Old 02-26-2011, 10:42 PM   #1
Winnie-Wise
 
UFO Pilot's Avatar
 
Join Date: Aug 2007
Location: Sonoma County, CA
Posts: 429
50 amp Shore Power shows 30 amp on EMS

This morning my 50 amp shore power suddenly went to 30 amp on the EMS panel. I have checked all of the breakers and measured the power thru the transfer switch at 240 volts. Any ideas on what to check or what the problem might be?
__________________
Wayne & Roberta and Maggie the Miracle Dog
08 Winnebago Destination 39W Gas UFO Workhorse Chassis
Making the Journey in our Destination

UFO Pilot is offline   Reply With Quote
Old 02-26-2011, 11:36 PM   #2
Winnebago Camper
 
mfire1339's Avatar
 
Join Date: Jun 2008
Location: Glendora Ca.
Posts: 34
Wayne, Are you saying you really have 50amp working at breakers but readout only says 30?

Mike
__________________
2004 Monaco Monarch
Blueox, SMI, 1990 Wrangler YJ
mfire1339 is offline   Reply With Quote
Old 02-27-2011, 05:44 AM   #3
Winnie-Wise
 
Bug512's Avatar
 
Join Date: Oct 2010
Location: Warren County, NJ
Posts: 300
Did you unplug from shore power and then plug back in?

I know on ours when plugged into 50 amps the amp display goes blank, reading the manual this is because it is disabled when plugged onto 50 Amp service.

Let us know..
__________________
Gene & Ginger 04 Winnebago Adventurer 33V, Workhorse, 11 Subaru Forester (Toad), Blue Ox Avail, BrakeBuddy, ScanGaugeII, BatteryMINDer, KONI FSD's
Gene's Pictures Ginger's Pictures Gene's Videos
Bug512 is offline   Reply With Quote
Old 02-27-2011, 06:10 AM   #4
Winnebago Camper
 
Join Date: Aug 2010
Posts: 19
I've had this issue several times. In each case one of the breakers on the campground connection wasn't properly set. Not tripped, but maybe dirty. Resetting the breaker several times has always cleared the problem. If not, contact the campground. They should have someone come look at it.

Agree with the previous post. If you're getting 50amp shore power, your display should be blank. On mine, the little lights showing which circuts are active are all green, but no amperage readout.
lpasekof is offline   Reply With Quote
Old 02-27-2011, 07:00 AM   #5
Winnebago Owner
 
Join Date: Jun 2007
Posts: 109
If, in fact, you have 120 VAC on each leg and all AC plugs are hot, water heater works on electric, etc., then you need a new pc (control) board for your Intellitec Powerline EMS. Other folks have had the same problem (me included).
__________________
NoMoreAZ

2006 Itasca Horizon 40KD, 2004 Honda CR-V
NoMoreAZ is offline   Reply With Quote
Old 02-27-2011, 07:16 AM   #6
Winnebago Owner
 
jackrobinryan's Avatar
 
Join Date: Oct 2006
Location: wherever
Posts: 50
Assuming your house batteries are well charged, one simple test can eliminate the converter as a possible culprit....

If your converter is located under the lowest drawer under the stove, remove the drawer and unplug the 110VAC converter plug from it's power recepticle.

Check the EMS display, if it has returned to "normal", (ie 12vdc is from the batteries only) the converter's DC output may be suspect. If the EMS still exibits the problem, look elsewhere.

More than several of us have had converter problems that looked like EMS circuit board problems, when in fact the board problem were caused by it.

good luck and keep us posted.
__________________
2007 Adventurer 38T w/
sway & trac bars, Koni FSDs and SafeT+
2006 Jeep Liberty toad
jackrobinryan is offline   Reply With Quote
Old 02-27-2011, 07:04 PM   #7
Winnie-Wise
 
dengraham's Avatar
 
Join Date: Sep 2005
Location: Crossville, Tennessee
Posts: 417
You should "start over" by disconnecting from the post and disconnecting the 12 volt by turning off the 12 volt switch. Then turn on the 12 volt switch (which will reset the EMS panel); test the post and reconnect to the post. Let us know if this worked.
__________________
Dennis & Trish (and Sparky Doodle)
2013 Meridian 42E
2011 Ford Explorer
dengraham is offline   Reply With Quote
Old 02-27-2011, 07:10 PM   #8
Winnie-Wise
 
UFO Pilot's Avatar
 
Join Date: Aug 2007
Location: Sonoma County, CA
Posts: 429
I checked all of the breakers, disconnected and reconnected, and I tried 2 other 50 amp outlets. I have a Magnum 2000 inverter that was installed about 1 year ago. I believe it may be the EMS itself but don't know how to test it myself.
__________________
Wayne & Roberta and Maggie the Miracle Dog
08 Winnebago Destination 39W Gas UFO Workhorse Chassis
Making the Journey in our Destination

UFO Pilot is offline   Reply With Quote
Old 02-27-2011, 07:11 PM   #9
Winnie-Wise
 
UFO Pilot's Avatar
 
Join Date: Aug 2007
Location: Sonoma County, CA
Posts: 429
Quote:
Originally Posted by dengraham View Post
You should "start over" by disconnecting from the post and disconnecting the 12 volt by turning off the 12 volt switch. Then turn on the 12 volt switch (which will reset the EMS panel); test the post and reconnect to the post. Let us know if this worked.
Do you mean the house battery disconnect switch?
__________________
Wayne & Roberta and Maggie the Miracle Dog
08 Winnebago Destination 39W Gas UFO Workhorse Chassis
Making the Journey in our Destination

UFO Pilot is offline   Reply With Quote
Old 02-27-2011, 07:13 PM   #10
Winnie-Wise
 
UFO Pilot's Avatar
 
Join Date: Aug 2007
Location: Sonoma County, CA
Posts: 429
Quote:
Originally Posted by mfire1339 View Post
Wayne, Are you saying you really have 50amp working at breakers but readout only says 30?

Mike
I tested thru the transfer switch (240 in and out) but not thru the main breaker in the RV.
__________________
Wayne & Roberta and Maggie the Miracle Dog
08 Winnebago Destination 39W Gas UFO Workhorse Chassis
Making the Journey in our Destination

UFO Pilot is offline   Reply With Quote
Old 02-27-2011, 07:56 PM   #11
Winnebago Owner
 
Keith K's Avatar
 
Join Date: Feb 2005
Posts: 94
This has happened to me and has been addressed on other posts; in my case, the circuit board for the EMS is at fault. The EMS always shows 30A no matter what I'm on. It's not a problem, everything still runs as normal because I'm really on 50A, the only irritant is that the EMS shows faulty Amp draw - with both A/C and the dryer on, it may only register 8 amps, on other occasions, the use of an electric heater, dryer, and anything else may register 35 amps, and it shuts down the water heater, refer, etc. I've found that if this happens, I can turn off an appliance and it will drop back to a few amps. A minor irritant, not worth the trouble to me to get fixed. It's only been two years now.....
__________________
Fulltiming in a 2006 Ellipse 40FD

Our blog
Keith K is offline   Reply With Quote
Old 02-27-2011, 09:02 PM   #12
Winnie-Wise
 
dengraham's Avatar
 
Join Date: Sep 2005
Location: Crossville, Tennessee
Posts: 417
Wayne,
Yes, I mean the house disconnect switch. It is the only way to reset the EMS. Just disconnect from the post first to disconnect from the 120 volts, then turn off the house disconnect swith. Then turn it back on.
If you still have a problem; it still may be at the post. I have been at campgrounds were the 50 amp are just two 120 volts coming from one wire at the circuit box. Even though you have two 120 lines coming into the motor home it will not recognize it as 50 amp because you only have a single phase coming from the breaker box. (When I use my "cheater" cable if the two lines coming into the motor home are on the same phase (single) the EMS will still show only 30 amps.)
Another way to reset the EMS board is to take out the 7 amp fuse in the breaker panel but it is not easy to do.
If you can't get it to work; call Intellitec in Florida. Their support area helped me when I had no lights at all and that's when I realized the EMS needed to be "re-set."
Good luck.
__________________
Dennis & Trish (and Sparky Doodle)
2013 Meridian 42E
2011 Ford Explorer
dengraham is offline   Reply With Quote
Old 02-27-2011, 09:07 PM   #13
Winnie-Wise
 
dengraham's Avatar
 
Join Date: Sep 2005
Location: Crossville, Tennessee
Posts: 417
Wayne,
By the way, the campground called it a "modified" 50 amp because they really only had a single 30 amp wire which they "jumped" to both sides of the 50 amp plug. They argued that I was still getting two 120 lines coming into the motor home but I simply explained a 50 amp should have two separate lines with 120 volts on both lines. Each line needs their own 50 amp breaker. I hope I have not totally confused you.
__________________
Dennis & Trish (and Sparky Doodle)
2013 Meridian 42E
2011 Ford Explorer
dengraham is offline   Reply With Quote
Old 02-27-2011, 09:13 PM   #14
Winnie-Wise
 
UFO Pilot's Avatar
 
Join Date: Aug 2007
Location: Sonoma County, CA
Posts: 429
I am back at home now and plugged in to my own 50 amp service and still have the same problem. I will try the reset procedure tomorrow morning. If that doesn't fix the problem I will call Intellitec.
__________________
Wayne & Roberta and Maggie the Miracle Dog
08 Winnebago Destination 39W Gas UFO Workhorse Chassis
Making the Journey in our Destination

UFO Pilot is offline   Reply With Quote
Old 02-28-2011, 06:46 AM   #15
Winnebago Owner
 
Join Date: Jan 2008
Location: Pensacola, FL
Posts: 122
Sometimes unplugging the phone/lan cable from the inverter to the EMS panel for a minute or so resets the panel...Worth a try...
movin-on is offline   Reply With Quote
Old 02-28-2011, 11:10 PM   #16
Winnie-Wise
 
UFO Pilot's Avatar
 
Join Date: Aug 2007
Location: Sonoma County, CA
Posts: 429
I tried all of the suggestions here with no success. I have a mobile repairman coming tomorrow, I will post what he finds.

I called Intellitec this morning, they no longer offer tech support to owners, only to repairmen. They said it was due to safety concerns.
__________________
Wayne & Roberta and Maggie the Miracle Dog
08 Winnebago Destination 39W Gas UFO Workhorse Chassis
Making the Journey in our Destination

UFO Pilot is offline   Reply With Quote
Old 03-01-2011, 12:25 AM   #17
Winnebago Watcher
 
Drifter's Avatar
 
Join Date: Dec 2006
Posts: 4
Wayne, Try taking the Breaker panel cover off and make sure all the common connections are tight (white wires) make sure to disconnect from power source first.
__________________
Mike & Sharon and our Pup Frankie
2008 HR Endeavor 40PDQ

Drifter is offline   Reply With Quote
Old 03-01-2011, 09:01 PM   #18
Winnie-Wise
 
UFO Pilot's Avatar
 
Join Date: Aug 2007
Location: Sonoma County, CA
Posts: 429
Looks like it is the circuit board in the inverter and not covered by warranty. New board is on the way and the RV Tech will come back and install in next week.

The inverter was wired to feed the entire RV by running the 50 amp feed thru the inverter but that is a problem because the inverter is only rated at 30 amps. The Tech is going to have to do some circuit rewiring to keep it from happening again.
__________________
Wayne & Roberta and Maggie the Miracle Dog
08 Winnebago Destination 39W Gas UFO Workhorse Chassis
Making the Journey in our Destination

UFO Pilot is offline   Reply With Quote
Old 03-02-2011, 06:11 AM   #19
Winnebago Owner
 
Join Date: Jan 2008
Location: Pensacola, FL
Posts: 122
Hard to beleive that the high amp draw items (ac...elec water heater...etc) run thru the inverter but I guess you learn something every day...You should have a sub panel of inverter circuit breakers that will tell you what the inverter powers when it is on....You can get a Winnie wiring diagram online if you don't have it already to verify what is happening and before anyone rewires anything...
movin-on is offline   Reply With Quote
Old 03-02-2011, 10:50 AM   #20
Winnie-Wise
 
UFO Pilot's Avatar
 
Join Date: Aug 2007
Location: Sonoma County, CA
Posts: 429
The inverter was installed last year in Quartzsite. The Tech is going to put a sub panel in and wire it the way it should have been done when it was installed.
__________________
Wayne & Roberta and Maggie the Miracle Dog
08 Winnebago Destination 39W Gas UFO Workhorse Chassis
Making the Journey in our Destination

UFO Pilot is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electric system monitor panel shows 30 amp when hooked up to 50 amp Magumba Electrical | Charging, Solar and Electronics 13 03-05-2010 08:09 PM
Black Tank Sensor shows Empty - even when full! DavidLyle Plumbing | Systems and Fixtures 8 02-17-2010 02:38 PM
LP Sensor shows empty glenda1908 General Maintenance and Repair 7 02-28-2006 04:38 AM

» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Winnebago Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 08:03 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.