Old 08-21-2008, 01:49 PM   #1
Winnebago Camper
 
Join Date: Aug 2008
Posts: 15
Any REAL WORLD experience would be helpful...I'm attempting to figure-out the pros and cons of having a LP generator versus having a gasoline generator in a Class "C" Winnebago. Does the LP tank empty more quickly. If so, how much more quickly? How long can I expect a LP generator to run on a full tank of propane (assuming Air Conditioner is ON and intermittent use of other electrical appliances)? Is the somewhat lower wattage output of the LP generator significant?
TrailerFool is offline   Reply With Quote
Old 08-21-2008, 01:49 PM   #2
Winnebago Camper
 
Join Date: Aug 2008
Posts: 15
Any REAL WORLD experience would be helpful...I'm attempting to figure-out the pros and cons of having a LP generator versus having a gasoline generator in a Class "C" Winnebago. Does the LP tank empty more quickly. If so, how much more quickly? How long can I expect a LP generator to run on a full tank of propane (assuming Air Conditioner is ON and intermittent use of other electrical appliances)? Is the somewhat lower wattage output of the LP generator significant?
TrailerFool is offline   Reply With Quote
Old 08-21-2008, 05:21 PM   #3
Winnebago Master
 
Join Date: Sep 2005
Posts: 962
This webpage shows some of the information that you are looking for

Onan LP Genset

I believe that most LP tanks can be filled to 80% of their nominal capacity ... so if you have a 20 gallon LP tank ... the most it can contain is 16 gallons of LP. One of the disadvantages of LP gen sets is that you can't bring a 5 gallon can of LP to you motorhome when you run out ...

You need to check to see if the amperage is sufficient to run the air conditioning unit ... make sure that the gen set has enough power for the start up ... AC always have a large load at start up ...
skigramp is offline   Reply With Quote
Old 08-21-2008, 06:08 PM   #4
Winnebago Camper
 
Join Date: Aug 2008
Posts: 15
Hmmm....is that what class "C" Winnebago/Itasca Diesel motorhomes come with - a 20gal LP tank? Is that a dedicated tank for the LP generator (separate from the other LP tank(s)?
TrailerFool is offline   Reply With Quote
Old 08-21-2008, 06:20 PM   #5
Winnebago Owner
 
RedT's Avatar
 
Join Date: Sep 2000
Posts: 126
I think the real answer to your question lies in your usage - and the difference in cost between propane power and gasoline or diesel power genset.

For me, I seldom use a genset, therefore the ~$4,000 extra cost for the diesel generator did not make sense. Having said that, diesel or gasoline has more BTU's than propane. A propane genset running under a load will burn approx 1 gallon per hour. My experience with the propane genset is that it starts easily, provides plenty of power and has been trouble-free for five years.
__________________
RedT, US Air Force Retired
2004 Itasca Meridian VMSpc, Pressure Pro TPMS
2003 Jeep Liberty M&G Brakes System
RedT is offline   Reply With Quote
Old 08-21-2008, 07:01 PM   #6
Winnebago Owner
 
Join Date: Apr 2007
Posts: 115
LP gensets require less maintenace because lp is a dry fuel but have about 10 to 20% less watts for same gen on gas. Fuel usage will depend on gen size and load. Typical RV gensets use from 1/3 to 1 gal per hour. If genset is mounted in rv makes sence to run on rv motor fuel gas or diesel hope this heps.
__________________
2001 Horizon 2004 jeep GC
autofish is offline   Reply With Quote
Old 08-21-2008, 08:34 PM   #7
Winnebago Owner
 
porscheracer's Avatar
 
Join Date: Apr 2008
Location: Back at the stix'n'brix - East End, AR.
Posts: 197
I would only consider an LP generator if I didn't plan to use it - ever. It would be handy as a backup - but running full time at high load on a typical class C LP tank (16 gallons usable is about right), you'd be lucky to get 24 hours' use. Whan you're out of propane, you're out of everything - no electricity, refrigeration, cooking . . . nothing but gas to go get more propane.

I prefer diesel, but they're only available / practical if you have a diesel MH. And the only diesel C Winnebago makes is the View. As a comparison, the 7500W diesel in my Vectra uses about 10 gallons a day, full time boondocking at 90+ degrees, with the AC going as hard as it will go - plus all the other normal living usages. In other words - easy to make a full week on 4/5 of a tank of fuel (before the low fuel shutoff) - and by that time we're out of water and the holding tanks are full.
__________________
Norm & Janet

FMCA; WIT; FCOA; Good Sam; Passport
porscheracer is offline   Reply With Quote
Old 08-22-2008, 06:01 AM   #8
Winnebago Camper
 
Join Date: Aug 2008
Posts: 15
I wonder why Winnebago's Diesel "C" motorhomes (I'm only looking at used models) are only available with an LP generator. It seems like a diesel generator on those models would make perfect sense!
TrailerFool is offline   Reply With Quote
Old 08-22-2008, 08:45 AM   #9
Winnebago Owner
 
porscheracer's Avatar
 
Join Date: Apr 2008
Location: Back at the stix'n'brix - East End, AR.
Posts: 197
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by TrailerFool:
I wonder why Winnebago's Diesel "C" motorhomes (I'm only looking at used models) are only available with an LP generator. It seems like a diesel generator on those models would make perfect sense! </div></BLOCKQUOTE>

They were available with diesel generators. However, since the majority of C's sold are dealer stock items, the dealers are reluctant to add $5000 or so to the price for the diesel over the LP. There's always the (not inexpensive) option of retrofitting.
__________________
Norm & Janet

FMCA; WIT; FCOA; Good Sam; Passport
porscheracer is offline   Reply With Quote
Old 08-22-2008, 07:50 PM   #10
Winnebago Camper
 
Join Date: Aug 2008
Posts: 15
Is it possible to add a second LP tank to fix the LP capacity problem related to the LP generator?
TrailerFool is offline   Reply With Quote
Old 08-23-2008, 02:55 AM   #11
Winnebago Master
 
Join Date: Sep 2005
Posts: 962
People who stay in one spot for extended periods of time use one of these

LP extended stay adaptor

You could use one of these with a small LP tank like you have on your BBQ grill
skigramp is offline   Reply With Quote
Old 08-23-2008, 05:32 PM   #12
Winnebago Camper
 
Darryl's Avatar
 
Join Date: Nov 2006
Location: Smyrna, GA
Posts: 12
The LP generator is a good unit, and works well. You might also avoid some the the carb problems that the gasoline units can get from not being exercised regularily. However, it is a big issue if you dry camp. About 1 24 hr day or slightly more, depending on your usuage, is about all you will get with most LP tanks.

This is a big problem if you go to dog shows like me. Most shows are 3 or 4 days. This is a well known issue amongst the show people and also the reason most opt for either gasoline gen sets or diesel (if the coach is diesel). Unfortunaley, I have a diesel coach which I love, but it came with an LP genset which I hate. As a consequence, I only go to dry-camp dog shows in early spring or late fall, so I have a small, limited time that I need air conditioning. If I don't need A/C but 3 or 4 hrs a day, it works out just fine.
__________________
Darryl
Smyrna GA
Darryl is offline   Reply With Quote
Old 08-23-2008, 06:16 PM   #13
Winnebago Owner
 
porscheracer's Avatar
 
Join Date: Apr 2008
Location: Back at the stix'n'brix - East End, AR.
Posts: 197
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by skigramp:
People who stay in one spot for extended periods of time use one of these

LP extended stay adaptor

You could use one of these with a small LP tank like you have on your BBQ grill </div></BLOCKQUOTE>

A small (20#) LP tank would run a generator for maybe 4 hours, on moderate load. Rather an expensive way to go. If you're going to be using it much, I'd think a retrofit would be more cost effective in the long run - never mind the convenience.

BTW - and totally OT - skigramp . . . we were through your fine town about 2.5 weeks ago, after staying a couple of nights at Fond Du Lac, and on the way to the Keweenaw.
__________________
Norm & Janet

FMCA; WIT; FCOA; Good Sam; Passport
porscheracer is offline   Reply With Quote
Old 10-02-2008, 04:52 AM   #14
Winnebago Owner
 
Join Date: Oct 2007
Posts: 193
I have a a lp generator on diesel coach. I have spent over $10 an hour to keep it running. On the frits again. I don't run it that much because there is always something wrong with it. I will run it every month even if we aren't using it, but most of the time it doesn't work.

My solution is, I carry a Honda 2000 watt generator with me that we have probably well over 5,000 hours on it. I keeps the batteries topped off, will run the microwave if tv is not on. We never run the AC with it, but turn on all the exhaust fans, open the windows, and have a Vornado fan running in hot weather. Will usually keep the coach within 5 degrees or less of outside temps. This would be 5 degrees warmer than outside. We just learned to live with the temps.

We dry camp close to 6 months a year.

Honda generator will usually give us 10-12 hours on a gallon of fuel, also extremely quiet. You can stand right over it and carry on a conversation.
__________________
2008 Winnebago Vectra 40TD

1999-2008 traded in Suncruiser 90,000 miles
Jeeperrmartin is offline   Reply With Quote
Old 10-02-2008, 07:17 AM   #15
Winnebago Master
 
tderonne's Avatar
 
Join Date: Dec 2003
Location: Motor City, Mich
Posts: 1,004
"Class C Winnebago Diesel"

Do you mean Dodge Sprinter based stuff? Or perhaps the rare Ford Powerstroke equipped F350/450 one?

2008 View/Navions offered a diesel generator as an option. No diesel was available before that on them. I suspect the lack of a small diesel generator also means that the Ford based ones would all be LP generators.
__________________
Tim.

tderonne is online now   Reply With Quote
Old 10-02-2008, 07:21 AM   #16
Registered User
 
Join Date: Jun 2005
Posts: 729
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by TrailerFool:
I wonder why Winnebago's Diesel "C" motorhomes (I'm only looking at used models) are only available with an LP generator. It seems like a diesel generator on those models would make perfect sense! </div></BLOCKQUOTE>

Please double check on that. I believe that you can get the diesel generator as an option on the Dodge based Sprint Chassis.

For us, having a propane generator would be a deal killer.
FrontRangeRVer is offline   Reply With Quote
Old 10-02-2008, 11:48 AM   #17
Winnebago Owner
 
porscheracer's Avatar
 
Join Date: Apr 2008
Location: Back at the stix'n'brix - East End, AR.
Posts: 197
It's a matter of usage - as I've stated. We have an Onan Quiet Diesel 7500 on the Vectra, and it has ~1600 hours on it (in ~3 years). Cost of operation is approximately 1/2 gallon of diesel an hour, plus oil and filter changes - about $0.50/hour netted out. It is powerful, flexible and quiet. The only downside is it still smells like a diesel.

Our '08 View has the optional Onan 3500 Diesel. It is nowhere the unit that the QD is (nor the price). It is not as quiet as any of the premium diesel or gas (Honda), more along the line of a traditional 4KW gas MH generator (although significantly quieter than our 6500 Emerald on the LQ trailer). I'd have no problem running the Vectra one in a moderately quiet area - like a parking lot - not so the one on the View. It does, however, seem to only use about a quart an hour of fuel.

Why do we need a big genset? Over 50% or our "boondocking" is at sports car races, on paement in the paddock area, where absolutely no electricity is available. The ambient air temperatures range (frequently) into the 110* degree range, and there is NO shade. Alternatively, we may be in any sort of weather

We are on site for anywhere from 60 to 150 hours at a time. So, everybody who touts diesels isn't crazy!!
__________________
Norm & Janet

FMCA; WIT; FCOA; Good Sam; Passport
porscheracer is offline   Reply With Quote
Old 10-02-2008, 05:16 PM   #18
Winnebago Master
 
tderonne's Avatar
 
Join Date: Dec 2003
Location: Motor City, Mich
Posts: 1,004
Warning off topic...

I hear Topeka does have quite a parking lot to run that generator in. After 12 years of RunOffs, Topeka just didn't seem worth it. Road America....hmmmm....

Tim
(HP Festiva sitting in the garage)
__________________
Tim.

tderonne is online now   Reply With Quote
Old 10-02-2008, 06:05 PM   #19
Winnebago Owner
 
porscheracer's Avatar
 
Join Date: Apr 2008
Location: Back at the stix'n'brix - East End, AR.
Posts: 197
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by tderonne:
Warning off topic...

I hear Topeka does have quite a parking lot to run that generator in. After 12 years of RunOffs, Topeka just didn't seem worth it. Road America....hmmmm....

Tim
(HP Festiva sitting in the garage) </div></BLOCKQUOTE>

Yeah - all 200 hotel rooms in Elkhart Lake should be pretty busy next year.
__________________
Norm & Janet

FMCA; WIT; FCOA; Good Sam; Passport
porscheracer is offline   Reply With Quote
Old 10-02-2008, 06:19 PM   #20
Winnebago Camper
 
chasfm11's Avatar
 
Join Date: Mar 2004
Location: DFW Area, TX
Posts: 16
We have an LP genset (Onan 6.5K). It came with our used Class A. It runs both A/C units (13.5)just fine but as pointed out, it will suck about 1 gallon per hour if it is really hot outside. Most of the time, we use the genset to power just one A/C while driving in hot weather and it runs about 1/3 gallon per hour. We have 38 gallon take so, under most conditions, we can use both A/C for about 30 hours continuously on one tank.(remember it is 80% fill).

If we were locked in for several days in one place, the Lp genset would be a pain. I'd prefer diesel, where I could jerry jug in fuel if I needed to. We haven't really had that condition in the 4 years we've had the RV so the only annoyance is having to stop where they have propane and diesel on the road. Flying Js are great for that. Without those, sometimes we have to hit towns to find a propane distributor and some of those lots aren't very big - for a MH and toad.
__________________
2000 Georgie Boy Landau 36' DP
2005 Saturn Vue toad
KF5-NJY
chasfm11 is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
HI Winnebagoers !? Looking for full-time class A Mid-2000's 00wabbit Winnebago General Discussions 20 03-18-2013 05:32 AM
Frig will not run on generator... azloafer Electrical | Charging, Solar and Electronics 11 06-25-2010 12:32 AM
Goodbye class C, c'mon class A ghostrider General Maintenance and Repair 7 07-28-2009 08:06 AM

» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Winnebago Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 12:57 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.