Old 06-28-2018, 08:08 PM   #1
Winnebago Camper
 
wegobago's Avatar
 
Join Date: Feb 2018
Posts: 20
Generator breaker won't stay set

So just got back from 2700 mile trip, no problems. We were cleaning the rig, running the generator with 1 roof air on, brought vacum in, completeday that chore, unpluged it ,generator speeded up a bit air went off, tripping the breaker on the side of the generator, the 30 amp one, now that breaker won't stay on no matter what you do, probably fried something, any ideas, thanks
wegobago is offline   Reply With Quote
Old 06-28-2018, 09:06 PM   #2
Winnie-Wise
 
Tucsontoy's Avatar
 
Join Date: Feb 2018
Location: Tucson, AZ
Posts: 267
Do you have any shore power on? The gen may not like seeing it with a ATS.
__________________
2017 View 24V
Tucsontoy is offline   Reply With Quote
Old 06-28-2018, 09:48 PM   #3
Winnebago Camper
 
wegobago's Avatar
 
Join Date: Feb 2018
Posts: 20
No, just genet running, seems that a vacuum wouldn't pull any more juice than a microwave, and I've run them together before
wegobago is offline   Reply With Quote
Old 06-29-2018, 05:57 AM   #4
Winnebago Master
 
Join Date: Dec 2007
Posts: 992
Quote:
Originally Posted by wegobago View Post
So just got back from 2700 mile trip, no problems. We were cleaning the rig, running the generator with 1 roof air on, brought vacum in, completeday that chore, unpluged it ,generator speeded up a bit air went off, tripping the breaker on the side of the generator, the 30 amp one, now that breaker won't stay on no matter what you do, probably fried something, any ideas, thanks
The CB won't stay on with all 120V loads off?? Or is just when the A/C on and the vacuum plugged in?
Try turning off the 120V CB's in your main power panel and start the generator and then start turning on the CB's one at a time.
What year and model RV do you have and which generator model?
__________________
Al & Sharon
2006 Winnebago Journey 36G
https://downtheroadaroundthebend.blogspot.com/
al1florida is offline   Reply With Quote
Old 06-29-2018, 09:02 AM   #5
Winnebago Owner
 
Join Date: May 2018
Posts: 221
Thermal circuit breakers can wear during trips. When I did AC service after two or three trips the breaker is weakened and won't hold. But it tripped for a reason and loose electrical connections is the number one cause.
Mike Owens is offline   Reply With Quote
Old 06-29-2018, 09:59 AM   #6
Winnebago Camper
 
wegobago's Avatar
 
Join Date: Feb 2018
Posts: 20
Thank you ,I will try that method, hopefully that will narrow down some possible issues.
wegobago is offline   Reply With Quote
Old 06-29-2018, 10:03 AM   #7
Winnebago Camper
 
wegobago's Avatar
 
Join Date: Feb 2018
Posts: 20
That makes a lot of sense, the coach is 20 years old, excellent condition but connection issue's could be it . Hopefully nothing got hurt too bad
wegobago is offline   Reply With Quote
Old 06-29-2018, 10:10 AM   #8
Winnebago Camper
 
wegobago's Avatar
 
Join Date: Feb 2018
Posts: 20
Our coach is a 98 Adventurer 35WP and the generator is a Onan Emerald plus 5000
wegobago is offline   Reply With Quote
Old 06-29-2018, 12:59 PM   #9
Winnebago Master
 
Join Date: Dec 2007
Posts: 992
BTW, are you able to plug into shore power, even 15amp household circuit, to see if any breakers trip?
__________________
Al & Sharon
2006 Winnebago Journey 36G
https://downtheroadaroundthebend.blogspot.com/
al1florida is offline   Reply With Quote
Old 06-30-2018, 11:30 AM   #10
Winnebago Camper
 
wegobago's Avatar
 
Join Date: Feb 2018
Posts: 20
Ats fried

Found source of tripping breaker, ats is fried, any opinions on replacement type and style are welcome. Currently have hard wired surge protection for shore power
wegobago is offline   Reply With Quote
Old 07-05-2018, 07:00 AM   #11
Winnebago Master
 
jerichorick's Avatar
 
Join Date: Jun 2013
Location: Full-timer/volunteer w/SOWERS
Posts: 2,734
Quote:
Originally Posted by wegobago View Post
Found source of tripping breaker, ats is fried, any opinions on replacement type and style are welcome. Currently have hard wired surge protection for shore power

Fried usually means the connections were loose. Try checking out ebay: https://www.ebay.com/bhp/rv-transfer-switch


Is your rig 30 or 50A? That model had a 50A option.
__________________
Rick & Melissa Young & Dawson (RIP), 2011 Meridian 40U, FL XCL, ISL 380HP/DEF, Al 3000 MH, 2014 Honda CR-V, SMI AF1, Blue Ox TruCenter & tow equip.,EEZTire TPMS.
Servants On Wheels Ever Ready. Best job we ever paid to do . (full time volunteers)
jerichorick is offline   Reply With Quote
Old 07-05-2018, 10:40 AM   #12
Winnie-Wise
 
Journey39n's Avatar
 
Join Date: Jul 2010
Location: on a constant, around the country, trip!
Posts: 404
ATS, fried, you might need to be more specific. Considering the age of your unit, it is quite likely it does need to be replaced. But here is my story on an ATS failure. Totally my own fault, mind you.

The day was very hot, 90's. We had just driven into town, parked in our favorite Casino Parking lot. We turned the generator on, running A/C full blast to cool things down. All was running great.

Friends showed up, lets go, the restaurant will be crowded, go, go, lets go. I reached up and turned the generator off. As my hands left the switch, I knew I blew it. I always would raise the thermostat first to shut off the a/c before turning the generator off. It was one of those slap the forehead moments. But nothing to be done then, off to dinner with friends.

Upon our return later in the evening, started up the generator, running normally, but in its usual 30-40 seconds, the lights did not come on the power management panel indicating the gen-set and power loads. I restarted the generator several times, sometimes the lights would come on, then off, flash strangely, randomly, very odd. It was a hot night!

Next day, tried it again, worked for about 1 minute with the a/c on, then the power management lights blinked randomly, and the a/c and other 120v power was gone. OK, I knew it must be the ATS, I knew I must have fried the connections when shutting the generator off with the a/c going full blast the day before. My RV dealer just happened to be a mile away, so, we drove over, but they were booked solid for the day. One of the techs said, we might try plugging into one of their shore power poles and see what happens. We did, and the power management panel came on, all 120v systems were normal.

So, we travelled on to our next campground, plugged into shore power, all was good. Over the next three weeks, I started the generator several times, each time, the power management panel would work, a few minutes, or longer, start acting up, and shut off. But gradually, with generator power, it got better and better. But I knew I "fried' those connectors in the ATS on the generator side of the box.

Over the next few months, we used the generator sparingly, again, it would work most of the time, but still glitches from time to time. I know its possible to get inside the ATS unit and clean up the contacts, but I saw a chance to buy a new exact match ATS from Amazon as a clearance, discontinued model, and bought one. It has been riding around as a spare for the last three years. The generator and old ATS has been working perfectly with dozens of starts and over 250 hours use since the original incident.

So in my case, the ATS being fried was not a permanent problem.
__________________
2010 Journey 39n - 2017 Jeep Cherokee Trailhawk - this our 13th year living aboard, travelling and visiting the Pacific NW, summer 2023
Journey39n is offline   Reply With Quote
Old 07-15-2018, 08:38 AM   #13
Winnebago Camper
 
wegobago's Avatar
 
Join Date: Feb 2018
Posts: 20
Our unit has 2 ATS boxes on board, one for coach power and the other for rear air only. I replaced the main ats , started generator and heard a pop which tripped the breaker on the generator. Wondering if maybe some loose connections on generator sidea may be an issue, after all we just completed a 2700 mile trip ,running the generator and air all day, lots of vibration
wegobago is offline   Reply With Quote
Old 07-16-2018, 08:54 AM   #14
Winnebago Master
 
jerichorick's Avatar
 
Join Date: Jun 2013
Location: Full-timer/volunteer w/SOWERS
Posts: 2,734
Quote:
Originally Posted by wegobago View Post
Our unit has 2 ATS boxes on board, one for coach power and the other for rear air only. I replaced the main ats , started generator and heard a pop which tripped the breaker on the generator. Wondering if maybe some loose connections on generator sidea may be an issue, after all we just completed a 2700 mile trip ,running the generator and air all day, lots of vibration
They did things a bit different in '98. You have a A/C select switch and a ATS. The ATS is for putting the service panel on generator or shore power. The A/C switch selects the unit being controlled from the thermostat, I believe.

I have a delay circuit built into one of the units so two won't try to start at the same time. This would cause an overload and trip breakers.
I highly recommend that we all go through our ATS and service panel, tightening connections soon after taking delivery. After being on the road for some time it is a good idea to do this again. I have done this enough times now that I am confident that I will not have any loose connection issues to be concerned about soon. I'll simply go through thing in a couple of years or so just because. Also, operate all of the breakers once a year.
In your case you could have a wire that has chafed and is grounding out. It might be a good idea to use a volt meter to troubleshoot with. I would remove the lead from the tripping breaker and measure the resistance of it to ground. If it is very low find where it goes and open the circuit someplace in the middle. Test in both directions to see which way the trouble is showing. You have a great troubleshooting aid in the Winnebago resources wiring diagrams.

A side story. My start battery was not charging. In error I operated the chassis salesmen switch. The start battery started charging again! I think the contacts were a bit dirty in the solenoid. So now, from time to time, I hit the battery disconnect switches as a routine to be done. No charging issues since I have been doing this.

Please keep us posted at to what you find.
Happy trails.
Rick
__________________
Rick & Melissa Young & Dawson (RIP), 2011 Meridian 40U, FL XCL, ISL 380HP/DEF, Al 3000 MH, 2014 Honda CR-V, SMI AF1, Blue Ox TruCenter & tow equip.,EEZTire TPMS.
Servants On Wheels Ever Ready. Best job we ever paid to do . (full time volunteers)
jerichorick is offline   Reply With Quote
Old 07-16-2018, 10:28 AM   #15
Winnebago Camper
 
wegobago's Avatar
 
Join Date: Feb 2018
Posts: 20
Yes, we have a front ,rear a/c switch but 2 ats boxes and 2 shore power 30 amp cords, I can only assume it was an factory-installed set up. I will take your advice and check every connection I can get access to, I'm sure I'll find a short or loose connections somewhere. In the meantime, replacing both ats boxes due to age, new ones are smaller and more modern technology and don't require the use of wire nuts to connect the wiring. Thanks so much for your help, I'll post the outcome
wegobago is offline   Reply With Quote
Old 07-17-2018, 07:36 AM   #16
Winnebago Master
 
jerichorick's Avatar
 
Join Date: Jun 2013
Location: Full-timer/volunteer w/SOWERS
Posts: 2,734
Quote:
Originally Posted by wegobago View Post
Yes, we have a front ,rear a/c switch but 2 ats boxes and 2 shore power 30 amp cords, I can only assume it was an factory-installed set up. I will take your advice and check every connection I can get access to, I'm sure I'll find a short or loose connections somewhere. In the meantime, replacing both ats boxes due to age, new ones are smaller and more modern technology and don't require the use of wire nuts to connect the wiring. Thanks so much for your help, I'll post the outcome

A ATS is a dumb box with relays in it. The A/C controller in the diagram is what you say it is, a ATS that is not functioning as a ATS. That was a novel way to accomplish the need for power control to the A/C units.



Now lets see what the problem cause is and the fix.
Rick
__________________
Rick & Melissa Young & Dawson (RIP), 2011 Meridian 40U, FL XCL, ISL 380HP/DEF, Al 3000 MH, 2014 Honda CR-V, SMI AF1, Blue Ox TruCenter & tow equip.,EEZTire TPMS.
Servants On Wheels Ever Ready. Best job we ever paid to do . (full time volunteers)
jerichorick is offline   Reply With Quote
Old 07-17-2018, 01:55 PM   #17
Winnebago Camper
 
wegobago's Avatar
 
Join Date: Feb 2018
Posts: 20
Thanks for the tip, I'll check that first as a/c was running when all this started
wegobago is offline   Reply With Quote
Old 07-18-2018, 02:56 PM   #18
Winnebago Camper
 
wegobago's Avatar
 
Join Date: Feb 2018
Posts: 20
Gen breaker won't stay set

So this problem is unsolved, generator 20 amp breaker trips, all connections including a/c control switch look good ,no obvious burning or arcing visually. I have an outlet by the kitchen sink that is dead, I believe it's tied to the gfi in the bathroom, haven't checked wiring at generator breaker's yet, mind you this is all visual at this time. The ats had burned wires was replaced. Trying to do this myself but not there yet
wegobago is offline   Reply With Quote
Old 07-19-2018, 06:55 AM   #19
Winnebago Master
 
jerichorick's Avatar
 
Join Date: Jun 2013
Location: Full-timer/volunteer w/SOWERS
Posts: 2,734
Quote:
Originally Posted by wegobago View Post
So this problem is unsolved, generator 20 amp breaker trips, all connections including a/c control switch look good ,no obvious burning or arcing visually. I have an outlet by the kitchen sink that is dead, I believe it's tied to the gfi in the bathroom, haven't checked wiring at generator breaker's yet, mind you this is all visual at this time. The ats had burned wires was replaced. Trying to do this myself but not there yet
GFCI's have the reputation of failing.



With all of the breakers off in your service panel, does your generator 20A breaker still trip?
__________________
Rick & Melissa Young & Dawson (RIP), 2011 Meridian 40U, FL XCL, ISL 380HP/DEF, Al 3000 MH, 2014 Honda CR-V, SMI AF1, Blue Ox TruCenter & tow equip.,EEZTire TPMS.
Servants On Wheels Ever Ready. Best job we ever paid to do . (full time volunteers)
jerichorick is offline   Reply With Quote
Old 07-20-2018, 05:56 PM   #20
Winnebago Camper
 
wegobago's Avatar
 
Join Date: Feb 2018
Posts: 20
Quote:
Originally Posted by jerichorick View Post
GFCI's have the reputation of failing.



With all of the breakers off in your service panel, does your generator 20A breaker still trip?
Yes 20 amp breaker on generator trips when the main panel is completely shut down. Replaced faulty gfci, all good there.
wegobago is offline   Reply With Quote
Reply

Tags
generator


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Powered Door awning won't stay closed?? pameridan04 General Maintenance and Repair 11 05-10-2010 02:13 PM
Diesel Generator won't stay running Mike-N-Sally Electrical | Charging, Solar and Electronics 8 01-01-2010 12:08 AM
Sliding Closet doors won't stay closed scottma General Maintenance and Repair 14 05-10-2009 02:57 PM
Sofa footrest won't stay locked in the "in" position CHIPPYSGT Winnebago General Discussions 6 03-29-2008 09:22 AM
Sliding Pocket Door Won't Stay Open/Closed Mike in Florida General Maintenance and Repair 21 12-13-2007 03:32 PM

» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Winnebago Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 11:48 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.