Powerline 2004 Energy Maintenance reading incorrectly

Before I call the RV Doctor, thought I would lean on the collective wisdom of the forum.

We are running a 2007 Journey 34SH. When parked at our bricks n sticks we normally keep her plugged into a 50 amp supply and she functions as a guest house. We are leaving for our spring trip next week, and noticed that the Powerline service type display only indicates 30 amp. All four of the systems in the Power Status window are indicating normally. Our SurgeGard 35550 indicates both legs are hot, to me that means the issue is downstream of it.

Anyone have any constructive thoughts?

Now that I think of it, We have two other things that cause us to go hmmmm, but will open separate threads for each.
Oldchinahand is offline   Reply With Quote
Old 04-28-2017, 06:00 PM   #2
Winnie-Wise
 
Join Date: Jul 2006
Location: Michigan
Posts: 471
Here's a 3 page thread on the subject...

http://www.irv2.com/forums/f101/plug...-a-295651.html
__________________
Ed & Joie
2004 Vectra 40KD
Freightliner Chassis and Cummins ISC
emiddleb is offline   Reply With Quote
Old 04-28-2017, 07:20 PM   #3
Winnebago Master
 
grtharris's Avatar
 
Join Date: Apr 2003
Location: Skiatook, OK
Posts: 1,467
Oldchinahand First check to see if any 110 VAC beaker are turned off.
__________________
Grant & Pat
2014 Adventurer 35P
2021 Rapid Red 4dr Bronco OBX
grtharris is offline   Reply With Quote
Old 04-28-2017, 11:01 PM   #4
Winnebago Master
 
Oldchinahand's Avatar
 
Join Date: Mar 2017
Location: Tucson, AZ
Posts: 535
thanks. sounds like dnystrom and I ave the same problem. I have laid a voltmeter across my supply and am confident in it. Plus, the my surgegard reads correctly. Am going through every 125v breaker I can find including the two 50amp breakers on the power center.

Much like avoiding packrats, I am doing anything, everything anyone says (that sounds logical to an old main space engineer) :-)
Oldchinahand is offline   Reply With Quote
Old 04-30-2017, 06:38 PM   #5
Winnebago Master
 
Oldchinahand's Avatar
 
Join Date: Mar 2017
Location: Tucson, AZ
Posts: 535
Thanks to all. Problem seems to be resolved. In the interest of sharing results with others having this issue, grtharris was on point. beginning at the 50amp service, I hand over handed from the 50amp service, through the hardwired surgegard, through the ABT and on to the power center located under the bed. All was visually OK. So I turned off the 50 amp service, went back through the system, closed all 125v breaker then opened them, turned back on the 50 amp service. Zip! Powerline still indicating only 30amp. So then I closed and opened all the 125v breakers with the 50amp service on. Magic! Powerline indicated receiving 50 amp. So, I turned off the 50amp service, waited a few minutes, turned the 50 amp back on. Magic again! Powerline reads receiving 50amp. So the fix seems to be cycling the 125v breakers with the 50amp service on. Why? I don't know. I don't know why kids and dogs like me either. Which one of the breakers was the culprit? Don't know that either. Can't see the Powerline from the power center. If happens again, will have she-who-must-be-obeyed assist while I cycle breakers one at a time.
Oldchinahand is offline   Reply With Quote
Old 04-30-2017, 09:45 PM   #6
Winnebago Master
 
cbeierl's Avatar
 
Join Date: Aug 2005
Location: Nashua, NH
Posts: 1,823
According to the 110 Volt Load Center/Auto Transfer Switch diagram for your coach the Engine Heater circuit breaker (rightmost 15A breaker) must be on for the EMS to function correctly. See the note "/8\" on the lower left of page 5 of the pdf and the corresponding symbol in the upper right of the same page indicating the breaker involved.

You should be able to test this by connecting to 50A shore power and turning off that breaker--the EMS panel should revert to 30A. If you turn the breaker back on it should correctly display 50A service.
__________________
Chris Beierl

2005 Winnebago Vectra 36RD
cbeierl is offline   Reply With Quote
Old 05-01-2017, 02:38 PM   #7
Winnebago Master
 
Oldchinahand's Avatar
 
Join Date: Mar 2017
Location: Tucson, AZ
Posts: 535
Great guidance Chris! So simple when you read the tech manual. Proves the old adage, even rocket science is not rocket science to a rocket scientist. Added the diagrams to my tech library.

Now, we should just relax and enjoy our new knowledge (here comes the but monkey), but I know that the navigator and I will cover many road miles discussing the logic of having that particular function of the EMS controlled by the Engine Block Heater circuit breaker. Rhetorical statement.
Oldchinahand is offline   Reply With Quote
Old 05-01-2017, 03:11 PM   #8
Winnebago Master
 
cbeierl's Avatar
 
Join Date: Aug 2005
Location: Nashua, NH
Posts: 1,823
Actually the reason is the EMS needs to monitor the power lines of one circuit on the 'other' leg of 50A system (2 separate 120V circuits, 180deg out of phase with each other)--that's how it can detect 50A vs 30A (which is all one leg and therefore the same phase in all circuits).
__________________
Chris Beierl

2005 Winnebago Vectra 36RD
cbeierl is offline   Reply With Quote
Old 05-01-2017, 09:07 PM   #9
Winnebago Master
 
DancinCampers's Avatar
 
Join Date: Nov 2004
Location: On the Road Westward
Posts: 711
On my previous 2003 Adventurer it was the water heater breaker.
__________________
Dan & Sharon & Kasey (Our Yorkie Puppy (12 Yrs Old) On the Road (2012 Journey 36M, 2006 Jeep Liberty)
USN-Ret ('65-'93) Fulltimers, Class of 2012
DancinCampers is offline   Reply With Quote
Reply

Tags
maintenance, power


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Powerline Energy Management System and surge protection macnut Electrical | Charging, Solar and Electronics 27 12-01-2016 10:05 AM
Smart Energy Management system not reading 50 amp power CWHTRAINS Electrical | Charging, Solar and Electronics 21 08-29-2016 06:29 AM
Problem with Intellitec Powerline Energy Mgmt System Hikerdogs Electrical | Charging, Solar and Electronics 8 08-05-2012 04:39 PM
Powerline Energy Mgmt System Prob Matt1616 Electrical | Charging, Solar and Electronics 8 04-12-2006 04:35 PM

» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Winnebago Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 06:59 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.