On 50amp one circuit goes out

New 2018 Vista XL 35f. Hooked up 50amp shore power, hot day and both ACs running, tv on and the DW fires up the hair dryer and the system recognizes the draw and gently powers down the rear ac just like it is supposed to. Problem is the 30amp circuit for the rear ac won't come back up. Tried everything I could think of (circuit breakers both inside the coach and on the pole. Finally in desperation I unplugged the 50amp at the post, counted to 10, plugged it back in and every came back to normal. This happened a couple more times over the weekend. I also use a surge/polarity protector. Dealer says if it happens at another rv site, bring it in. Anybody know anything that might cause this or have a suggestion?
RvExplorer is offline   Reply With Quote
Old 06-11-2018, 08:17 PM   #2
Winnebago Camper
 
Join Date: Jan 2018
Posts: 32
Have the campground check their 50 amp breaker as one side of the breaker will have burned connects and the other side will be ok. The amp draw thru the burnt connects causes the system in the unit to shut down. I have seen this problem at several different rv parks.
Matterbery is offline   Reply With Quote
Old 06-11-2018, 09:04 PM   #3
Winnebago Master
 
Wayne M's Avatar
 
Join Date: Aug 2008
Location: Texas
Posts: 1,665
Low voltage on the pedestal (One leg) us most likely low. Could be from loose connections at the pedesal or arcing or loose connections at the distribution box.
__________________
Wayne MSGT USMC (Ret) & Earlene (CinCHouse)
2015 Winnebago Tour 42QD - 2020 Lincoln Nautilus Reserve (TOAD)
(RVM-14) It is what it is, and then it is what you make of it.
Wayne M is offline   Reply With Quote
Old 06-12-2018, 08:45 AM   #4
2018 Vista 35f
 
Join Date: Apr 2018
Location: Wenatchee WA
Posts: 17
Thanks to both of you. This happened on the maiden voyage. We set out again in a couple of week and will have 50 amp service in a very nice park so that will be a good test.
RvExplorer is offline   Reply With Quote
Old 06-12-2018, 09:27 AM   #5
Winnebago Master
 
jerichorick's Avatar
 
Join Date: Jun 2013
Location: Full-timer/volunteer w/SOWERS
Posts: 2,734
Quote:
Originally Posted by RvExplorer View Post
New 2018 Vista XL 35f. Hooked up 50amp shore power, hot day and both ACs running, tv on and the DW fires up the hair dryer and the system recognizes the draw and gently powers down the rear ac just like it is supposed to. Problem is the 30amp circuit for the rear ac won't come back up. Tried everything I could think of (circuit breakers both inside the coach and on the pole. Finally in desperation I unplugged the 50amp at the post, counted to 10, plugged it back in and every came back to normal. This happened a couple more times over the weekend. I also use a surge/polarity protector. Dealer says if it happens at another rv site, bring it in. Anybody know anything that might cause this or have a suggestion?

One of the common problems with all electrical systems, especially the new builds, is loose wire connections in the ATS and service panel. For the older, many miles on the road, rigs it is simply vibration that loosens the screws. For the new builds it is poor attention given by the installers of the equipment.


On of the more common, and most expensive, failures is when the neutral from the pedestal comes loose. This puts 240VAC onto your service panel. The inverter and MW usually fail under this condition. For this reason alone I check my electrical connections each year. Which reminds me. Time for the check.
__________________
Rick & Melissa Young & Dawson (RIP), 2011 Meridian 40U, FL XCL, ISL 380HP/DEF, Al 3000 MH, 2014 Honda CR-V, SMI AF1, Blue Ox TruCenter & tow equip.,EEZTire TPMS.
Servants On Wheels Ever Ready. Best job we ever paid to do . (full time volunteers)
jerichorick is offline   Reply With Quote
Old 06-12-2018, 09:58 AM   #6
2018 Vista 35f
 
Join Date: Apr 2018
Location: Wenatchee WA
Posts: 17
At the risk of sounding dumb, what is the ATS and where would I find these screw connections that I should keep and eye on?
RvExplorer is offline   Reply With Quote
Old 06-12-2018, 11:00 AM   #7
Winnie-Wise
 
luvlabs's Avatar
 
Join Date: Feb 2012
Location: Las Cruces, NM
Posts: 415
The ATS (Automatic Transfer Switch) is located where your shore power cord comes into the RV. The loose connections being referred to are in the ATS with the connections to the shore cord, the generator, and the main power cord back into the RV.

You can check these pretty easily and safely - unplug the shore power cord, make sure the generator is off, and remove the cover to the ATS. Using the appropriate tool, check the tightness of each connection. They don't have to be gorilla tight, just snug.
__________________
Roger & Mary
2017 Winnebago Navion 24V
2014 Tiffin Phaeton 36GH (Sold)
luvlabs is offline   Reply With Quote
Old 06-16-2018, 04:47 PM   #8
Winnebago Master
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 2,039
Quote:
Originally Posted by luvlabs View Post
The ATS (Automatic Transfer Switch) is located where your shore power cord comes into the RV. The loose connections being referred to are in the ATS with the connections to the shore cord, the generator, and the main power cord back into the RV.

You can check these pretty easily and safely - unplug the shore power cord, make sure the generator is off, and remove the cover to the ATS. Using the appropriate tool, check the tightness of each connection. They don't have to be gorilla tight, just snug.
I might add, make sure your inverter is off, otherwise one might have a shocking time tightening the screws.
__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA 1SG, retired;PPA,Good Sam Life member,FMCA. "We the people are the rightful masters of both the Congress and the Courts - not to overthrow the Constitution but to overthrow men who pervert the Constitution." Abraham Lincoln
Ray,IN is offline   Reply With Quote
Old 06-16-2018, 05:46 PM   #9
Retired Sailor and Wench
 
Join Date: Feb 2018
Location: Crowley, TX
Posts: 32
Newbie Question:

Is the ATS the relay I hear activate when I plug in or unplug shore power?
Tailhooker is offline   Reply With Quote
Old 06-16-2018, 06:04 PM   #10
Winnebago Master
 
SarahW's Avatar
 
Join Date: Oct 2011
Location: Houston TX
Posts: 881
Quote:
Originally Posted by Tailhooker View Post
Newbie Question:

Is the ATS the relay I hear activate when I plug in or unplug shore power?
Yes. A slight "thump."
SarahW is offline   Reply With Quote
Old 06-16-2018, 06:19 PM   #11
Retired Sailor and Wench
 
Join Date: Feb 2018
Location: Crowley, TX
Posts: 32
Thanks SarahW - a slight "thump" is what I hear!
Tailhooker is offline   Reply With Quote
Old 06-17-2018, 08:07 AM   #12
Winnebago Master
 
jerichorick's Avatar
 
Join Date: Jun 2013
Location: Full-timer/volunteer w/SOWERS
Posts: 2,734
I have been thinking about this problem a bit. Here are some general thoughts.


1/ Try not to plug into a hot service. If you miss the neutral, even briefly, you could damage your electrical system.
2/ Watch the power monitoring panel voltage as the loads come on line. You should not see the voltage drop below 110V at any time. If it does there is a poor connection someplace or a problem with the park power.
3/ On 30A or generator loads will be shed automatically by the EMS (energy management system). In the case of the generator, the breaker on it may trip if the loads are too great.
4/ My coach has a great feature. On 30A, if the shore power is maxing out, the inverter will supply supplement power. I have seen it do this a few times when running the microwave.
__________________
Rick & Melissa Young & Dawson (RIP), 2011 Meridian 40U, FL XCL, ISL 380HP/DEF, Al 3000 MH, 2014 Honda CR-V, SMI AF1, Blue Ox TruCenter & tow equip.,EEZTire TPMS.
Servants On Wheels Ever Ready. Best job we ever paid to do . (full time volunteers)
jerichorick is offline   Reply With Quote
Old 06-17-2018, 12:35 PM   #13
Winnebago Master
 
grtharris's Avatar
 
Join Date: Apr 2003
Location: Skiatook, OK
Posts: 1,460
RvExplorer When you are connected to a 50 amp service none of the loads will shed/turn off. As mentioned above somewhere in the electrical system, more than likely the power pestle, you where loosing one leg of the 50 amp service and ending up with a single leg of a 30 amp service.
__________________
Grant & Pat
2014 Adventurer 35P
2021 Rapid Red 4dr Bronco OBX
grtharris is offline   Reply With Quote
Old 06-18-2018, 07:58 AM   #14
Winnie-Wise
 
Join Date: Apr 2016
Posts: 286
I agree that the problem is likely a lost leg, or some other problem, in the pedestal but if OP is using a surge protector, don't all of them have indicator lights that show the source of a problem? I believe I would have headed right to the protector to see what is was indicating. Just a thought.
Upinsmoke is offline   Reply With Quote
Old 06-18-2018, 08:39 AM   #15
2018 Vista 35f
 
Join Date: Apr 2018
Location: Wenatchee WA
Posts: 17
I don't recall seeing any change in the lights on the surge protector. Odds are its the pedestal. Its at a private yacht club installed by a lot of volunteer labor. I head out this Wed to a nice park with 50 amp and we will see if the problem arises again. Thank you all again for the tips!!
RvExplorer is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
30amp or 50amp?? Greybeard Electrical | Charging, Solar and Electronics 12 07-15-2008 08:57 AM
Coiled 50amp electric cable whyoder Electrical | Charging, Solar and Electronics 12 06-26-2008 09:20 AM
Power Line One Panel Limits One Leg 50 Amp circuit to 30 Amps SteveG Electrical | Charging, Solar and Electronics 17 03-05-2008 04:43 PM
living room slide goes out crooked peter griffin General Maintenance and Repair 8 05-31-2007 05:32 PM
LP Furnace blew out circuit board panel? SOLVED - See last page!!! Old Snipe General Maintenance and Repair 15 10-07-2006 08:49 AM

» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Winnebago Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 03:41 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.