amps.
4. At some point in time the power to the load side is shut off. No blinking light, no caution light, the line lights are on, power is normal to in side (line) of SG.
5. I have doubled check to make sure I have the correct voltage, 120 +/- 2 volts coming off house and line voltage at SSG is same. Run to house is with the line that came with the MH so length of run should not be an issue.
6. At some point in time I loose the power to the load side of the SG.
7. Last night I disconnected the load side of the SG and resinstalled. When the power was turned back on at the breaker the delay light blinking for correct time and power came back to MH.
8. Again at some point in time I lost power to the load side of the SG. This happened some time during the night.
9. This morning I check voltage, 120 +/- 1 volt.
10. Both line lights were lit.
11. No power to load side of SG.
12. No caution light on.

Does anyone have any ideas as to what may be happening???

MH is a 2007 Journey 36G.
jk_and_dog is offline   Reply With Quote
Old 11-25-2007, 04:20 AM   #2
Winnebago Owner
 
Join Date: May 2006
Location: virginia beach
Posts: 166
I have installed the surge guard 50/30 Amp hard wire surge protector into the MH. The unit appears to be working well for a period of time and then at some point I loose power on the load side.
1. I have a 30 amp service from the house and have used it on numerious times to keep power to the MH.
2. I installed the SG protector yesterday and it worked as it was suppose to with the 2 min. 8 sec delay (blinking light).
3. I checked the panel in MH and it indicated normal, 30 amp service. With heater running it was pulling approximately 15 to 20 amps.
4. At some point in time the power to the load side is shut off. No blinking light, no caution light, the line lights are on, power is normal to in side (line) of SG.
5. I have doubled check to make sure I have the correct voltage, 120 +/- 2 volts coming off house and line voltage at SSG is same. Run to house is with the line that came with the MH so length of run should not be an issue.
6. At some point in time I loose the power to the load side of the SG.
7. Last night I disconnected the load side of the SG and resinstalled. When the power was turned back on at the breaker the delay light blinking for correct time and power came back to MH.
8. Again at some point in time I lost power to the load side of the SG. This happened some time during the night.
9. This morning I check voltage, 120 +/- 1 volt.
10. Both line lights were lit.
11. No power to load side of SG.
12. No caution light on.

Does anyone have any ideas as to what may be happening???

MH is a 2007 Journey 36G.
jk_and_dog is offline   Reply With Quote
Old 11-25-2007, 04:36 AM   #3
Winnie-Wise
 
rvten's Avatar
 
Join Date: Nov 2002
Location: Crossville, TN USA
Posts: 397
If the voltage drops to less than 108 volts the SG is suppose to turn off. To pretect the RV.DO you have a voltage monitor plugged in? The voltage drop may only last a few minutes and by time you do your check voltage is back mup.
__________________
Tom & Bonnie
2008 Winnebago Aspect 29H
A Class C Not a B+
2010 Ford Flex
rvten is offline   Reply With Quote
Old 11-25-2007, 05:48 AM   #4
Winnebago Master
 
Join Date: Dec 2005
Location: Buxton, North Dakota
Posts: 1,037
Could be a faulty SG. Does it drop the load side if there isn't a heavier load, perhaps just the converter?
__________________
2003 Winnebago Adventurer 38G F53/ V10 605 watts of Solar
1999 Winnebago Brave 35C Handicap Equipped
F53/V10
1999 Jeep Cherokee & 1991 Jeep Wrangler Renegade
John Hilley is offline   Reply With Quote
Old 11-25-2007, 06:16 AM   #5
Winnebago Owner
 
Join Date: Oct 2006
Posts: 128
Check input and output voltage at the transfer switch when the problem condition is present. Those switches have been known to drop out when they get a little hot. The switch being "new" has nothing to do with its condition or operation. Had to replace mine under warranty before the unit was 12 months old. Good luck, keep us informed to the problem resolution.
__________________
06 Itasca Meridian 36G, 350 Cat , Flnr XC-S Chassis

07 Jeep Wrangler Unlimited
Chief is offline   Reply With Quote
Old 11-25-2007, 07:56 AM   #6
Winnie-Wise
 
Harry B's Avatar
 
Join Date: May 2006
Location: Central Florida
Posts: 358
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">I have doubled check to make sure I have the correct voltage, 120 +/- 2 volts coming off house and line voltage at SSG is same. </div></BLOCKQUOTE>

If you are measuring the voltage right at the terminal block of the Surgeguard, then I would say the Surgeguard is bad.

Even if the voltage had dropped below the Surgeguard minimum, when it came back up the Surgeguard should start the delay count down and reconnect again.

Have you tried disabling the Surgeguard by turning the key? When the Surgeguard is disabled via the key it should disregard any bad input.
__________________
Harry
2015 Tuscany 40 KQ
2013 Honda CR-V
Harry B is offline   Reply With Quote
Old 11-25-2007, 02:54 PM   #7
Winnebago Master
 
AFChap's Avatar
 
Join Date: Aug 2002
Location: ...hopefully on the road!
Posts: 1,653
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">10. Both line lights were lit.
11. No power to load side of SG.
12. No caution light on. </div></BLOCKQUOTE>

Those three things should not occur at the same time. I would be talking to the SurgeGuard folks if I were you.
__________________
Paul (KE5LXU) ...was fulltimin', now parttimin'
'03 Winnebago UA 40e TRADED OFF JUL 2023 / '17 Jeep Grand Cherokee toad
AFChap is offline   Reply With Quote
Old 11-25-2007, 04:16 PM   #8
Winnebago Owner
 
Join Date: May 2006
Location: virginia beach
Posts: 166
Finally gave up. Will be calling the SG people tomorrow.

Thanks everyone for their assistance.
jk
jk_and_dog is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
50 amp. surge guard installation advice. RCtime Electrical | Charging, Solar and Electronics 12 11-20-2008 11:10 PM
Surge Protectors Sammie Electrical | Charging, Solar and Electronics 8 01-31-2007 04:27 AM
Power Surge With Gen Startup LazyDog Electrical | Charging, Solar and Electronics 13 03-08-2006 03:18 AM

» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Winnebago Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 01:19 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.