Old 06-16-2019, 02:55 PM   #1
Winnebago Owner
 
Wetstuff's Avatar
 
Join Date: Mar 2018
Location: Salisbury, Maryland
Posts: 242
Meter reading for parasitic drain - how?

From you guys and a nice mechanic on Youtube, I know I am hunting parasitic drain because the starting battery kept drawing down 'till it needed to be replaced. (my smart charger basically put: 'Don't waste my time again on this.' on the screen. I now have a new battery.

My meter is not like the one in the video, but I suspect I stumbled into the right setting? But, there appear to be two 'right' settings: 40A and 400A and they both 'read'.

....and do the leads themselves need to attach in some specific series to match the flow of current?

So, maybe you can fill me in with meter information before I go on the quest to find the source of my problem. Thanks.

Jim

Attached Thumbnails
Click image for larger version

Name:	meter1.jpg
Views:	117
Size:	1.34 MB
ID:	171746   Click image for larger version

Name:	meter2.jpg
Views:	107
Size:	1.37 MB
ID:	171747  

Wetstuff is offline   Reply With Quote
Old 06-16-2019, 04:23 PM   #2
Winnebago Master
 
Wayne M's Avatar
 
Join Date: Aug 2008
Location: Texas
Posts: 1,665
The amp meter needs to be in series by following the video, disconnecting the negative lead of the car battery and attaching the positive lead to the disconnected battery and the negative lead to the negative post. This completes the series connection. As stated in the video, make sure the vehicle is as you would exit and leave it. (Everything off, key removed.) Current (amps) is measured in series.

I am surprised that the meter you have registers 400A as that is one hefty meter. Are you sure it is not 400mA (Mili-Amps) 400mA is equivalent to 0.4 amps. Start out with the 40A. If your vehicle is pulling 40 Amp you have a big problem.

Jim, Winnebago typically uses the service battery to operate the steps. When I was having a problem with parasitic drainage I was leaving the step switch in the on position. Talking with Winnebago the explained that the current draw on the steps when the switch is in the "on" position creates a current drain that the trickle charge cannot keep up with. Once I left the switch in the "off" position I did not have a parasitic drain. Just some food for thought. Charge the battery to full and turn off the step switch when you leave the MH. Yes the steps will be out unless you can reach the switch through the screen door when it is closed. If the screen door activates the magnetic switch. I had a mid door entry and was able to use a short stick to push the switch to off.
__________________
Wayne MSGT USMC (Ret) & Earlene (CinCHouse)
2015 Winnebago Tour 42QD - 2020 Lincoln Nautilus Reserve (TOAD)
(RVM-14) It is what it is, and then it is what you make of it.
Wayne M is offline   Reply With Quote
Old 06-16-2019, 06:12 PM   #3
Winnebago Master
 
Join Date: Oct 2017
Location: Elk Grove, CA
Posts: 3,574
I assume the photo is of your meter. I Googled the model # and see that it will read both AC and DC amps via the clamp. This greatly simplifies things since you only need to clamp it on the wire in question and there's no need to disconnect the wire. Note that one side of the clamp is labeled + and the other -. This is how it should be oriented. Were you to accidentally reverse this, I'm pretty sure it would only reverse the +/- sign of the resulting reading.

Your manual should have the instructions on how to do this. Here's a video that shows this (starting at about 1:35):



Keep us posted on your progress.

By the way, the specs do say it has a 400A capacity.
__________________
Bob C
2002 Itasca Suncruiser 35U
Workhorse Chassis
BobC is offline   Reply With Quote
Old 06-17-2019, 06:46 AM   #4
Winnebago Owner
 
Wetstuff's Avatar
 
Join Date: Mar 2018
Location: Salisbury, Maryland
Posts: 242
Thanks, guys... Ya, Wayne - it looks like I guessed right about the orientation, but another video, like Bob's video, points out: this is a 'clamp' meter for a reason ...I do not need to use the probes.

Wayne... I also suspect the automatic stairs. They have been a problem since the first month and have now completely retired. I am unable to work lying on my back (tho' I sleep that way) I lose blood pressure if I have to raise my arms to do work. So...

I have a young mechanic putting in the Trik-L-Start this week and will have him disconnect drive arm for the stairs to look for a method to make the steps manual.

Jim
Wetstuff is offline   Reply With Quote
Old 06-17-2019, 12:06 PM   #5
Winnebago Master
 
Join Date: Oct 2017
Location: Elk Grove, CA
Posts: 3,574
If the issue is a parasitic drain from the steps, disconnecting the actuator arm isn't going to help. It's not the actual extending/retracting that's the issue, it's the current draw while on standby. It shouldn't be difficult to bypass the automatic stair switch and put in a manual one but you'll need to wire it so the existing on/off switch is out of the circuit and the step is controlled by a single actuating switch so that it's never on stand-by. I would thing the wiring diagrams would show this pretty clearly.
__________________
Bob C
2002 Itasca Suncruiser 35U
Workhorse Chassis
BobC is offline   Reply With Quote
Old 06-17-2019, 12:23 PM   #6
Winnebago Master
 
Wayne M's Avatar
 
Join Date: Aug 2008
Location: Texas
Posts: 1,665
Yep, clamp amp meters work as long as they are capable of the small, or large, amperage.

I don't know the make and model of your MH, but is there a way to reach the step on/off switch when you exit? As I said, I was able to reach mine with a short 2 foot stick. I'd close the screen door and reach in through the opening and turn the switch off when it was retracted. My newer one I cannot reach the switch so I just leave it in the off position extended. I don't know if my newer coach has sufficient trickle charge with the steps on, and I'm not going to find out. :-)

Another alternative may be to just cut the power going to the step controller and splice in a toggle switch somewhere where it can be reached. This is assuming it may be the step.

p.s., the steps are controlled by the controller electronic current limiting switch. When a high state of current is reach the controller goes into high current state and stops the motor but the current remains.so the step is continuously drawing current.

At least, that is how I understand it and I'm just a layman on the subject.
__________________
Wayne MSGT USMC (Ret) & Earlene (CinCHouse)
2015 Winnebago Tour 42QD - 2020 Lincoln Nautilus Reserve (TOAD)
(RVM-14) It is what it is, and then it is what you make of it.
Wayne M is offline   Reply With Quote
Old 06-17-2019, 01:20 PM   #7
Winnebago Owner
 
Wetstuff's Avatar
 
Join Date: Mar 2018
Location: Salisbury, Maryland
Posts: 242
Roger - understand pretty much both. Using the meter as a 'clamp meter' vs. those pointy leads, I get a 6+ amps draw with nothing (I can see) going on. Step switch is in the OFF.

....I'll seek out the 'controller' also.

I plan to raise the gauge cluster cowling as that seems to be where at a lot of chassis (Workhorse P32) knife fuses are located ...over by the 110v converter, there does not seem to be anything listed that pertains.

Bob, I would rather do away with the auto open/close feature. If gravity will open it and it does not take a lineman to close it - I imagine I can rig a simple pin-lock I use on tractor implements. Thanks.

Jim
Wetstuff is offline   Reply With Quote
Old 06-19-2019, 01:51 PM   #8
Winnebago Owner
 
4x4van's Avatar
 
Join Date: Apr 2011
Location: SoCal
Posts: 203
There is no way that your steps are drawing 6 Amps in standby mode; something else is going on.
__________________
You don't stop playing because you grow old...You grow old because you stop playing!
2004 Itasca M30W
4x4van is offline   Reply With Quote
Old 06-19-2019, 02:48 PM   #9
Winnebago Owner
 
Wetstuff's Avatar
 
Join Date: Mar 2018
Location: Salisbury, Maryland
Posts: 242
4X, It seems the only immediate culprit. It has been disconnected and things are reasonably stable. I bought one of those cigar-lighter gizmos that monitor the voltage and adds extra USB outlets. It's gone from 12.6v to 12.4 as you see. That's over a 24hr period. Tomorrow my mechanic is going to install the shore power charger for the chassis battery and see if we can mechanically disconnect the steps.

I put in a new aux. fan and it works a charm! $40. The OEM's drive pin finally gave up; the motor would run but the blade was stationary.

Jim
Attached Thumbnails
Click image for larger version

Name:	12v.jpg
Views:	104
Size:	1,014.9 KB
ID:	171774   Click image for larger version

Name:	fan3.jpg
Views:	106
Size:	1.47 MB
ID:	171775  

Wetstuff is offline   Reply With Quote
Old 06-23-2019, 04:21 PM   #10
2015 Itasca Spirit 27QP
 
Join Date: Sep 2018
Location: Murfreesboro, TN
Posts: 286
The steps and other loads must have a fuse or breaker somewhere. Use it to isolate loads.
JoeC is offline   Reply With Quote
Old 06-23-2019, 08:59 PM   #11
2015 Itasca Spirit 27QP
 
Join Date: Sep 2018
Location: Murfreesboro, TN
Posts: 286
Battery voltage dropping from 12.6 to 12.4 overnight means nothing. Lead-acid batteries can drop voltage at that level without any load. If you really want to know what's going on with your battery, properly install a battery monitor using a shunt, where every load's return path has to go through the negative-connected shunt. I use the Victron BMS-712 for the coach batteries, and there are other similar type devices. Each load or circuit can be monitored after all are shut off through pulling the DC fuses and then enabling one at a time.

As for your starter battery, it can also be monitored but don't forget about the ECM (engine computer) and other electronic devices that may be active even though the ignition switch is off.
JoeC is offline   Reply With Quote
Old 06-23-2019, 09:17 PM   #12
2010 Winnebago Via 25r
 
Join Date: Sep 2017
Location: Enid, OK73701
Posts: 15
Battery tender

Quote:
Originally Posted by Wayne M View Post
The amp meter needs to be in series by following the video, disconnecting the negative lead of the car battery and attaching the positive lead to the disconnected battery and the negative lead to the negative post. This completes the series connection. As stated in the video, make sure the vehicle is as you would exit and leave it. (Everything off, key removed.) Current (amps) is measured in series.

I am surprised that the meter you have registers 400A as that is one hefty meter. Are you sure it is not 400mA (Mili-Amps) 400mA is equivalent to 0.4 amps. Start out with the 40A. If your vehicle is pulling 40 Amp you have a big problem.

Jim, Winnebago typically uses the service battery to operate the steps. When I was having a problem with parasitic drainage I was leaving the step switch in the on position. Talking with Winnebago the explained that the current draw on the steps when the switch is in the "on" position creates a current drain that the trickle charge cannot keep up with. Once I left the switch in the "off" position I did not have a parasitic drain. Just some food for thought. Charge the battery to full and turn off the step switch when you leave the MH. Yes the steps will be out unless you can reach the switch through the screen door when it is closed. If the screen door activates the magnetic switch. I had a mid door entry and was able to use a short stick to push the switch to off.
I keep a battery tender plugged in at all times. The memory on the radio helps drain the battery. Once I plugged in the battery tender I have had no more problems. I plugged a plug strip so the BATTERY TENDER could reach. As long as you have 110v to it u are good while driving and overnight you r ok. It is when it sets up is when it drains down
Mbarton557 is offline   Reply With Quote
Old 06-24-2019, 05:40 AM   #13
Winnebago Owner
 
Join Date: Dec 2006
Location: New Hampshire
Posts: 81
You mentioned that your steps have completely quit on you. I had a class c that the steps stopped working and the problem was the pivots on the steps had rusted to the point where the motor could not move them any more. Could this cause a high amp draw if the steps are not completely closed. Try unplugging the step motor and see if the draw goes away.
Don G is offline   Reply With Quote
Old 06-24-2019, 06:31 AM   #14
Peaceful Explorer
 
RzRzRzR's Avatar
 
Join Date: Apr 2018
Location: Northwestern NJ
Posts: 67
Quote:
Originally Posted by JoeC View Post
Battery voltage dropping from 12.6 to 12.4 overnight means nothing. Lead-acid batteries can drop voltage at that level without any load. If you really want to know what's going on with your battery, properly install a battery monitor using a shunt, where every load's return path has to go through the negative-connected shunt. I use the Victron BMS-712 for the coach batteries, and there are other similar type devices. Each load or circuit can be monitored after all are shut off through pulling the DC fuses and then enabling one at a time.

As for your starter battery, it can also be monitored but don't forget about the ECM (engine computer) and other electronic devices that may be active even though the ignition switch is off.
I agree. You should look into a battery monitor with a shunt. The Victron BMS-712 is great!
__________________
-- An old Coastie in a 2003 Itasca Sunrise 36M -- Semper Paratus!
RzRzRzR is offline   Reply With Quote
Old 06-24-2019, 06:58 AM   #15
Winnebago Owner
 
Join Date: Sep 2017
Location: Greenville, South Carolina
Posts: 108
Don't do it

Wetstuff,
It would be a shame to eliminate the automatic step feature. My last RV was a 2007 Adventurer that had parasitic drain, that would kill the battery in 2 to 4 weeks. I installed a small battery disconnect on the chassis battery (Walmart). It took about 1 minute to lift the stair and turn the knurled knob to connect or disconnect. No trouble after that.


I have corrected two entirely different, quirky problems with the steps on the Adventurer and the Journey and was very happy to have reliable steps again. That may be for another thread, but I wouldn't mind helping.
Richard
__________________
2010 Winnebago Journey 34Y
2020 Chev Equinox toad, Invisibrake.
skyking is offline   Reply With Quote
Old 06-24-2019, 10:27 AM   #16
Winnebago Camper
 
Join Date: May 2018
Posts: 18
Radio drain

I had a similar problem and after changing the engine battery twice discovered the culprit was the engine/coach radio switch. Make sure it is on coach when not driving. p.s. I also installed the Trick-L-Start and strongly recommend it to keep the engine battery charged while on house power.
LeonardoBF is offline   Reply With Quote
Old 06-24-2019, 01:09 PM   #17
2015 Itasca Spirit 27QP
 
Join Date: Sep 2018
Location: Murfreesboro, TN
Posts: 286
LeonardoBF,

You are on the right track now, except for installing a Victron BMV-712, or similar shunt-style battery monitor, to monitor your coach and start batteries. Maybe some day the RV manufacturers will start putting decent electrical systems in the coaches, or at least make them an option. The Amp-L-Start (Trick-L-Start but better) however, is mandatory in my opinion.
JoeC is offline   Reply With Quote
Old 06-24-2019, 02:55 PM   #18
Winnebago Owner
 
Wetstuff's Avatar
 
Join Date: Mar 2018
Location: Salisbury, Maryland
Posts: 242
Thanks, guys. It seems a couple of problems are solved. I now have a 5 amp Trik-L-Start wired into the new starting battery and my young mechanic refused to make my steps manual without looking at them. He found my problem.

Mine are funky looking, but without the issues you had Don. I wonder if there was a lot more salt on your roads. (I made a separate posting about the steps)

Anyway, these ghosts have been chased out of this 2002 graveyard - for the moment at least.

Jim
Wetstuff is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
How to determine parasitic load on the starting Wetstuff Electrical | Charging, Solar and Electronics 19 11-24-2019 06:47 PM
Parasitic power draw chunker Winnebago Class A Motorhomes 7 11-12-2017 08:47 PM
Hourglass Symbol Flashing On Meter gr8wit Electrical | Charging, Solar and Electronics 6 01-29-2007 01:25 PM
Parasitic battery drain Ken & Joyce Electrical | Charging, Solar and Electronics 9 03-11-2006 07:06 AM
Surge Protector Vs Meter Check John and Elaine Electrical | Charging, Solar and Electronics 9 08-04-2005 05:24 PM

» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Winnebago Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 03:51 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.