Old 11-25-2014, 02:48 PM   #1
Winnebago Camper
 
BLAdventurer's Avatar
 
Join Date: Jan 2013
Posts: 13
Basement air will not run in heat mode

I have run system in heat mode before with no problem. Air conditioning mode works fine. When I put it in heat mode, you can hear the unit start but the fan does not come on. Outside temperature is about 55, so that is not an issue. We are in a 06 Adventurer.
BLAdventurer is offline   Reply With Quote
Old 11-25-2014, 04:30 PM   #2
Winnebago Master
 
DancinCampers's Avatar
 
Join Date: Nov 2004
Location: On the Road Westward
Posts: 711
Once the tstat calls for heat, all the functions are handled by the pc board in the basement unit. You didn't say which fan is not starting, but I assume the indoor fan. The troubleshooting guide on the rv comfort website should help determine which component might have failed.
__________________
Dan & Sharon & Kasey (Our Yorkie Puppy (12 Yrs Old) On the Road (2012 Journey 36M, 2006 Jeep Liberty)
USN-Ret ('65-'93) Fulltimers, Class of 2012
DancinCampers is offline   Reply With Quote
Old 11-25-2014, 06:44 PM   #3
Winnebago Master
 
Join Date: Sep 2005
Posts: 962
I once had a similar problem (mine was actually cooling) ...

I unplugged the power cord from the pedestal ... waited about a minute ... then plugged it back in ... and everything worked ...

I think the PC board needed to reboot ...
skigramp is offline   Reply With Quote
Old 11-25-2014, 07:40 PM   #4
Winnebago Owner
 
Rockwood27's Avatar
 
Join Date: Jun 2012
Location: Freedom, NH
Posts: 83
Outside temp at 55? Just open the windows!! JK!! If you set the room temp 4-5 above ambient room temp, the gas furnace will try to kick on. Is this your problem?
__________________
Fran, Mary & Zoey (silver Cocker)
2006 Itasca Sunrise 35A, 2005 W-22, Allison 1000 5 speed
'13 Ford Focus ST or '10 Prius on Master Tow Dolly 80THD-SB or '00 Jeep Cherokee 4-down
Rockwood27 is offline   Reply With Quote
Old 11-25-2014, 07:51 PM   #5
Winnebago Camper
 
BLAdventurer's Avatar
 
Join Date: Jan 2013
Posts: 13
Outside temp at 55? Just open the windows!! JK!! If you set the room temp 4-5 above ambient room temp, the gas furnace will try to kick on. Is this your problem?
No, my problem is the inside blower does not work in heat mode. Gas furnace is working fine. Probably is the control board. I will attempt a reset in the morning after the rain passes.
BLAdventurer is offline   Reply With Quote
Old 11-26-2014, 02:57 PM   #6
Winnebago Master
 
bobmac's Avatar
 
Join Date: Mar 2008
Location: Southern Ontario
Posts: 562
You should have a look at the Manual that came with the Coach to determine if that is how it is designed to operate. In my 09 Journey, the heat pump will not operate unless there is 4 degrees or less difference between the thermostat setting and the ambient inside temperature. If below that, the furnace runs until it reaches the set thermostat temperature - then on subsequent starts, the heat pump runs. Yours sounds to me like it is properly operating like mine.
Good luck,
__________________
Bob
09 Journey 39Z
Southern Ontario
bobmac is offline   Reply With Quote
Old 11-26-2014, 03:05 PM   #7
Winnebago Camper
 
BLAdventurer's Avatar
 
Join Date: Jan 2013
Posts: 13
Thanks for all the replies. I did a reset to no avail. So I am off to the service department next week. Not my favorite place to go.
BLAdventurer is offline   Reply With Quote
Old 11-26-2014, 03:20 PM   #8
KIX
Winnebago Master
 
KIX's Avatar
 
Join Date: Dec 2006
Location: St. Augustine, FL
Posts: 587
If you go online to the Airxcel website you can find a service manual for your heat pump. There are trouble shooting "trees" that will help you find the problem and define which part to change. You'll need to have your specific model number.
__________________
KIX
'02 Ultimate Advantage 40J Spartan MM - Cummins ISC
KIX is offline   Reply With Quote
Old 11-26-2014, 09:23 PM   #9
Winnebago Master
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 2,039
My inside fan will not operate on "constant run" when in heat-mode, but does in cool-mode. Took the coach in to have it repaired and was told that's the way it is designed. I wasn't charged so I know they weren't saying that for the shop time money.
That RV technician also said that if I have other similar problems, to remove the T'stat from the wall and make sure the wire connections aren't corroded and losing contact before spending money.
__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA 1SG, retired;PPA,Good Sam Life member,FMCA. "We the people are the rightful masters of both the Congress and the Courts - not to overthrow the Constitution but to overthrow men who pervert the Constitution." Abraham Lincoln
Ray,IN is offline   Reply With Quote
Old 11-27-2014, 06:33 PM   #10
Winnebago Master
 
grtharris's Avatar
 
Join Date: Apr 2003
Location: Skiatook, OK
Posts: 1,460
BLAdventurer, move the mode switch on the thermostat around, they are a know weak point on that thermostat.
__________________
Grant & Pat
2014 Adventurer 35P
2021 Rapid Red 4dr Bronco OBX
grtharris is offline   Reply With Quote
Old 11-27-2014, 06:48 PM   #11
Winnie-Wise
 
Bug512's Avatar
 
Join Date: Oct 2010
Location: Warren County, NJ
Posts: 300
Quote:
Originally Posted by grtharris View Post
BLAdventurer, move the mode switch on the thermostat around, they are a know weak point on that thermostat.
I second that. When switching to electric heat a slight tap left of right will make her work. I know, I should order a thermostat !
__________________
Gene & Ginger 04 Winnebago Adventurer 33V, Workhorse, 11 Subaru Forester (Toad), Blue Ox Avail, BrakeBuddy, ScanGaugeII, BatteryMINDer, KONI FSD's
Gene's Pictures Ginger's Pictures Gene's Videos
Bug512 is offline   Reply With Quote
Old 11-28-2014, 07:17 AM   #12
Winnebago Camper
 
KD4XR's Avatar
 
Join Date: Jul 2014
Location: Alabaster, AL
Posts: 46
I had a similar problem with my 06 Horizon. The problem was a faulty air flow sensor. The heat pump would not start because it didn't detect adequate air flow.
__________________
Jerry & Susie, Alabaster, AL
2006 Itasca Horizon 40KD, 2014 CRV, Blue Ox
2017 Harley RoadGlide Ultra
KD4XR is offline   Reply With Quote
Old 11-28-2014, 08:01 PM   #13
Winnie-Wise
 
ChasA's Avatar
 
Join Date: Mar 2007
Location: Apex, NC
Posts: 449
KD4XR
I think you're talking about the furnace. The furnace requires air flow before lighting the burner. A heat pump is electric only used to be called reverse cycle air conditioning.
__________________
2010 Winnebago Journey Express 34Y
2010 Freightliner XCS (mfd 9/'09)
'07 Saturn Vue V6
ChasA is offline   Reply With Quote
Old 11-29-2014, 05:50 AM   #14
Winnebago Watcher
 
tandj385's Avatar
 
Join Date: Oct 2014
Posts: 2
I have the same situation as grtharris describes, find I have to wiggle the tstat mode switch more often on our 04 Adventurer.
tandj385 is offline   Reply With Quote
Old 11-29-2014, 08:12 AM   #15
Winnebago Camper
 
KD4XR's Avatar
 
Join Date: Jul 2014
Location: Alabaster, AL
Posts: 46
Quote:
Originally Posted by KD4XR View Post
I had a similar problem with my 06 Horizon. The problem was a faulty air flow sensor. The heat pump would not start because it didn't detect adequate air flow.
In my case the description of the repairs states...

"Checked furnace it had a bad Sail switch disassembled unit to gain access to the switch had to repair the switch repaired reassembled unit and tested working good now"

So, based on that description, a relationship between the the front furnace and the heat pump does exist.
__________________
Jerry & Susie, Alabaster, AL
2006 Itasca Horizon 40KD, 2014 CRV, Blue Ox
2017 Harley RoadGlide Ultra
KD4XR is offline   Reply With Quote
Old 11-29-2014, 09:25 AM   #16
Winnie-Wise
 
Bug512's Avatar
 
Join Date: Oct 2010
Location: Warren County, NJ
Posts: 300
Strange that a problem with the furnace would effect the operation of the heat pump since they are two separate pieces of equipment.
__________________
Gene & Ginger 04 Winnebago Adventurer 33V, Workhorse, 11 Subaru Forester (Toad), Blue Ox Avail, BrakeBuddy, ScanGaugeII, BatteryMINDer, KONI FSD's
Gene's Pictures Ginger's Pictures Gene's Videos
Bug512 is offline   Reply With Quote
Old 11-29-2014, 10:42 AM   #17
Winnebago Master
 
grtharris's Avatar
 
Join Date: Apr 2003
Location: Skiatook, OK
Posts: 1,460
The sail switch is in the gas furnace there not any connection between the basement air unit and the gas furnace other than the thermostat which just sends the call for heat or A/C.
BLAdventurer, does the inside fan run on A/C. If it does I'm still thinking thermostat.
__________________
Grant & Pat
2014 Adventurer 35P
2021 Rapid Red 4dr Bronco OBX
grtharris is offline   Reply With Quote
Old 11-29-2014, 06:14 PM   #18
Winnebago Master
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 2,039
Quote:
Originally Posted by KD4XR View Post
In my case the description of the repairs states...

"Checked furnace it had a bad Sail switch disassembled unit to gain access to the switch had to repair the switch repaired reassembled unit and tested working good now"

So, based on that description, a relationship between the the front furnace and the heat pump does exist.
My only connection is the manual switch for selecting electric or gas heat. I suppose that could be corroded and losing contact.
__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA 1SG, retired;PPA,Good Sam Life member,FMCA. "We the people are the rightful masters of both the Congress and the Courts - not to overthrow the Constitution but to overthrow men who pervert the Constitution." Abraham Lincoln
Ray,IN is offline   Reply With Quote
Old 11-30-2014, 08:40 PM   #19
Winnebago Camper
 
BLAdventurer's Avatar
 
Join Date: Jan 2013
Posts: 13
Thanks for all the suggestions. "Murphy" had a better plan, just move the MH to the Iron Bowl state and it now works. Even works at home now. Canceling my service appointment in the morning. Don't really know what was causing it.
BLAdventurer is offline   Reply With Quote
Old 12-17-2015, 02:08 PM   #20
Winnebago Watcher
 
Join Date: Dec 2015
Posts: 3
I have been having a similar problem, If inside is 68 and I start the generator and turn the elecric heat on and up to 70 SOMETIMES, the fan comes on and it works wonderfully, then during a cycle, I hear it click, but no fan, I do hear a compressor groaning, and I watch the amp meter go from 2- over 30, I then fear its going to burst into flame, so I click it to gas heat and it works fine...I have replaced the board inside the basement, which allowed the a/c to properly work, and I have changed the thermostat, just because, I have changed the starters and resistors they are attatched to...ANY SUGGESTIONS would be greatly appreciated, my wallet it getting thin...thx
Snotamer is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Run Basement/Propane Heat while driving? Ruddog General Maintenance and Repair 15 11-17-2015 09:39 PM
Atwood water heater not working on electric mode Marguerite66 Electrical | Charging, Solar and Electronics 16 04-19-2015 08:31 PM
Tru Air icing up in heat mode FDchief General Maintenance and Repair 31 02-14-2011 12:10 PM

» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Winnebago Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 11:33 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.