Problems with GFCI

I have a problem that has bothered me for a long time.

The Freedom Combi 1500 inverter on board had problems with the GFCIs and burned them.

One day I found that the Leviton GFCIs are not compatible with the Inverter, so I replaced all with Legrand - Pass & Seymour GFCIs.

The problem is that Legrand detects a phase-neutral inversion and deactivates the entire line.

I checked all the receptacles 120 V on board and they are all wired correctly, but on the neutral, where there should not be electricity, I always detect a voltage between 24 and 36 V.

I can not understand what is happening.

I can not put the Leviton GFCI back on because the Inverter burns them literally, they can not keep the Legrand because they snap and leave me without power. What to do?

I have read all the posts in the forum but I have not found a similar case.

Has anyone a similar experience?

How did you solve it?

Thanks from now!
F702119 is offline   Reply With Quote
Old 08-21-2018, 07:17 AM   #2
Winnebago Master
 
powercat_ras's Avatar
 
Join Date: May 2015
Location: Manhattan, Kansas USA
Posts: 1,318
The online manual for the inverter charger is dated 1998 so I assume yours is quite old.
Can you tell us the make model year of your RV and if the unit is original OEM?

I have never heard the phrase "Phase Neutral Inversion" before can you say in a different way what you think the inverter output is doing?

Is there any problem with the GFCIs when the unit is just cutting thru shore power with it's internal transfer switch?

Why have you installed so many GFCIs ? I assume the OEM had 1 or 2 at most.

Thanks, I hope I can be of more help once you provide more information.
__________________
Randy - Manhattan, Kansas
2015 Vista 27N
2020 Ford Escape Hybrid
powercat_ras is offline   Reply With Quote
Old 08-21-2018, 07:30 AM   #3
Winnebago owner
 
F702119's Avatar
 
Join Date: Sep 2017
Location: Trento
Posts: 22
Quote:
Originally Posted by powercat_ras View Post
The online manual for the inverter charger is dated 1998 so I assume yours is quite old.
Can you tell us the make model year of your RV and if the unit is original OEM?

I have never heard the phrase "Phase Neutral Inversion" before can you say in a different way what you think the inverter output is doing?

Is there any problem with the GFCIs when the unit is just cutting thru shore power with it's internal transfer switch?

Why have you installed so many GFCIs ? I assume the OEM had 1 or 2 at most.

Thanks, I hope I can be of more help once you provide more information.
Thank You!

Yes, august 1999, original unit!

When I insert the tester in the receptacles it detects inverted phase/neutral; when I measure the voltage in the neutral find anywhere from 24 to 36 Volt.

Apparently there are no electrical problems (short circuits or other).

The GFCI on board are only 2.

The inverter now keeps it off because I use the city grid.
__________________
Winnebago Ultimate Advantage 38UK 2000
Freightliner XC Chassis
Caterpillar 3126B 300 HP
F702119 is offline   Reply With Quote
Old 08-21-2018, 05:15 PM   #4
Winnebago Master
 
powercat_ras's Avatar
 
Join Date: May 2015
Location: Manhattan, Kansas USA
Posts: 1,318
Quote:
Originally Posted by F702119 View Post
Thank You!

Yes, august 1999, original unit!

When I insert the tester in the receptacles it detects inverted phase/neutral; when I measure the voltage in the neutral find anywhere from 24 to 36 Volt.

Apparently there are no electrical problems (short circuits or other).

The GFCI on board are only 2.

The inverter now keeps it off because I use the city grid.
Do the lights indicate Correct with shore power on?

Are you using a tester like this?


Can you describe the light result indicator you are getting. I am confused because I have never seen one of these testers with one of the light combinations labeled Phase Neutral Inversion
__________________
Randy - Manhattan, Kansas
2015 Vista 27N
2020 Ford Escape Hybrid
powercat_ras is offline   Reply With Quote
Old 08-21-2018, 05:24 PM   #5
Winnebago owner
 
F702119's Avatar
 
Join Date: Sep 2017
Location: Trento
Posts: 22
Quote:
Originally Posted by powercat_ras View Post
Do the lights indicate Correct with shore power on?

Are you using a tester like this?


Can you describe the light result indicator you are getting. I am confused because I have never seen one of these testers with one of the light combinations labeled Phase Neutral Inversion
Yes! I have this tester, but...

for your convenience you can read, on the twin forum, what I wrote, I hope can help you to understand better the issue.

Here you will find all the latest developments:

Problems with GFCI - iRV2 Forums

Thank You!
__________________
Winnebago Ultimate Advantage 38UK 2000
Freightliner XC Chassis
Caterpillar 3126B 300 HP
F702119 is offline   Reply With Quote
Reply

Tags
ems, problems


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Problems with the GFCI Leviton ... F702119 Electrical | Charging, Solar and Electronics 6 07-05-2018 09:05 AM
2013 Vista 35B GFCI plug motohomo Winnebago Class A Motorhomes 9 05-27-2015 02:55 AM
GFCI Plug Won't Reset RETLT Electrical | Charging, Solar and Electronics 28 11-25-2014 08:43 AM
GFCI for Winnebago 38J TheToads Electrical | Charging, Solar and Electronics 12 12-02-2013 06:31 PM
GFCI outlet in bath? John_Canfield Electrical | Charging, Solar and Electronics 8 12-22-2005 08:10 AM

» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Winnebago Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 12:02 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.