Quote:
Originally Posted by cmpncrsaider View Post
So we will only be able to use it at campgrounds with 240 volt 50 amp, maybe some 30 amp 240 sites but would be dryer only when it's on at 30 amp site.
Not to be a wiseacre, but I hope for your sake you never plug into a 30 amp receptacle that's wired for 240 VAC.

Rusty
RustyJC is offline   Reply With Quote
Old 01-03-2014, 04:53 PM   #22
Winnie-Wise
 
dengraham's Avatar
 
Join Date: Sep 2005
Location: Crossville, Tennessee
Posts: 417
John (cmpncrsaider),
I am very very concerned about your statements. If you buy an RV stackable washer/dryer you will not need nor get what you suggest. If you install a residential washer and dryer stackable you will never get the current from your existing electrical panel to run the dryer. If you connect to any RV pedestal at a campground, you will not be able to connect to a 240 volt dryer whether 30 amp or 50 amp. It is important that you understand the difference between a residential connection compared to an RV connection.
As stated above, yes you are getting a total of 240 volts "available" from the pedestal but only 120 is available on one line and another 120 on the other line. Both are NOT going to the dryer (or any other device in the motorhome.)
I do agree having a separate washer and dryer is better but please understand they are 120 v units.
__________________
Dennis & Trish (and Sparky Doodle)
2013 Meridian 42E
2011 Ford Explorer
dengraham is offline   Reply With Quote
Old 01-04-2014, 08:47 AM   #23
Registered User
 
mel s's Avatar
 
Join Date: Mar 2010
Posts: 340
Quote:
Originally Posted by dengraham View Post
John (cmpncrsaider),
If you connect to any RV pedestal at a campground, you will not be able to connect to a 240 volt dryer whether 30 amp or 50 amp.
As stated above, yes you are getting a total of 240 volts "available" from the pedestal but only 120 is available on one line and another 120 on the other line. Both are NOT going to the dryer (or any other device in the motorhome.)
dengraham
I agree.
A 30A RV pedestal receptacle can't be used for any 240V appliance because it only provides 120VAC.

However, since 240VAC is "available" in every "properly wired" 50A pedestal receptacle, a 240V dryer can be used in any RV.........but only if the proper circuit breaker, wire and receptacle is added into the RV.

120V dryers, like this one: Whirlpool 3.4 cu. ft. 120V Electric Dryer - White : Sears Outlet, are available.

IMO using a 120V dryer would be more sensible, (and less expensive), than re-wireing an RV to use a 240V dryer....(AND a 120V dryer can be used with power from either a 30A or a 50A pedestal receptacle).

Mel
'96 Safari
mel s is offline   Reply With Quote
Old 01-04-2014, 05:14 PM   #24
Winnebago Camper
 
cmpncrsaider's Avatar
 
Join Date: Sep 2011
Location: New Jersey
Posts: 38
Quote:
Originally Posted by mel stuplich View Post
dengraham
I agree.
A 30A RV pedestal receptacle can't be used for any 240V appliance because it only provides 120VAC.

However, since 240VAC is "available" in every "properly wired" 50A pedestal receptacle, a 240V dryer can be used in any RV.........but only if the proper circuit breaker, wire and receptacle is added into the RV.

120V dryers, like this one: Whirlpool 3.4 cu. ft. 120V Electric Dryer - White : Sears Outlet, are available.

IMO using a 120V dryer would be more sensible, (and less expensive), than re-wireing an RV to use a 240V dryer....(AND a 120V dryer can be used with power from either a 30A or a 50A pedestal receptacle).

Mel
'96 Safari
I hear want your sayin but panel under the bed to location of new dryer is an easy run, 30 amp 2 pole breaker , 30 amp receptacle, and about 10' of #10 wire. That said 120 volt dryer is worth looking into for sure. Maybe I'll start a thread to see if people are happy with 120 volt dryer.
__________________
John and Vicki,2004 Winne Vectra 350 Cummins, 10k lb Blu Ox tow bar , 04 Dodge Ram 1500 4wd toad
cmpncrsaider is offline   Reply With Quote
Old 01-05-2014, 06:59 PM   #25
Winnebago Master
 
cbeierl's Avatar
 
Join Date: Aug 2005
Location: Nashua, NH
Posts: 1,823
Quote:
Originally Posted by cmpncrsaider View Post
I hear want your sayin but panel under the bed to location of new dryer is an easy run, 30 amp 2 pole breaker , 30 amp receptacle, and about 10' of #10 wire. That said 120 volt dryer is worth looking into for sure. Maybe I'll start a thread to see if people are happy with 120 volt dryer.
If you were to do that you would only be able to run the dryer when connected to a 50A shore line. A 30A or less shore line or your generator will only provide 120V. Overall it seems like a poor idea.
__________________
Chris Beierl

2005 Winnebago Vectra 36RD
cbeierl is offline   Reply With Quote
Old 01-05-2014, 07:12 PM   #26
Winnebago Camper
 
PushedAround's Avatar
 
Join Date: Sep 2012
Location: Ambler, PA
Posts: 36
Yes it is easy to rewire your dryer feed to 240 volts but before you do I would check on the wattage of the 120 volt dryer vs the 240 model. In the compact size there may not be much of a difference in performance. And as far as the poll goes, my DW loves the way our washer & dryer work. I don't know how we'd get through those damp rainy days without them.
__________________
Larry & Cheryl Oscar, Louie, Ranger & Henry (our Springers)
PushedAround is offline   Reply With Quote
Old 01-05-2014, 07:49 PM   #27
Winnie-Wise
 
dengraham's Avatar
 
Join Date: Sep 2005
Location: Crossville, Tennessee
Posts: 417
Chris,
I was thinking the same thing but I didn't know if it would not run at all, or if the heating elements would trip the breaker? I guess it would depend on the wiring of the specific dryer??
__________________
Dennis & Trish (and Sparky Doodle)
2013 Meridian 42E
2011 Ford Explorer
dengraham is offline   Reply With Quote
Old 01-06-2014, 09:56 AM   #28
Registered User
 
mel s's Avatar
 
Join Date: Mar 2010
Posts: 340
Quote:
Originally Posted by cbeierl View Post
If you were to do that you would only be able to run the dryer when connected to a 50A shore line. A 30A or less shore line or your generator will only provide 120V. Overall it seems like a poor idea.
cbeierl
You are correct that a 30A or less shore line will only provide 120V.
(I also believe that a using a 120V dryer makes the most sense).

However, some, (most?), RV generators provide two lines of 120VAC to the coach.
A properly wired 240V dryer receptacle in a coach with a generator providing 2 120V lines to the coach will/should get 240V from either a 50A shore power receptacle or from the generator.

Again, I recommend consulting an electrician before modifying the AC.

Mel
'96 Safari
mel s is offline   Reply With Quote
Old 01-06-2014, 03:01 PM   #29
Winnebago Master
 
cbeierl's Avatar
 
Join Date: Aug 2005
Location: Nashua, NH
Posts: 1,823
Quote:
Originally Posted by mel stuplich View Post
cbeierl
...
However, some, (most?), RV generators provide two lines of 120VAC to the coach.
A properly wired 240V dryer receptacle in a coach with a generator providing 2 120V lines to the coach will/should get 240V from either a 50A shore power receptacle or from the generator.
...
As far as I know the 5,500-watt Cummins Onan Marquis Gold generator in the OP's coach only outputs 120V.
__________________
Chris Beierl

2005 Winnebago Vectra 36RD
cbeierl is offline   Reply With Quote
Old 01-06-2014, 03:17 PM   #30
Winnebago Master
 
Mr_D's Avatar
 
Join Date: May 2011
Location: Vancouver, WA
Posts: 560
Quote:
Originally Posted by mel stuplich View Post
However, some, (most?), RV generators provide two lines of 120VAC to the coach.
A properly wired 240V dryer receptacle in a coach with a generator providing 2 120V lines to the coach will/should get 240V from either a 50A shore power receptacle or from the generator.

Again, I recommend consulting an electrician before modifying the AC.

Mel
'96 Safari
But a 50 amp RV circuit is two 120 feeds at 50 amps EACH, that's 12,000 watts. So, in order to use the full capacity you would need a 12,000 watt generator although you could use less IF you watched your usage.
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft
Charter Lifetime GS Member, SKP, FMCA,
RV'ing since 1957, NRA Benefactor Life, towing '14 CR-V
Mr_D is offline   Reply With Quote
Old 01-06-2014, 05:12 PM   #31
Registered User
 
mel s's Avatar
 
Join Date: Mar 2010
Posts: 340
Quote:
Originally Posted by Mr_D View Post
But a 50 amp RV circuit is two 120 feeds at 50 amps EACH, that's 12,000 watts. So, in order to use the full capacity you would need a 12,000 watt generator although you could use less IF you watched your usage.
Mr_D
There are 2 "out of phase" 120VAC 30A lines coming from my 6.3 KW Onan.
Since most 240 VAC dryers need less than 30A, 50A is not necessary.

But since neither you or I intend to use a 240V dryer in our RV, (because a 120V dryer makes more sense), it matters not!

Mel
Mel
mel s is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Spot free Rinse DennisLB Winnebago General Discussions 27 08-28-2008 05:57 AM
Winnebago's Heat shield that's Spot welded under chassis FrontRangeRVer General Maintenance and Repair 14 09-05-2006 05:26 AM

» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Winnebago Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 12:59 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.