03-02-2017, 07:06 PM
|
#1
|
Winnebago Camper
Join Date: Sep 2015
Location: Saskatchewan
Posts: 32
|
Another (sporadic)Coleman Mach Basement Heat Pump Problem
I have a 2002 Journey with the basement Coleman 6535 unit... The unit has generally worked very well, have changed out faulty fan Capacitors prior and off and running again; today I replaced a Compressor Run Capacitor thinking that may be the issue, nope. This problem has me stumped.. Yesterday, in heat mode, you could hear the fans start and compressor start, they would run for a couple seconds then quit, few minutes later same thing, this would happen several times then the unit would fire and stay running and bring the interior up to correct stat temp. This has happened several times throughout the day.
As I sit here writing this, the unit has cycled 1/2 dozen times, trying to start and then stop, this moment it has started and is running and I can feel the inside temps rising as they should (at this moment the unit is running properly). The outside air temp is approx 58F and our stat setting is 74F.
Any thoughts?
__________________
2002 Winnebago Journey DL 39QD, 2013 Jeep Wrangler, 2014 HD Limited, 1972 FX1200
|
|
|
03-02-2017, 11:43 PM
|
#2
|
Winnebago Owner
Join Date: Sep 2011
Location: Denver, CO
Posts: 120
|
Wish I could hear this unit "try" to start .......... or put an amprobe on it: but I'd hazard a "guess" anyway: A fairly common failure mode with older compressors is that they just sometimes get to be "hard starters" with internal wear and then they need more starting torque to get underway. With a strap-on "kicker" they often last many more years. These kicker/hard start capacitors are reasonable enough that it is probably worth "throwing a part" at it. It just takes a few minutes to install (couple of push-on flag connectors) once you get access to the run cap and the directions will be in the package. The kicker will be in parallel (additive) with the run cap and will only be active for milliseconds.........just a quick kick in the pants, so to speak; then it "drops out" of the ckt.
I buy mine at a wholesaler but you can get a popular one from Amazon:
https://www.amazon.com/Supco-ERPP6-C...ir+conditioner
Just my $.02, of course. Let us know how it all turns out, pls.
Someone on the forum may have had this exact problem......in which case, their advice would be better, methinks.
Good luck, and safe travels.
Ed S in Denver
__________________
Ed Sievers, Denver, CO
07 WBGO Outlook 31-C Sold Real good coach, just time to hang up the keys at 91.
"Be the person you needed when you were younger"
|
|
|
03-04-2017, 06:13 PM
|
#3
|
Winnebago Owner
Join Date: Oct 2008
Posts: 176
|
If the AC portion runs with out a problem, I would have your "Reversing valve" checked out When calling for heat this valve must change positions
|
|
|
03-05-2017, 08:24 AM
|
#4
|
Winnebago Camper
Join Date: Sep 2015
Location: Saskatchewan
Posts: 32
|
Quote:
Originally Posted by lwasouth
If the AC portion runs with out a problem, I would have your "Reversing valve" checked out When calling for heat this valve must change positions
|
I agree, my gut feeling aswell.. I think the valve is sticking...
__________________
2002 Winnebago Journey DL 39QD, 2013 Jeep Wrangler, 2014 HD Limited, 1972 FX1200
|
|
|
03-07-2017, 08:26 AM
|
#5
|
Winnebago Camper
Join Date: Sep 2015
Location: Saskatchewan
Posts: 32
|
Had tech check my unit.. Could find nothing wrong.. Seems I was not recieveing proper voltage, 50 Amp, at campground.. Tech fired up generator, no Colman Mach heat pump issues... all amperage and volts were correct.
I purchased a good quality surge protector which also cuts power with power drops below 108V or over 130V...
plugged into new site, unit is working as designed...
__________________
2002 Winnebago Journey DL 39QD, 2013 Jeep Wrangler, 2014 HD Limited, 1972 FX1200
|
|
|
03-07-2017, 09:34 AM
|
#6
|
Winnebago Camper
Join Date: Jan 2015
Posts: 17
|
Nothing like speaking from experience.
=== Replace AIR FILTER ====
Now Start troubleshooting.
|
|
|
03-07-2017, 09:55 PM
|
#7
|
Winnebago Owner
Join Date: Sep 2011
Location: Denver, CO
Posts: 120
|
Nice to hear a story with a happy ending, Petesflhtk. Thanks for letting us all know how it turned out........................ appreciate it.
__________________
Ed Sievers, Denver, CO
07 WBGO Outlook 31-C Sold Real good coach, just time to hang up the keys at 91.
"Be the person you needed when you were younger"
|
|
|
03-13-2017, 05:49 PM
|
#8
|
Winnebago Camper
Join Date: Sep 2015
Location: Saskatchewan
Posts: 32
|
****Updatae****
Well, guess I spoke to quickly.. My gremlin has returned... Sporatic/not starting starting as designed. Sometimes 1st or Compressor cuts in them immediately shuts down or raises temp partially up yo stat temp then stops..
__________________
2002 Winnebago Journey DL 39QD, 2013 Jeep Wrangler, 2014 HD Limited, 1972 FX1200
|
|
|
07-24-2020, 05:33 AM
|
#9
|
Winnebago Watcher
Join Date: Jul 2020
Posts: 2
|
Did you ever resolve this issue? I am having the same problem on my 2002 Journey. It seems to be worse after the unit has not been run for a few days/weeks. It does it in heat or cool mode. Once it has been running for a while it seems to be ok. Thanks
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Thread Tools |
Search this Thread |
|
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|