Self induced electrical problem

I thought I should share the following with fellow RVers

Last weekend I plugged into a 50 amp service outlet for the first time since I summarized the water system. The power panel showed 20 or 30 amp service and the corresponding load. Not what I had expected from a 50 amp connection. Looked like a 30 amp setup to me and just before I went to the camp office to ask what the heck was goin on, the little lady told me that the water had not heated up like she had hoped it would. After a tiny bit of troubleshooting (checking the circuit breaker) I remembered that I had shut off the water heater CB when I winterized the coach and never set it back ON when I summarized it. With the water heater CB ON, the power panel all the indications I would expect from a 50 amp connection. Saved me a trip to the office and saved me an opportunity to look like a fool.

Thought someone might like to know this.d
__________________
2004 Itasca Sunrise W22 chassis GM 8.1 Allison 1000 Towing a 2007 Chevy Cobalt four wheels down.
Switchflicke is offline   Reply With Quote
Old 07-01-2015, 09:00 PM   #2
Winnebago Master
 
FIRE UP's Avatar
 
Join Date: Dec 2009
Location: Out there, somewhere
Posts: 1,742
Quote:
Originally Posted by Switchflicke View Post
I thought I should share the following with fellow RVers

Last weekend I plugged into a 50 amp service outlet for the first time since I summarized the water system. The power panel showed 20 or 30 amp service and the corresponding load. Not what I had expected from a 50 amp connection. Looked like a 30 amp setup to me and just before I went to the camp office to ask what the heck was goin on, the little lady told me that the water had not heated up like she had hoped it would. After a tiny bit of troubleshooting (checking the circuit breaker) I remembered that I had shut off the water heater CB when I winterized the coach and never set it back ON when I summarized it. With the water heater CB ON, the power panel all the indications I would expect from a 50 amp connection. Saved me a trip to the office and saved me an opportunity to look like a fool.

Thought someone might like to know this.d
SwitchFlicke,
You didn't do anything, any different, from any one of us. What you did was completely normal. I have been there so many times that I'm lucky I'm still alive. Anyway, keep on having a great time RVing. Don't sweat the small stuff.
Scott
__________________
2004 ITASCA HORIZON 36GD, 2011 GMC Sierra 1500 4x4 Toad '08 GL 1800 Gold Wing
Retired-29.5 yrs, SDFD, Ham - KI6OND
Me, Karla and the Sophie character, (mini Schnauzer)
FIRE UP is offline   Reply With Quote
Old 07-03-2015, 09:49 PM   #3
Winnebago Master
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 2,098
I got lost in your story somewhere. The water heater on 120VAC -or shut off, has nothing to do with 50A or 30A service, it works exactly the same way.
The only thing that affected 50A service is one leg of the incoming power was not working at first.
__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA 1SG, retired;PPA,Good Sam Life member,FMCA. "We the people are the rightful masters of both the Congress and the Courts - not to overthrow the Constitution but to overthrow men who pervert the Constitution." Abraham Lincoln
Ray,IN is offline   Reply With Quote
Old 07-04-2015, 05:44 AM   #4
Winnebago Master
 
wa8yxm's Avatar
 
Join Date: Mar 2009
Posts: 851
ON atwood water heaters there is a RED WIRE hooked to a device labeled E.C.O. you unhook it and the water heater will not heat up.. this is the suggested winterizing method.. (Turns on fault light)

What does this do? Tells the control board that it is too hot already. (hotter than it is supposed to be).

Took a shower the other day never turned on hot water.. I am in S.E. GA. WHo needs a water heater. Just a 50' hose and you got all the hot you need.
__________________
Home is where I park it!
[SIGPIC][/SIGPIC]
wa8yxm is offline   Reply With Quote
Old 07-04-2015, 09:04 AM   #5
Winnebago Owner
 
Join Date: Oct 2014
Location: Cypress River Manitoba
Posts: 84
Yes Ray,IN it doesn't make any sense does it. But that's the way it wuz. I was hoping someone might know WHY it worked that way.


Thanks wa8yxm, I shall look for that red wire and consider disconnecting it when I winterize next.


I won't lose any sleep over it, but my curious mind needs to be fed!!
__________________
2004 Itasca Sunrise W22 chassis GM 8.1 Allison 1000 Towing a 2007 Chevy Cobalt four wheels down.
Switchflicke is offline   Reply With Quote
Old 07-04-2015, 01:50 PM   #6
Winnebago Master
 
cbeierl's Avatar
 
Join Date: Aug 2005
Location: Nashua, NH
Posts: 1,823
Quote:
Originally Posted by Ray,IN View Post
I got lost in your story somewhere. The water heater on 120VAC -or shut off, has nothing to do with 50A or 30A service, it works exactly the same way.
The only thing that affected 50A service is one leg of the incoming power was not working at first.
The EMS panel uses the water heater circuit to detect the presence of 50A service (since it's on the 'other' leg of the 120V service). If that circuit breaker is turned off the EMS panel with not properly detect 50A service.
__________________
Chris Beierl

2005 Winnebago Vectra 36RD
cbeierl is offline   Reply With Quote
Old 07-04-2015, 10:09 PM   #7
Winnebago Owner
 
Join Date: Oct 2014
Location: Cypress River Manitoba
Posts: 84
Thanks for your response Chris. I was kind of thinking that must be along the lines of the 'problem', but as most of us, there is still a lot to learn about the way the builders think. Thanks again.
__________________
2004 Itasca Sunrise W22 chassis GM 8.1 Allison 1000 Towing a 2007 Chevy Cobalt four wheels down.
Switchflicke is offline   Reply With Quote
Old 07-05-2015, 06:45 PM   #8
Winnebago Master
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 2,098
Quote:
Originally Posted by cbeierl View Post
The EMS panel uses the water heater circuit to detect the presence of 50A service (since it's on the 'other' leg of the 120V service). If that circuit breaker is turned off the EMS panel with not properly detect 50A service.
Old dogs can learn something new, thanks.
__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA 1SG, retired;PPA,Good Sam Life member,FMCA. "We the people are the rightful masters of both the Congress and the Courts - not to overthrow the Constitution but to overthrow men who pervert the Constitution." Abraham Lincoln
Ray,IN is offline   Reply With Quote
Reply

Tags
electrical


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Winny owner self-replacing rear camera wagonmaster2 Electrical | Charging, Solar and Electronics 16 04-12-2011 12:50 PM
ELECTRICAL OUTLET/TV PROBLEM - SERVICE CENTER CAUSED emmmw Electrical | Charging, Solar and Electronics 7 12-14-2008 06:54 AM
electrical problem SeaRay Electrical | Charging, Solar and Electronics 6 09-04-2007 11:32 AM
Electrical problem with Jacks FrankO General Maintenance and Repair 8 08-24-2007 12:58 AM
Electrical problem or operator error. resqguy Electrical | Charging, Solar and Electronics 23 09-11-2005 05:46 AM

» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Winnebago Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 11:21 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.