Quote:
Originally Posted by wegobago
Yes 20 amp breaker on generator trips when the main panel is completely shut down. Replaced faulty gfci, all good there.
|
The generator output goes back to the ATS. Look at these diagrams:
http://www.winnebagoind.com/diagram/1998/126758.pdf This one shows a 4x4 box.
http://www.winnebagoind.com/diagram/1998/126818.pdf Sheet 8 of 25 shows the location of the 4x4 box, left side of diagram under bedroom. Disconnect the wires in there and measure each to ground with a VOM. You have a short some place on the generator feed. Worst case, internal to the generator.