Okay, sounds like a breaker might be tripped or a problem but then you have a battery problem of some sort as well, which may be due to not being charged! The generator starts off battery power so a second thing to look at, so I suggest starting with the less complex 110AC power first.
This is the 110AC power drawing to take a look at how it flows from the plug to other things inside:
https://www.winnebago.com/Files/File...ire_158199.pdf
At the left is the cord and when plugged it feeds directly to the main 30 amp breaker at left in the power center, which then feeds power to the rest of the breaker for the different legs of power.
The first 15 amp one is the easy one to check as it feeds first to the frig outlet where there is a GFCI breaker that is likely to be tripped and that shuts off all power from there out on that line of outlets. So find if those outlets are dead, find the frig outlet and try resetting it.
Possible all that line then works???
Always a good trick to try the breakers by flipping then off and then fully on again to assure they are actually reset, not just looking reset! Try both 30 main and 15 amp.
Then once that line is working I would work my way left to right, testing to find what works or not and working on each problem as a single question to get the 110 AC working first and then check 12DC as the converter has to have the 110AC to work!
Start simple and the rest may begin to work but come back and we can do a second look if you get stumped?