03-01-2006, 02:12 PM
|
#1
|
Winnebago Master
Join Date: Sep 2004
Posts: 527
|
I will soon be in a campground with 30 amp service. What are the downsides? As I understand the air conditioner will run on one compressor instead of two. Am I correct? Is this the only downside?
__________________
2017 Dutch Star 4369
Huey Pilot — Vietnam 1971-72
Author of ACE, The Story of Lt. Col. Ace Cozzalio
2016 Independent Publishers Book Awards Winner
|
|
|
03-01-2006, 02:12 PM
|
#2
|
Winnebago Master
Join Date: Sep 2004
Posts: 527
|
I will soon be in a campground with 30 amp service. What are the downsides? As I understand the air conditioner will run on one compressor instead of two. Am I correct? Is this the only downside?
__________________
2017 Dutch Star 4369
Huey Pilot — Vietnam 1971-72
Author of ACE, The Story of Lt. Col. Ace Cozzalio
2016 Independent Publishers Book Awards Winner
|
|
|
03-01-2006, 02:45 PM
|
#3
|
Winnebago Master
Join Date: Dec 2002
Location: Sarver, PA/Crystal River, FL/Shelocta, PA
Posts: 1,196
|
Both compressors will run fine on 30amp. Proof is many Winnebago's only come with 30 amp and they have basement AC.
__________________
Sarver, PA/Crystal River, FL/Shelocta, PA · FMCA 335149 · W3TLN 2005 Suncruiser 38R · W24, no chassis mods needed · 2013 Honda Accord EX-L · 2008 Honda Odyssey EX-L
[SIGPIC][/SIGPIC]
|
|
|
03-01-2006, 02:56 PM
|
#4
|
Winnebago Master
Join Date: Nov 2004
Location: On the Road Westward
Posts: 711
|
Yes & No.
If you have the Energy Management System (EMS) it will automatically shut down different circuits to keep you under 30 AMPs. At least, that is how ours works. We have successfully operated both AC's on 30 amps.
I am not sure of the sequence, but ours will turn off the #2 AC compressor, the hot water heater, the refrigerator & the Hi Speed AC fan to keep load below 30 Amps.
I have watched this happen when we hit the microwave button.
When done with the microwave, the EMS will put the other loads back on line.
Of course, if the EMS has shed all 4 loads & you continue to add other loads then the breaker will trip.
I would also recommend keeping an eye on the voltage.
When we are on 30 Amp service, & I really would like both AC's on line then I switch refrig & hot water heater to gas.
__________________
Dan & Sharon & Kasey (Our Yorkie Puppy (12 Yrs Old) On the Road (2012 Journey 36M, 2006 Jeep Liberty)
USN-Ret ('65-'93) Fulltimers, Class of 2012
|
|
|
03-01-2006, 04:03 PM
|
#5
|
Winnebago Master
Join Date: Nov 2005
Posts: 1,520
|
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by Tom N:
Both compressors will run fine on 30amp. Proof is many Winnebago's only come with 30 amp and they have basement AC. </div></BLOCKQUOTE>
Tom,
While the newer basement air units can run on 30 amps the older ones (prior to 2000?) have a manual 50/30 amp switch in the cabinet over the microwave. I believe the 30 amp units began when they started calling them "True Air" but I am not 100% sure on that.
Thats why they have that book that is never supposed to be removed from the coach and is always handed on when ownership changes. ;>
Best regards,
Neil
__________________
Neil V
2001 Winnebago Adventurer WFG35U
|
|
|
03-01-2006, 05:04 PM
|
#6
|
Winnie-Wise
Join Date: Jan 2005
Location: south NJ
Posts: 423
|
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by NeilV:
am not 100% sure on that.
Thats why they have that book that is never supposed to be removed from the coach and is always handed on when ownership changes. ;>
Best regards,
Neil </div></BLOCKQUOTE> Yea, right, ever buy a use car? Not every coach has a "Book"
<sub>Edited HTML Code for quote</sub>
__________________
2001 32-V Suncruiser,Ford V-10, 310 HP, 4 Koni FSD's, KVH Tracvision,trickle charge, awning travel lock, 1 dinning room slide; no roof leaks, 03malibu toad sometimes, Blackhawk all terrain towbar, Roadmaster brake Pro,1 wife,1 westy, life is good!
|
|
|
03-02-2006, 01:24 AM
|
#7
|
Winnebago Master
Join Date: Oct 2000
Location: North East Indiana
Posts: 762
|
Both compressors on the Tru Air will operate fine on 30 amps as long as you have the EMS. This is true of the heat pump side also. I am presently into my 3rd month using mine daily and no problems so far.
|
|
|
03-02-2006, 02:04 AM
|
#8
|
Winnebago Master
Join Date: Jan 2005
Location: Back at the ranch
Posts: 2,041
|
Rex - I doubt that you will notice any difference; the EMS will do the work of shedding loads as needed.
__________________
--John
2005 Horizon 40AD, 2005 Jeep Liberty CRD
|
|
|
03-02-2006, 04:05 AM
|
#9
|
Winnebago Master
Join Date: Sep 2004
Posts: 527
|
Thanks for all the answers. The EMS will handle it for me.
__________________
2017 Dutch Star 4369
Huey Pilot — Vietnam 1971-72
Author of ACE, The Story of Lt. Col. Ace Cozzalio
2016 Independent Publishers Book Awards Winner
|
|
|
03-02-2006, 04:26 AM
|
#10
|
Administrator Emeritus
Join Date: Dec 2003
Location: Virginia Beach, VA
Posts: 1,319
|
Hasn't really been asked,but I would strongly advise the use of a surge guard. Just in the past couple of days I've read posts elsewhere on these forums where the surge guard "caught" problems with a campground's power pedestal.
You can opt to have one hard-wired to the coach,or perhaps one like THIS ONE that we bought at RVUPGRADES....
|
|
|
|