Similar Experiences? If so what did you do?

During my second most recent escape to the RV to 'exercise' the jacks, Gennie and engine I recieved a bit of a jolt! (pun intended)
The owners manual advises to always have the electrical line plugged in prior to starting the generator and I have always done this without incident. On this occasion it took the customary second toggle of the start switch before the gennie started up. Within seconds I could smell a problem and upon investigation recognized that the surge protector I had installed to protect the electronics had fried. Putting it down to a surge from the startup I replaced the surge protector, this time with a power bar/surge protector with an on/off switch figuring that with the switch off the electrical surge, should it occur would not make it to and blow the surge protector. I can then turn the bar on after the gennie has settled into a nice even tempo. It seems this worked however it must have again surged with the most recent startup as the GFI trip was activated in one circut only. As it happens it is the same circut that fried the surge protector. No other circut was affected. Once the gennie settles and the GFI is reset all seems well! There does not appear to be a reduction in power level (microwave works as well as ever, no need to fire up the AC [yet] in this climate)!
Any thoughts from the wealth of experience out there?

Thanks Rich
__________________
Rich '10 Providence 40X
"We make a living by what we get, but we make a life by what we give". Norman MacEwan
LazyDog is offline   Reply With Quote
Old 03-06-2006, 08:18 AM   #2
Winnebago Camper
 
LazyDog's Avatar
 
Join Date: Nov 2005
Location: Wherever we park!
Posts: 31
Similar Experiences? If so what did you do?

During my second most recent escape to the RV to 'exercise' the jacks, Gennie and engine I recieved a bit of a jolt! (pun intended)
The owners manual advises to always have the electrical line plugged in prior to starting the generator and I have always done this without incident. On this occasion it took the customary second toggle of the start switch before the gennie started up. Within seconds I could smell a problem and upon investigation recognized that the surge protector I had installed to protect the electronics had fried. Putting it down to a surge from the startup I replaced the surge protector, this time with a power bar/surge protector with an on/off switch figuring that with the switch off the electrical surge, should it occur would not make it to and blow the surge protector. I can then turn the bar on after the gennie has settled into a nice even tempo. It seems this worked however it must have again surged with the most recent startup as the GFI trip was activated in one circut only. As it happens it is the same circut that fried the surge protector. No other circut was affected. Once the gennie settles and the GFI is reset all seems well! There does not appear to be a reduction in power level (microwave works as well as ever, no need to fire up the AC [yet] in this climate)!
Any thoughts from the wealth of experience out there?

Thanks Rich
__________________
Rich '10 Providence 40X
"We make a living by what we get, but we make a life by what we give". Norman MacEwan
LazyDog is offline   Reply With Quote
Old 03-07-2006, 03:01 AM   #3
Administrator Emeritus
 
Join Date: Dec 2003
Location: Virginia Beach, VA
Posts: 1,319


Saw this was disappearing at the bottom of the page without any reply for Rich....

rebelsbeach is offline   Reply With Quote
Old 03-07-2006, 03:09 AM   #4
Winnie-Wise
 
troth's Avatar
 
Join Date: Aug 2003
Location: NE Ohio
Posts: 387
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">microwave works as well as ever </div></BLOCKQUOTE>


I think the nuke was saved by the surge protector frankly. To me, it sounds like you need to get a check-up on your generator by authorized service.... It should not be putting out over 130vac and that's what your surge protector caught before it cooked. Is it an Onan? Has anybody been messin' with the carb or governor?
__________________
Last Brave 2004 34D
troth is offline   Reply With Quote
Old 03-07-2006, 03:47 AM   #5
Winnebago Camper
 
LazyDog's Avatar
 
Join Date: Nov 2005
Location: Wherever we park!
Posts: 31
Sorry Guys

Should have been more specific regarding the generator. Your guess is good one; An Onan 6.5 and it's been working fine until now. The rig's in storage at the house and nobody's been playing!

Thanks for the responses!

Rich
__________________
Rich '10 Providence 40X
"We make a living by what we get, but we make a life by what we give". Norman MacEwan
LazyDog is offline   Reply With Quote
Old 03-07-2006, 03:59 AM   #6
Winnebago Owner
 
Join Date: Dec 2003
Location: MN,USA
Posts: 217
When the generator starts there should be a brief period of no AC power before it "comes on-line". Are you experiencing this? When you say that you are to have "the elecrical ine plugged in" is that the cord used to get AC from either shore or generator?
__________________
2004 Itasca Sunrise 36', Workhorse
2003 Suzuki XL7
Dsouthw524 is offline   Reply With Quote
Old 03-07-2006, 05:40 AM   #7
Winnebago Camper
 
LazyDog's Avatar
 
Join Date: Nov 2005
Location: Wherever we park!
Posts: 31
Yep, the 30amp line which either plugs to shore power or plugs to generator outlet. As for the brief period of no AC I would have to check. How brief are we talking? 1-5 seconds? more?
I also don't understand why only the one circut would be affected. There are two with GFI protection yet only the one seems to trigger.

Rich
__________________
Rich '10 Providence 40X
"We make a living by what we get, but we make a life by what we give". Norman MacEwan
LazyDog is offline   Reply With Quote
Old 03-07-2006, 06:10 AM   #8
Winnebago Camper
 
Join Date: Feb 2002
Location: Springfield,Mo. USA
Posts: 48
I think the delay on the generater is in the automatic changeover circuit which you dont have if you have to plug the shoreline into the generater outlet. One output on the generater is probably wired to the rear airconditioner and the other supplies the coach and front air. If you are getting a voltage surge it sounds like a defect in the voltage regulater.
__________________
bflem Springfield,Mo. Juno Beach,Fl.
bflem is offline   Reply With Quote
Old 03-07-2006, 07:39 AM   #9
Winnebago Camper
 
Join Date: Aug 2002
Location: Southwest Ohio
Posts: 7
I always turn off my main breakers before I start the gen set, start the generator, wait a minute to let it stabilize, then turn the main breakers on. You may want to try that.
ohiorvers is offline   Reply With Quote
Old 03-07-2006, 09:25 AM   #10
Winnebago Camper
 
LazyDog's Avatar
 
Join Date: Nov 2005
Location: Wherever we park!
Posts: 31
Thanks Rich
Turning off the main breaker is the conclusion I had come to as well. To be safe I'll add a generator checkup to the list for the next visit to the dealer in the event there is a voltage regulator issue. Thanks for the advice bflem!
Do the dealers routinly have the where-with-all to properly diagnose this type of issue or should I go directly to Onan service?

Again, thanks!
Rich
__________________
Rich '10 Providence 40X
"We make a living by what we get, but we make a life by what we give". Norman MacEwan
LazyDog is offline   Reply With Quote
Old 03-07-2006, 09:27 AM   #11
Winnebago Master
 
Tom N's Avatar
 
Join Date: Dec 2002
Location: Sarver, PA/Crystal River, FL/Shelocta, PA
Posts: 1,196
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content"> I always turn off my main breakers before I start the gen set, start the generator, wait a minute to let it stabilize, then turn the main breakers on. You may want to try that. </div></BLOCKQUOTE>

There is no need to do this as there is approximately a 30 second time delay before the generator kicks into the circuit.
__________________
Sarver, PA/Crystal River, FL/Shelocta, PA · FMCA 335149 · W3TLN
2005 Suncruiser 38R · W24, no chassis mods needed · 2013 Honda Accord EX-L · 2008 Honda Odyssey EX-L
[SIGPIC][/SIGPIC]
Tom N is offline   Reply With Quote
Old 03-07-2006, 03:21 PM   #12
Winnebago Owner
 
Join Date: Jun 2003
Location: On the road, USA
Posts: 192
We had this also happen to us and the answer was go to Onan now and let them do the adjusting needed. We used our generator alot and no one ever messed with it so maybe it just happens over time. Our surge litterally burned the surge protector and everywhere the surge protector was touching anything. The stuff plugged in were not hurt though.

The tech at Onan said we were getting way to much power on start up.
Savannah is offline   Reply With Quote
Old 03-07-2006, 05:45 PM   #13
Winnebago Owner
 
Dougmyers's Avatar
 
Join Date: Jan 2006
Location: TEXAS
Posts: 92
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by Savannah:
We had this also happen to us and the answer was go to Onan now and let them do the adjusting needed. We used our generator alot and no one ever messed with it so maybe it just happens over time. Our surge litterally burned the surge protector and everywhere the surge protector was touching anything. The stuff plugged in were not hurt though.

The tech at Onan said we were getting way to much power on start up. </div></BLOCKQUOTE>
===================================

I agree go to Onan, they have the test devices to check it out correctly.
I have tried others that say they can fix them and payed for nothing when all was said and done I always ended up back at an Onan service center for the correct fix!
__________________
Doug & Diane Myers

DFW, Texas
Dougmyers is offline   Reply With Quote
Old 03-08-2006, 03:18 AM   #14
Winnebago Camper
 
LazyDog's Avatar
 
Join Date: Nov 2005
Location: Wherever we park!
Posts: 31
That settles it then!

Will let you know the results! Thanks everyone for the feedback!

__________________
Rich '10 Providence 40X
"We make a living by what we get, but we make a life by what we give". Norman MacEwan
LazyDog is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Smoke at startup 1badhemi General Maintenance and Repair 7 11-13-2016 03:35 AM
New Season startup Blues... Refig no work. pameridan04 Heating, Cooling and Appliances 12 04-23-2012 06:41 PM
1999 UA - Use of Gen-turi on Gen exaust daellishou Electrical | Charging, Solar and Electronics 7 02-25-2010 03:24 PM
Genset "bangs" at startup and shutdown? RanchoVectra Electrical | Charging, Solar and Electronics 24 08-05-2006 06:22 AM

» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Winnebago Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 07:01 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.